Just wondering if the local utility company is responsible (e.g. pay for repairs) for the splicing of the service conductors at the service point? (I’m in Ontario).
I was up on a roof looking at the service point (the masthead runs through the roof) … the splices do have rubber insulation, but the insulation is rectangular in shape and is open at the ends (and somewhat old and broken).
They usually are because they are the ones that do the connecting of service at the service point (this is where the service begins, thus service point). However, open ends of the insulation on those rectangular splices are usually not an issue as long as they won’t short circuit if they come in contact with one another. Post some pics of the splices.
Thanks kindly Simon … I didn’t think they were in need of correction, since the insulators were designed to be open-ended (will try to get up the roof later, we have snow on the roofs today).
I was just curious, since I have seen some pics in the course material where there was no insulation (in need of correction) … thanks again!
If the insulation is missing or looks like it’s about to fall off (severely degraded) because it’s so brittle/old/cracked/charred then yes, I would comment and have the POCO come out and look at it. If it just looks aged, no problem. When you see enough of them you will quickly be able to tell when they stand out from the “norm”. Just takes a little practice