Is this discoloration on the main breaker bus a concern

Hi, appreciate your thoughts if the discoloration on the main breaker bus a concern.

No plus ten chatacters

4 Likes

No, but the back fed breaker appears to be missing a hold down.

5 Likes

I agree the discoloration is common on Siemens and GE panels.

4 Likes

Since the breaker is tied to the line, do i need to call the electricity company to shutdown the line and hire a pro ?

Should we ignore the 25-amp max label?

1 Like

No.

Yes.

___

3 Likes

Thanks Richard

The 25 amp max is for a breaker opposite of the 100 amp main.

5 Likes

Thank you.

2 Likes

Got to love the 25amp max sticker where the 100 amp breaker is installed.

This might be the reason for the discoloration.

The 25amp max sticker is opposite the 100amp main breaker. Can you guess the rating of the panel? It’s simple math.

1 Like

Morning, Richard. Hope to find you well.

To myself, there appears to be a hold down kit installed left of the backfeed main breaker.

That’s the bonding strap. And also, the wrong side of the breaker for a hold down kit.

1 Like

Given the location of the 25 amp max sticker I wonder if the 100 amp could be a factory installed breaker. Some more photos may help.

2 Likes

Thank you for this post. It is a good post and a great topic.

Here was a recent one I discovered. Feel free to weigh in; I would be interested in everyone’s opinion.

Not sure if this will help. Let me know if u r looking for specific area. I never open the panel like this when i bought the home. The blue tapes are new breakers when i renovated house recently. Not marked is the new 50 amp for 40 amp EV charger. TIA.