Are wall sconces over a bathtub suppose to be GFCI protected? It’s a regular tub, not a spa.


Originally Posted By: jpope
This post was automatically imported from our archived forum.



No. But they must be outside the area specified in NEC 410.4(D)


![](upload://At5ETKhT34dHCbqK2weX4Vk5vtE.jpeg)


Originally Posted By: Blaine Wiley
This post was automatically imported from our archived forum.



great diagram, Jeff!


Originally Posted By: bbadger
This post was automatically imported from our archived forum.



It is but I must pint out wall sconces are not prohibited from ‘the zone’.


Quote:
410.4(D) Bathtub and Shower Areas. No parts of cord-connected luminaires (fixtures), hanging luminaires (fixtures), lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing and includes the zone directly over the tub or shower stall.



Originally Posted By: jpope
This post was automatically imported from our archived forum.



You’re right Bob. It even says that in the diagram icon_rolleyes.gif


Originally Posted By: syared
This post was automatically imported from our archived forum.



Thanks!


Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



If this is a shower you want to look for a “suitable for wet locations” if it is where the shower can spray it.


I suppose Darwin is the only limiting factor to who relamps while standing in the water.


Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Greg Fretwell wrote:
I suppose Darwin is the only limiting factor to who relamps while standing in the water.


Looks like it. ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)

I would not feel comfortable installing dry location wall sconces above a tub but there is not an NEC not to do it.


Originally Posted By: jkormos
This post was automatically imported from our archived forum.



hey they make nice soap dishes icon_biggrin.gif


Originally Posted By: jsieg
This post was automatically imported from our archived forum.



O.K. so what’s the rules for recessed dan lighting???


Originally Posted By: away
This post was automatically imported from our archived forum.



Jason,


Per the image posted by Jeff, they would be allowed above or within the zone. I would like to believe they would need to be rated for a wet location as well but can't find anything on that offhand unless. And I don't know if Greg's post is referencing the sconces in particular or luminaires in general.


--
Andrew Way
Keystone Residential Inspection Services PLLC
817.441.9598
www.keystoneinspections.com

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



away wrote:
I would like to believe they would need to be rated for a wet location


If it is a shower stall as well as a tub the fixtures will br required to be listed for wet locations.


Originally Posted By: mgault
This post was automatically imported from our archived forum.



Above my garden tub I have 2 not rated for wet locations but the covers must remain in place (can’s with flat plastic ‘covers’)


The one above the separate shower stall is rated for a wet or damp locations...
All are 9 foot ceilings so I guess they coulda' put in anything ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)


Originally Posted By: away
This post was automatically imported from our archived forum.



Bob,


Thanks for clearing that up, I kind of figured they would need to be. I just haven't made it through the entire IRC and NEC yet. ![icon_biggrin.gif](upload://iKNGSw3qcRIEmXySa8gItY6Gczg.gif)

Just to be safe, when I find them I always recommend ascertaining whether they are listed for wet locations or not. Especially the shower stalls that have really low ceilings, 7 or 7.5 feet, where water/moisture is more likely going to have an impact and possible consequences.


--
Andrew Way