# Is this a double tap?

**URL:** <https://forum.nachi.org/t/is-this-a-double-tap/76692>\
**Category:** Electrical Inspections\
**Created:** [March 30, 2013, 1:43am UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692 "2013-03-30T01:43:41Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![rgiles1](https://avatars.discourse-cdn.com/v4/letter/r/b19c9b/32.png) [@rgiles1](https://forum.nachi.org/u/rgiles1)\
**Post date:** [March 30, 2013, 1:43am UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/1 "2013-03-30T01:43:41Z")

</div>

Hello all,

I am Robert, a new student member thats been lurking around and absorbing info for the past couple of weeks.

Is this a double tap in the lower right breaker? I think it is but would like some help please. thanks…

[ATTACH]

 ![Bulllock.03.29.2013 084.jpg](https://global.discourse-cdn.com/internachi/original/2X/1/1cbcfe7636133328cc7dfb6a3b1de1548e0088b5.jpeg)[/ATTACH]

 ![Bulllock.03.29.2013 085.jpg](https://global.discourse-cdn.com/internachi/original/3X/e/0/e018bd7b6d05bc9eccd531391a55599f90235e33.jpeg)

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [March 30, 2013, 1:50am UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/2 "2013-03-30T01:50:49Z")

</div>

Two conductors under a single terminal that is rated for one conductor = “double tap”

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [March 30, 2013, 1:56am UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/3 "2013-03-30T01:56:19Z")

</div>

Here’s another example for you… 🙂

 ![DSCI0096.jpg](https://global.discourse-cdn.com/internachi/original/3X/4/a/4a0a0f34d13c80a5266f980a892512359a42c998.jpeg)

---

<div class="post-metadata">

**Author:** ![rgiles1](https://avatars.discourse-cdn.com/v4/letter/r/b19c9b/32.png) [@rgiles1](https://forum.nachi.org/u/rgiles1)\
**Post date:** [March 30, 2013, 8:05am UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/4 "2013-03-30T08:05:10Z")

</div>

thank you gentlemen…

---

<div class="post-metadata">

**Author:** ![lmorrison](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lmorrison/32/58376_2.png) [@lmorrison](https://forum.nachi.org/u/lmorrison)\
**Post date:** [April 1, 2013, 4:26am UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/5 "2013-04-01T04:26:06Z")

</div>

I can’t tell for certain if where this exits the panel if it has a cable clamp. (wire nut in way). Since this looks like an add on circuit (by an amateur?) I would not doubt if it is missing. Looks like they do have room for one more breaker…lucked out.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [April 1, 2013, 8:42am UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/6 "2013-04-01T08:42:26Z")

</div>

What you’re seeing in photo #2 is the leads to a small transformer likely for a door bell.

---

<div class="post-metadata">

**Author:** ![rgiles1](https://avatars.discourse-cdn.com/v4/letter/r/b19c9b/32.png) [@rgiles1](https://forum.nachi.org/u/rgiles1)\
**Post date:** [April 1, 2013, 9:30am UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/7 "2013-04-01T09:30:44Z")

</div>

more helpful food for thought…thank you:)

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [April 1, 2013, 10:20am UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/8 "2013-04-01T10:20:09Z")

</div>

Regardless of the reason, unless the device is rated for multiple conductors you would have a double tap. Easy to fix with a twist connector but alas…you report, they get fixed:)

---

<div class="post-metadata">

**Author:** ![cbottger](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cbottger/32/206_2.png) [@cbottger](https://forum.nachi.org/u/cbottger)\
**Post date:** [April 1, 2013, 1:27pm UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/9 "2013-04-01T13:27:19Z")

</div>

> [@pabernathy](#):
>
> Regardless of the reason, unless the device is rated for multiple conductors you would have a double tap. Easy to fix with a twist connector but alas…you report, **they get fixed** 🙂

Cats and dogs get fixed hows about a repair:p:D

---

<div class="post-metadata">

**Author:** ![cvannest](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cvannest/32/170994_2.png) [@cvannest](https://forum.nachi.org/u/cvannest)\
**Post date:** [April 1, 2013, 4:00pm UTC](https://forum.nachi.org/t/is-this-a-double-tap/76692/10 "2013-04-01T16:00:13Z")

</div>

What Pope said is exactly right. If “terminal that is rated for one conductor”. There are a few brands that are rated for 2 conductors. Square D QO and Homeline breakers 10 to 30 amp, single and double pole can have (2) 14-10 gauge wire. And there is a Cutler Hammer breaker as well. The ones in your pic are GE, so they knew for sure it was “double tapped”. In future inspections, take note of the brand and model, as well as the panel box to see if the UL listing allows that type of breaker.