Originally Posted By: bbadger
This post was automatically imported from our archived forum.
--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
--
Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
Originally Posted By: bbadger
This post was automatically imported from our archived forum.
--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
Quote: |
Residential single family home. A set of pull down stairs was installed to an attic. A water heater was installed in the attic. I installed a porcelain pull chain lampholder. The inspector wants a switch rather than the pull chain.
I think he's wrong. I can't find any NEC reference that says I need a separate snap switch. Who's right? |
--
Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
Originally Posted By: bbadger
This post was automatically imported from our archived forum.
Quote: |
I can't find any NEC reference that says I need a separate snap switch. |
--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN
Originally Posted By: dbowers
This post was automatically imported from our archived forum.
Originally Posted By: roconnor
This post was automatically imported from our archived forum.
--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
I am absolutely amazed sometimes by how much thought goes into doing things wrong
Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.
Originally Posted By: roconnor
This post was automatically imported from our archived forum.
--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
I am absolutely amazed sometimes by how much thought goes into doing things wrong
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
--
Jerry Peck
South Florida
Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.
Originally Posted By: bbadger
This post was automatically imported from our archived forum.
jpeck wrote: |
Dan has the correct answer. |
--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
bbadger wrote: | ||
No, not for the question asked. If you read the question the poster is asking for the NEC reference. Forget the other codes for this particular question.  I am sure Dan is correct if the poster asked for other code references. |
dbowers wrote: |
Short & simple. If there is equipment in the under-floor space (crawlspace) or attic requiring servicing it needs a light. The light can have an integral switch (pull chain) BUT the control (turn-on) for the light should be at the opening to the space - that kinda rules out the pull-chain UNLESS the light is right by the access opening????? |
--
Jerry Peck
South Florida
Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.
jpeck wrote: |
Dan has the correct answer.
Maybe, IF ... It is not a slam dunk Yes or No. IF the pull chain lighting outlet is NOT at the point of entry, and many are not, then the pull chain does not meet the requirement that the point of control be at the point of entry. |
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
Greg Fretwell wrote: | ||
It sort of depends on how long the chain is doesn't it? |
--
Jerry Peck
South Florida
Originally Posted By: lfranklin
This post was automatically imported from our archived forum.
Originally Posted By: roconnor
This post was automatically imported from our archived forum.
Greg Fretwell wrote: |
Are they usiing the IRC "electrical" code or the NEC?
I understand the building codes are leaning toward the IRC |
--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
I am absolutely amazed sometimes by how much thought goes into doing things wrong
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
lfranklin wrote: |
What if the chain was ran vertical, in a matter that it would stay in place (say 10 to 20 ft) |
--
Jerry Peck
South Florida
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
jpeck wrote: | ||
Larry, You mean horizontally? (Yeah, it's late.) That would not be how it was intended. That would really make it a rinky-dink installation, something that Billy-Bob-Joe homeowner would do. |
Quote: |
Storage or Equipment Spaces.
For attics, underfloor spaces, utility rooms, and basements, at least one lighting outlet containing a switch or controlled by a wall switch shall be installed where these spaces are used for storage or contain equipment requiring servicing. At least one point of control shall be at the usual point of entry to these spaces. The lighting outlet shall be provided at or near the equipment requiring servicing. |
--
Joe Tedesco, NEC Consultant