Incorrect wire size for a 100 amp circuit breaker

I would just install a 200 amp service. The difference in material costs is minimal between a 200 amp and a 150 amp and the amount of labor is the same.

4 Likes

This is good advice

I don’t understand the power lines capacity. From the utility. How many amps are in those utility conductors???

It doesn’t really matter. If they need to be upgraded they will upgrade them.

2 Likes

And thanks guys for freely passing on this information.

Just a regular electric car. A grocery grabber.

We stopped using the chart in 2014.

150 AMP breaker X 83% = 124.5 AMPS. #1 is 130 AMPS, so #1 is OK.

1 Like

Thank you sir.

What would the calculation be for a 200 amp service???

Overhead/underground? Call them first. Explain what you are doing. While the NEC applies to you they are the ones supplying the power. They may have certain rules in your area

1 Like

I will do just that.

Overhead service to a gooseneck 10 feet clearance

image

This is the NESC

1 Like

Are you in Michigan Robert

Read his sig

I don’t understand
You mean the non member

New Jersey

How did you determine that

Read his “signature”

I have a lot to learn. And when I do, I will be just as helpful and patient with the next new guys as you all have been with me. Thanks

2 Likes