Mega mobile home park in central Florida; circa mid 80’s. 1981 home with sub in bedroom, sub has 150 amp main breaker, neutrals and grouds separated. Only meter box on front exterior, no exterior main panel. No disconnect for SE cable from meter box to sub. Got to looking around and all other homes the same situation. Any thoughts, thanks.
If it is the main; then, the neutrals and grounds should be bonded (they’re not); the problem is; without a main panel on the exterior; there is no breaker protection for the SE from the meter to the panel in the bedroom leaving an approximate 12 foot SE cable w/o breaker protection. I’ve done numerous mobiles and all (up to now) have an exterior main panel making the panel provided with the home, set up as a sub with N&Grds separated. Like I said previouly; this is a maga park and all other homes were set up the same way. Its not likely that all are wrong but I’m just not getting it.
As long as the service entrance conductors are outside they can remain unfused, even if 100 foot long. The SE needs to be as short as practical once they enter the building.
Thanks all; The SE is routed under the home and runs approximately 12 feet to the interior panel. , but my main concern is; if only a meter box on exterior, wouldn’t this make the interior panel the main w/ N& Grds bonded (they’re not) and the lack of breaker protection on the SE cable from the meter box to this interior panel.
Jim, I’m assuming the by outside, you’re including under the home, if this is the case; then, the SE only runs a few feet up to the interior panel which is close to the floor. But still, should this interior panel be considered the main?
From Michigan, it appears to be the service disconnect where grounding and grounded contuctors would be bonded. However, I don’t know if the SE is as short as practical once they enter the home.