ccurrins
(Christopher Currins, CMI)
August 12, 2015, 2:33am
21
kshepard:
It seems pretty obvious that the 200 amp disconnect is the service disconnect. There’s only one of those on a house. That’s the point of first disconnect. There’s not two different service disconnects in this one panel.
Then there’s a 125-amp disconnect, pretty obvious that it goes to the sub-panel, a common condition. I can’t see in this photo where the sub-panel disconnect pulls it’s power from. Randy? Is it connected to a breaker at the bottom of the supply bus bar? Is it connected to a set of lugs (connection points) that are connected to the bottom of the supply bus bar?
Look closer. Flipping off the 200 amp breaker will not cut power to the 125 amp breaker. They are both fed individually from meter.
rdimit
(Randy Dimit, #60269)
August 12, 2015, 2:49am
22
That is correct. What they have done is place both Main Breakers for the Main panel and the Sub-panel in the same place, essentially. The Main is a 200 amp service and the Sub is a 125 amp service, obviously.
btoye
(Bradley Toye, CMI)
23
Yep, the 200A breaker AND the 125A breaker IS the service disconnect.
jhutchings
(Jeremy P. Hutchings, IOS.2284-RES)
August 12, 2015, 4:34am
24
These are the types that are popular here in the Las Vegas Valley. I am sorry for the poor quality photos.
jhutchings
August 12, 2015, 4:35am
25
How do I turn these photos the right way up?
rmeier2
(Robert Meier)
August 12, 2015, 8:47am
26
Since there are two service disconnects how do you determine the size of the service?
rdimit
August 12, 2015, 1:12pm
27
I’m no expert by any means, but I would go with the highest main. As in my case, 200A.
rlewis5
(Roy Lewis, CERTIFIED MASTER INSPECTOR RETIRED)
August 12, 2015, 1:28pm
28
Use a free photo editing program like Xnview
kshepard
(Kenton Shepard, CMI)
August 12, 2015, 2:56pm
29
OK, I cropped it and lightened the exposure. I’ve never seen one like this.
rlewis5
August 12, 2015, 3:15pm
30
The top breaker is for the sub and the other for the main.
On deadfront cover someone wrote subpanel at that top knockout.
jhutchings
August 12, 2015, 3:53pm
31
Thank you! I’ll give that a try.
jhutchings
August 12, 2015, 4:31pm
32
enlighten us grasshopper.
rmeier2
(Robert Meier)
August 12, 2015, 9:24pm
33
IMO you would use the ampacity of the service entrance conductors once you’ve installed more than a single service disconnect.
This may help, take look at the diagram in post #34:
http://forums.mikeholt.com/showthread.php?t=165201&highlight=multiple+service+disconnects
jhutchings
August 12, 2015, 10:19pm
34
That drawing helped me wrap my head around it. Everything is mostly underground here and I do not have enough balls to snip off the power company tag to peek inside. Not for a fear of electrocution but rather getting in trouble with the homeowner or power company.