Hi, appreciate your thoughts if the discoloration on the main breaker bus a concern.
No plus ten chatacters
No, but the back fed breaker appears to be missing a hold down.
Since the breaker is tied to the line, do i need to call the electricity company to shutdown the line and hire a pro ?
Should we ignore the 25-amp max label?
No.
Yes.
___
Thanks Richard
The 25 amp max is for a breaker opposite of the 100 amp main.
Thank you.
Got to love the 25amp max sticker where the 100 amp breaker is installed.
This might be the reason for the discoloration.
The 25amp max sticker is opposite the 100amp main breaker. Can you guess the rating of the panel? It’s simple math.
Morning, Richard. Hope to find you well.
To myself, there appears to be a hold down kit installed left of the backfeed main breaker.
That’s the bonding strap. And also, the wrong side of the breaker for a hold down kit.
Given the location of the 25 amp max sticker I wonder if the 100 amp could be a factory installed breaker. Some more photos may help.