# How do you flash this?

**URL:** <https://forum.nachi.org/t/how-do-you-flash-this/36686>\
**Category:** Exterior Inspections\
**Created:** [February 26, 2009, 5:15am UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686 "2009-02-26T05:15:18Z")\
**Posts on this page:** 13\
**Page:** 1

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [February 26, 2009, 5:15am UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/1 "2009-02-26T05:15:18Z")

</div>

Did a 2 story home with a lower roof over the kitch. Lower roof meets the rear wall and at the roof/wall intersection there is a vent (like a ridge vent). How can you have proper flashing here if there is a vent? Anyone got any illustrations?

Photo is from on top of the 1st level looking at the vent. (FYI: there was no accessible attic space beneath the lower roof.)

Yes, there was a water stain on the ceiling below. :shock:

![022409 065.JPG](https://global.discourse-cdn.com/internachi/original/2X/d/ded50c959f78a6644567189554a732a44d3c9d88.jpeg)

![022409 065.JPG](https://global.discourse-cdn.com/internachi/original/2X/d/ded50c959f78a6644567189554a732a44d3c9d88.jpeg)

![022409 065.JPG](https://global.discourse-cdn.com/internachi/original/2X/d/ded50c959f78a6644567189554a732a44d3c9d88.jpeg)

![022409 065.JPG](https://global.discourse-cdn.com/internachi/original/2X/d/ded50c959f78a6644567189554a732a44d3c9d88.jpeg)

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [February 26, 2009, 5:48am UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/2 "2009-02-26T05:48:17Z")

</div>

Eliminate the vent, start over and and flash correctly.

---

<div class="post-metadata">

**Author:** ![bgraham](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bgraham/32/179260_2.png) [@bgraham](https://forum.nachi.org/u/bgraham)\
**Post date:** [February 26, 2009, 10:41am UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/3 "2009-02-26T10:41:01Z")

</div>

Joe,  
Check this out  
[http://www.roof-2-wall.com/](http://www.roof-2-wall.com/)

---

<div class="post-metadata">

**Author:** ![dvalley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvalley/32/206092_2.png) [@dvalley](https://forum.nachi.org/u/dvalley)\
**Post date:** [February 26, 2009, 11:47am UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/4 "2009-02-26T11:47:32Z")

</div>

> [@ccurrins](#):
>
> Eliminate the vent, start over and and flash correctly.

No…do not recommend eliminating the vent, as this is a newer vent that recently came out and I think it serves it purpose.

It appears to be a Cor-a-vent that was not flashed properly. Recommend flashing upgrade.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [February 26, 2009, 12:50pm UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/5 "2009-02-26T12:50:29Z")

</div>

You guys are great. Thanks to all!

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [February 26, 2009, 7:13pm UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/6 "2009-02-26T19:13:26Z")

</div>

> [@](#):
>
> Originally Posted by **ccurrins** [http://nachi.cachefly.net/forum/images/2006/buttons/viewpost.gif](http://www.nachi.org/forum/f16/do-you-flash-37668/#post493978)  
> _Eliminate the vent, start over and and flash correctly._

> [@dvalley](#):
>
> No…do not recommend eliminating the vent, as this is a newer vent that recently came out and I think it serves it purpose.
> 
> It appears to be a Cor-a-vent that was not flashed properly. Recommend flashing upgrade.

OK, my bad. “Remove vent, start over and flash correctly”.

---

<div class="post-metadata">

**Author:** ![klott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/klott/32/59_2.png) [@klott](https://forum.nachi.org/u/klott)\
**Post date:** [February 26, 2009, 8:30pm UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/7 "2009-02-26T20:30:29Z")

</div>

Turn around and drop pants! 😉

---

<div class="post-metadata">

**Author:** ![jhaynes](https://avatars.discourse-cdn.com/v4/letter/j/ce7236/32.png) [@jhaynes](https://forum.nachi.org/u/jhaynes)\
**Post date:** [February 27, 2009, 9:23am UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/8 "2009-02-27T09:23:02Z")

</div>

Joe,

I would refer it to a GC to look at…while those vents can work great, like any type of venting / flashing system, one must take into account the pitch.

As we all know, water can travel up hill (capillary action…negative pressure etc.) so even with a products such as this, they must be used in accordance with manufacturer instructions as well as realizing that such instructions must meet sound building principles.

I know from building homes over 30 years that not every product works as they say…nor does some of the past logic used in coming up with building codes stand the test of time (house wrap…getting homes to tight, etc). Which is part of the reason our industry exists…things can go wrong even when instructions are follow…any married man can tell you this… lol

Again, I would simply call it out and let a knowledgeable GC (or manufacturer rep)  
check it out.

regards

Jeff

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [February 28, 2009, 3:32am UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/9 "2009-02-28T03:32:18Z")

</div>

I referred it to a roofer. Said it likely leaks.

---

<div class="post-metadata">

**Author:** ![Frank\_Albert](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/frank_albert/32/947_2.png) [@Frank\_Albert](https://forum.nachi.org/u/Frank_Albert)\
**Post date:** [March 2, 2009, 7:52pm UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/10 "2009-03-02T19:52:56Z")

</div>

Want to bet the window isn’t flashed? The window is the first red flag in vinyl siding. I recently updated a page on my website and it shows new work with plently of leaks built in,

[http://www.albertsroofing.com/Window%20Flashing.htm](http://www.albertsroofing.com/Window%20Flashing.htm)

---

<div class="post-metadata">

**Author:** ![Frank\_Albert](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/frank_albert/32/947_2.png) [@Frank\_Albert](https://forum.nachi.org/u/Frank_Albert)\
**Post date:** [March 2, 2009, 8:07pm UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/11 "2009-03-02T20:07:33Z")

</div>

I just updated the page again.

---

<div class="post-metadata">

**Author:** ![cbrown1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cbrown1/32/250162_2.png) [@cbrown1](https://forum.nachi.org/u/cbrown1)\
**Post date:** [March 6, 2009, 9:35pm UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/12 "2009-03-06T21:35:57Z")

</div>

I bet it is like Frank says and the problem is the moisture barrier and flashing under the window.

---

<div class="post-metadata">

**Author:** ![dvalley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvalley/32/206092_2.png) [@dvalley](https://forum.nachi.org/u/dvalley)\
**Post date:** [March 7, 2009, 11:58am UTC](https://forum.nachi.org/t/how-do-you-flash-this/36686/13 "2009-03-07T11:58:43Z")

</div>

> [@Frank\_Albert](#):
>
> Want to bet the window isn’t flashed? The window is the first red flag in vinyl siding. I recently updated a page on my website and it shows new work with plently of leaks built in,
> 
> [http://www.albertsroofing.com/Window%20Flashing.htm](http://www.albertsroofing.com/Window%20Flashing.htm)

Frank,

Nice site with great images. Thanks.

Here’s a house I did yesterday.

One of many ways to send water behind your siding…  
 ![IMG_4251.JPG](https://global.discourse-cdn.com/internachi/original/2X/c/c089e5aaa450883a3532b435f5ee1f80cadecdec.jpeg)