I am attaching a photo of an electrical panel that the realtor claims has no issues/faults, and says she was told so by an electrician. Any Input?

 ![IMG_3646.jpg](https://global.discourse-cdn.com/internachi/original/3X/2/b/2bf38b42d4936fb431649d965abfb73c31a3f855.jpeg)

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [January 14, 2015, 10:15pm UTC](https://forum.nachi.org/t/grounding-issues/92950/2 "2015-01-14T22:15:04Z")

</div>

What do you think is wrong with it?

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 10:18pm UTC](https://forum.nachi.org/t/grounding-issues/92950/3 "2015-01-14T22:18:28Z")

</div>

Robert,

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 10:19pm UTC](https://forum.nachi.org/t/grounding-issues/92950/4 "2015-01-14T22:19:11Z")

</div>

Robert, I am looking for input, not confirmation of my assessment. However, I think there is a grounding issue.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [January 14, 2015, 10:24pm UTC](https://forum.nachi.org/t/grounding-issues/92950/5 "2015-01-14T22:24:21Z")

</div>

Many issues here is a few…  
Looks like the ground and neutral are on the same breaker lug.  
The other appears to be a scorched wire.  
And where are those wires going …through the top?  
Where is ground/neutral bar?

 ![IMG_3646.jpg](https://global.discourse-cdn.com/internachi/original/3X/9/2/9263c2c558a978456714fe11899fde720cd49785.jpeg)

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [January 14, 2015, 10:30pm UTC](https://forum.nachi.org/t/grounding-issues/92950/6 "2015-01-14T22:30:05Z")

</div>

The neutral bar is on both sides vertically behind the CB’s. Since this is a service the EGC’s and neutrals can terminate on the same bar.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [January 14, 2015, 10:35pm UTC](https://forum.nachi.org/t/grounding-issues/92950/7 "2015-01-14T22:35:50Z")

</div>

Couldn’t see that in the pic…

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 10:37pm UTC](https://forum.nachi.org/t/grounding-issues/92950/8 "2015-01-14T22:37:24Z")

</div>

Roy,  
The blue and white wire go to a yard light mounted about ten feet away from the panel.  
Yes, Ground and Neutral are Co-mingled.  
The ground/neutral bar runs behind the top row of breakers.

 ![IMG_3644.jpg](https://global.discourse-cdn.com/internachi/original/3X/6/a/6a68c1325345012fe7ff5e8833c5564bf686cb42.jpeg)

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [January 14, 2015, 10:39pm UTC](https://forum.nachi.org/t/grounding-issues/92950/9 "2015-01-14T22:39:31Z")

</div>

> [@bwetzel1](#):
>
> Robert, I am looking for input, not confirmation of my assessment. However, I think there is a grounding issue.

Honestly the photo isn’t good enough to see everything so why don’t you give us a hint? 😃

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 10:43pm UTC](https://forum.nachi.org/t/grounding-issues/92950/10 "2015-01-14T22:43:45Z")

</div>

Robert,

I called the panel as improperly grounded having co-mingled ground and common conductors.

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 10:44pm UTC](https://forum.nachi.org/t/grounding-issues/92950/11 "2015-01-14T22:44:52Z")

</div>

This is a main panel with connection to the meter, and from there to the pole.

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 10:46pm UTC](https://forum.nachi.org/t/grounding-issues/92950/12 "2015-01-14T22:46:11Z")

</div>

Another photo

 ![IMG_3645.jpg](https://global.discourse-cdn.com/internachi/original/3X/0/6/06a9598cbf5d68d9d0c676b83b18250d5610341b.jpeg)

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 10:50pm UTC](https://forum.nachi.org/t/grounding-issues/92950/13 "2015-01-14T22:50:04Z")

</div>

I have uploaded better photos. Any more input?

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 10:56pm UTC](https://forum.nachi.org/t/grounding-issues/92950/14 "2015-01-14T22:56:38Z")

</div>

Roy, I am looking for all the issues, if you have time. Thanks.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [January 14, 2015, 11:03pm UTC](https://forum.nachi.org/t/grounding-issues/92950/15 "2015-01-14T23:03:29Z")

</div>

All look good in that pic…

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [January 14, 2015, 11:11pm UTC](https://forum.nachi.org/t/grounding-issues/92950/16 "2015-01-14T23:11:29Z")

</div>

> [@bwetzel1](#):
>
> Robert,
> 
> I called the panel as improperly grounded having co-mingled ground and common conductors.

As mentioned in a service panel the EGC’s and neutrals can be on the same bus. I don’t see any issues.

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 11:11pm UTC](https://forum.nachi.org/t/grounding-issues/92950/17 "2015-01-14T23:11:41Z")

</div>

No input here about ground loops and co-mingled common/ground conductors?  
How about the use of the common buss for ground wires?

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [January 14, 2015, 11:13pm UTC](https://forum.nachi.org/t/grounding-issues/92950/18 "2015-01-14T23:13:54Z")

</div>

> [@bwetzel1](#):
>
> How about the use of the common buss for ground wires?

It is the service main…i.e…First point of disconnect.

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 11:14pm UTC](https://forum.nachi.org/t/grounding-issues/92950/19 "2015-01-14T23:14:41Z")

</div>

My understanding is that the ground and common conductors can not be co-mingled on the same buss. In fact, there is a buss at the left for ground conductors, and a buss at the right for common conductors? The common buss is connected directly to the common conductor from the meter panel.

---

<div class="post-metadata">

**Author:** ![bwetzel1](https://avatars.discourse-cdn.com/v4/letter/b/34f0e0/32.png) [@bwetzel1](https://forum.nachi.org/u/bwetzel1)\
**Post date:** [January 14, 2015, 11:15pm UTC](https://forum.nachi.org/t/grounding-issues/92950/20 "2015-01-14T23:15:20Z")

</div>

Yes, it is the first point of disconnect.