Question for you!!

Home has a conditioned, finished basement. Drop ceiling tiles, then insulation with a vapor barrier that typically gets discolored at the barrier.

Seems like the installers typically install insulation that is for heat and not sound.

I was wondering what your thoughts and observations are?

I would not be installing this type of insulation in this manner, seems to trap air and create moisture.

Also they sealed the heating ducts above the drop panels.

![224412 050 (Small).JPG](https://global.discourse-cdn.com/internachi/original/3X/2/4/2411b30c6dcd64e7dee65232230f0c76c4f570aa.jpeg)

![224412 051 (Small).JPG](https://global.discourse-cdn.com/internachi/original/3X/5/7/5783e6a401fe107988d241a9ead852e3029c8c7e.jpeg)

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [September 25, 2012, 6:40pm UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/2 "2012-09-25T18:40:27Z")

</div>

I am only making a guess…  
Home was constructed with an Unfinished Basement Originally…  
Later…  
**Insulation was Improperly installed (vapor barrier down)**  
again  
Later…  
Basement area was Finished and the insulation was left intact…  
Removal of the vapor barrier (paper) is recommended at a minimum to correct…

That is the normal progression of the same situation when discovered in this geographic area…

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [September 25, 2012, 6:43pm UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/3 "2012-09-25T18:43:02Z")

</div>

> [@dmacy](#):
>
> Also they sealed the heating ducts above the drop panels.

Note the finished basement area as Unconditioned space…  
HVAC may not have been adequately sized for the basement addition.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [September 25, 2012, 6:44pm UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/4 "2012-09-25T18:44:00Z")

</div>

How is that any different from putting paper backed insulation around a bathroom for sound dampening?

I’m not an expert in building science but someone please explain how the paper harms anything. I don’t see how it does between two conditioned spaces.

---

<div class="post-metadata">

**Author:** ![ldapkus1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ldapkus1/32/951_2.png) [@ldapkus1](https://forum.nachi.org/u/ldapkus1)\
**Post date:** [September 25, 2012, 7:03pm UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/5 "2012-09-25T19:03:32Z")

</div>

The tabs are not attached to the joists and the batts are loosely installed so the vapor retardant paper is pretty much useless. I don’t think moisture will accumulate on the paper since the temperature difference isn’t much between the 2 levels. I see it from time to time on new construction.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [September 26, 2012, 1:24am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/6 "2012-09-26T01:24:59Z")

</div>

It probably happened like Joe H. described but I don’r see a problem because of what Linas posted. And Joe F. has a valid point about lack of harm so, David, I may comment but probably only verbally to the client. :mrgreen:

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [September 26, 2012, 1:30am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/7 "2012-09-26T01:30:46Z")

</div>

> [@lkage](#):
>
> It probably happened like Joe H. described but I don’r see a problem because of what Linas posted. And Joe F. has a valid point about lack of harm so, David, I may comment but probably only verbally to the client. :mrgreen:

I just note the deficiency  
and the potential for additional deficiencies to occur later… (which may occur days, weeks, months, years,…)

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [September 26, 2012, 1:34am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/8 "2012-09-26T01:34:17Z")

</div>

> [@jhagarty](#):
>
> I just note the deficiency  
> and the potential for additional deficiencies to occur later… (which may occur days, weeks, months, years,…)

What deficiency would you note, Joe?..the loose paper?

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [September 26, 2012, 1:36am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/9 "2012-09-26T01:36:59Z")

</div>

> [@lkage](#):
>
> What deficiency would you note, Joe?..the loose paper?

See Response # 2 …

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [September 26, 2012, 1:40am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/10 "2012-09-26T01:40:46Z")

</div>

> [@ldapkus1](#):
>
> The tabs are not attached to the joists…

Tabs appear to be stapled…  
Insulation (by weight) generally does not remain in place by mere placement alone…

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [September 26, 2012, 1:40am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/11 "2012-09-26T01:40:53Z")

</div>

> [@jhagarty](#):
>
> See Response # 2 …

Oh, you would recommend removal…

> [@jhagarty](#):
>
> I am only making a guess…  
> Home was constructed with an Unfinished Basement Originally…  
> Later…  
> Insulation was Improperly installed (vapor barrier down)  
> again  
> Later…  
> Basement area was Finished and the insulation was left intact…  
> **Removal of the vapor barrier (paper) is recommended at a minimum to correct…**
> 
> That is the normal progression of the same situation when discovered in this geographic area…

A little slicing maybe…

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [September 26, 2012, 1:44am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/12 "2012-09-26T01:44:44Z")

</div>

> [@lkage](#):
>
> Oh, you would recommend removal…

No…

Recommendation would be replacement in compliance with Manufacturer specification / recommendation…

If Insulation is present,  
at a minimum,  
it should be installed according to the manufacturer’s specifications.

