Inspection and Writing Assignment
Course: How to Inspect Water Heater Tanks Course
WATER HEATER CHARACTERISTICS:
Type: Electric Water Heater
Make: RHEEM
Model: RHEEMGLAS STANDARD
Capacity: 50 gals.
Wattage: Upper Element 4500 watts / Lower Element 4500 watts.
Manufactured: July/1996 (21 years)
Electrical Connection: 240 volts (+ grounding)
Located: Into a Garage (2 parking spots)
Observations:
PHOTO#1
Identification Label (UL listed)
PHOTO#2
In this picture can be seen a located spot of corrosion at the upper side of the body of the water heater. It seems to be a scratch that happened in some moment and it looks content it. This observation should be repaired to avoid its growing in the future under favorable conditions.
PHOTO#3
In this picture, we can see a progressive corrosion process between the head of the cold-water inlet pipe and its surroundings. This can be a major issue and should be evaluated with special detail. If we see the age of this water heater, 21 years, we can understand that this kind of problem can appear in some moment.
PHOTO#4
In this picture, we can see several conditions that should be notified to the client:
1.- This water heater could be the original water heater of the house; independently about how well maintained and how well is working in this moment this equipment it overpassed its lifespan many years ago and it should be replaced as soon as be possible.
2.-The pipes that were used to make the inlet and outlet connection, PVC pipes, should be replaced before installing a new water heater. In this area, it would be recommendable to use copper pipes for security reasons. This area is extremely hot and is exposed to mechanical damages.
3.- A stronger shut-off valve different than plastic should installed into the cold-water inlet line.
4.- We couldnt see a check valve inside the area where the water heater is installed. If with a more detailed investigation this valve is not found it should be installed, always before the shutoff valve, previously to the water heater.
5.-It would be recommendable the installation of an Expansion Tank after the shutoff valve. In this case look complicated its installation because of the short space available between the wall and the water heater.
6.-In this picture can be seen a siphon in the hot water outlet. This siphon should have a derivation to be cleaned.
7.- In case the water heater be replaced, it can’t be used again the existent T&P valve, a new one must be installed.
PHOTO#5
The Drain Valve installed in this water heater is made of plastic, this is not recommendable and it should be replaced with a specific valve made from brass.
PHOTO#6
In this picture is depicted the existent drain line. In the way that this discharge is installed represent a high risk for the inhabitants of the house and must be reinstalled under secure conditions. There are many reports about how this kind of situation can finish on hazardous situations.
As a summary, a master plumber should be required by the client for confirming, detecting and solve all the observation stated here, independently if the house is sold or not, its a matter of security.