Kickout Question

Inspection of a new reroof in Oregon. The old asphalt roofing was removed to the decking and new underlayment and shingles were installed, along with new vent boots and skylights. The existing step flashing at this sidewall was reused and appears to have been properly interwoven with the new shingles.

At the bottom of the roof/wall intersection, however, the roofer added the kickout shown in the photo. It appears to be surface-mounted over the existing step flashing rather than integrated into the flashing assembly as the first piece of step flashing.

InterNACHI’s detail shows the kickout integrated as the first piece of the step-flashing system, with the next flashing/shingle course overlapping it. Oregon’s residential code also describes the step flashing at the end of the sidewall as being turned out to direct water away from the wall.

My question is how you would report this particular installation? Assuming the existing step flashing continues behind this area and remains serviceable, would you still call the surface-applied kickout an improper flashing installation, or treat it as an auxiliary diverter whose effectiveness/integration cannot be confirmed? There is ANOTHER, original kickout beyond it that dumps directly into the gutter.

IF it lacked any step-flashing behind/underneath it, I would call this out as a defect as it is a point where moisture could penetrate into the structure underneath. IN THIS CASE, though, I don’t think that can happen.

How would you write this up on a report?

Seth, please post additional pictures showing the second kickout plashing dumping into the gutter.

Also, if that joint is open to water entry (It appears so but is hard for me to tell for sure.), water will get under the kickout flashing shown and potentially under the shingles. Kickout flashing should be installed so water drains over it, NOT BEHIND AND UNDER IT.

Recommend correction to prevent water draining behind and under the kickout flashing potentially causing damage to sheathing, framing, etc. underneath.

Edit:

The top of the underneath shingle is about where the tip of the arrow is. So, water can migrate under the below shingles.

1 Like

Thanks for your comment Larry. I’m sorry I don’t have a better picture of this issue showing the kickout right past it (about 6" farther down). The roofer did the same thing on the other side of the house, though. You can kind of see it here:

The darker black is the new kickout. The gray with the white is the original one. Basically, the roofer wove the old step flashing into the new shingles. That all looked fine. There was already a (pretty shallow) kickout present. The roofer did replace a couple of the step flashing segments and correctly integrated them. However, he added new kickouts a few inches “up-roof” from the originals. The newly added ones were NOT integrated correctly into the the other step flashing segments, but just placed on top of them. The kickouts do weave correctly into the adjacent shingles.

Water running down the siding or along the step flashing could go behind the added, new kickout. However, I don’t think it would penetrate into the structure, as the original step flashing is present underneath to prevent penetration.

I was thinking therefore of calling it a minor defect – improper installation of the kickout. But I figured I should ask those of you who are more experienced first.

Are you willing to pay for any damage that may be caused by the improperly installed kickout flashing? If not, recommend repair.

I prefer not to label defects as major or minor.

They are defects. Whether they are major or minor is up to the client.

For instance, an improperly supported deck may be a minor fix for a qualifed carpenter client but a major problem for a single mother with 3 kids.

2 Likes

Hmm, I don’t like it. I have to wonder why they would put that in there like that, when it would have been much better and easier to just add a new piece below the existing kickout. Is it possible there was an issue that appeared right after re-roofing, and this was the fix? I would recommend further evaluation by a qualified roofer. I would want it removed and improve the original kickout instead. The reason I would want a roofer to do it, is because if there were any fasteners installed, those holes will need to be properly patched.

1 Like

I am on the other side of that discussion. I see a big part of our job as going the next step and informing our clients why this defect is important and that one, not so much. Even people who are knowledgeable nearly always appreciate and even want that guidance and opinion even if it only reinforces what they already thought.

Regarding the photos of the kickout, that sure looks like a bad installation that could lead water going places we don’t like. “Sealing” or caulking that transition would not be considered a good fix. I think you made a good observation.

1 Like

It looks to me like the second kickout flashing was installed because the first attempt was improper. In looking at the second photo that shows both the original and the new kickout flashing, it appears as though there is no real diverter on the original kickout flashing. It may just be the angle of the photo, but it doesn’t look as though the bend to divert water into the gutter is present. When I encounter something like this my first thought is “this home has already been inspected once and they’ve gone back and tried fixing it.” Whether that’s the case or not, if it’s not right, call it out.

It is installed incorrectly…The diverter or kickout flashing should have been placed behind the step flashing and not on top of it. As it is now, water will get behind the kickout flashing.

3 Likes