Sorry if you feel offended…  
It is what it is…

---

<div class="post-metadata">

**Author:** ![ldapkus1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ldapkus1/32/951_2.png) [@ldapkus1](https://forum.nachi.org/u/ldapkus1)\
**Post date:** [September 26, 2012, 1:56am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/13 "2012-09-26T01:56:09Z")

</div>

> [@jhagarty](#):
>
> Tabs appear to be stapled…  
> Insulation (by weight) generally does not remain in place by mere placement alone…

I see it remain in place, without stapling almost 95% of the time. Sorry to burst your bubble.

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [September 26, 2012, 2:06am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/14 "2012-09-26T02:06:47Z")

</div>

> [@ldapkus1](#):
>
> I see it remain in place, without stapling almost 95% of the time. Sorry to burst your bubble.

Not bursting any bubble…  
over the last 10 years +…  
I am sure My Office has encountered / ;produced more Inspections than you have…

as I said…  
In this market…  
It is what it is…

**and if installed improperly…**  
**it is improperly installed…**

I have not encountered a disclaimer on the product for Installation within Chicago…  
maybe the product labeling varies in your area…

---

<div class="post-metadata">

**Author:** ![ldapkus1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ldapkus1/32/951_2.png) [@ldapkus1](https://forum.nachi.org/u/ldapkus1)\
**Post date:** [September 26, 2012, 2:18am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/15 "2012-09-26T02:18:25Z")

</div>

> [@jhagarty](#):
>
> Not bursting any bubble…  
> over the last 10 years +…  
> _ **I am sure My Office has encountered / ;produced more Inspections than you have…** _
> 
> as I said…  
> In this market…  
> It is what it is…
> 
> **and if installed improperly…**  
> **it is improperly installed…**
> 
> I have not encountered a disclaimer on the product for Installation within Chicago…  
> maybe the product labeling varies in your area…

I really don’t care, you just need to realize you are wrong. Admit it and move on.

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [September 26, 2012, 2:36am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/16 "2012-09-26T02:36:34Z")

</div>

If both sides of the insulation are conditioned why is it wrong?

---

<div class="post-metadata">

**Author:** ![ldapkus1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ldapkus1/32/951_2.png) [@ldapkus1](https://forum.nachi.org/u/ldapkus1)\
**Post date:** [September 26, 2012, 2:39am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/17 "2012-09-26T02:39:48Z")

</div>

> [@jjimenez](#):
>
> If both sides of the insulation are conditioned why is it wrong?

Removing the paper will have no effect. Period.

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [September 26, 2012, 3:56am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/18 "2012-09-26T03:56:31Z")

</div>

> [@jjimenez](#):
>
> **If both sides of the insulation are conditioned why is it wrong**?

Original post and picture suggest that the basement HVAC supply ducts (installed) have been taped / removed from service…

so finished **Basement is Unconditioned** …

maybe you missed that post…

---

<div class="post-metadata">

**Author:** ![ldapkus1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ldapkus1/32/951_2.png) [@ldapkus1](https://forum.nachi.org/u/ldapkus1)\
**Post date:** [September 26, 2012, 9:55am UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/19 "2012-09-26T09:55:19Z")

</div>

Dave mentioned that the **basement is conditioned.** For vapor retardant backed insulation, the tabs must be attached to the bottom of the joists to retard air/vapor movement. This installation will work as a noise barrier but vapors will migrate past the vapor barrier. It’s pretty simple. Some folks just don’t get it.

---

<div class="post-metadata">

**Author:** ![dmacy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dmacy/32/1466_2.png) [@dmacy](https://forum.nachi.org/u/dmacy)\
**Post date:** [September 26, 2012, 12:47pm UTC](https://forum.nachi.org/t/insulation-between-heated-areas/72197/20 "2012-09-26T12:47:20Z")

</div>

Just to clarify my post.

The basement is conditioned (with furnace in unfinshed area, has louvered doors, but the finished rooms are not being heated properly as you can see in the photo of the sealed registers. This would make unconditioned. (not sure the thoughts of sealing vents), most likely not enough heat/air going to 1st/2nd floors. (like Joe stated)

I see this insulation often but the vapor barrier often gets stained (moldy substance). I believe the best practice would be to use unfaced insulation between conditioned areas. (why I was posting)

Also this should go in HVAC but what are your thoughts on a make up air system for a high efficiency furnace that is bringing in outside air with the high efficiency venting?

Seems like a waste of money.