Does anyone have a copy of NFPA 211 that they can share information about.  
  
  
On a factory built wood burning fireplace what is the roof clearance. Above the roof and to the closest point of the roof and what is the minimum distance above that point?  
  
3 - 2 - 10 ?  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [May 16, 2004, 12:00am UTC](https://forum.nachi.org/t/manufactured-fireplaces-nfpa-211/175575/2 "2004-05-16T00:00:00Z")

</div>

**Originally Posted By: rcloyd**  
**This post was automatically imported from our archived forum.**

* * *
  
Peter:  
  
  
Look at the manufacturer's installation instructions for the required height.  
It should be installed in accordance with its listing.  
  
  
Regards,  

* * *
  

--  
Russell G. Cloyd  
Intra-Spec Home Inspections  
& Code Consulting, LLC  
859-586-4591  
[www.intra-spechomeinspections.com](http://www.intra-spechomeinspections.com)

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [May 16, 2004, 12:00am UTC](https://forum.nachi.org/t/manufactured-fireplaces-nfpa-211/175575/3 "2004-05-16T00:00:00Z")

</div>

**Originally Posted By: jpeck**  
**This post was automatically imported from our archived forum.**

* * *
  
Minimum height for a chimney (not a gas vent) is 3’ high above the roof - MINIMUM.  
  
  
AND  
  
Minimum height is 2' higher than ANY part of ANY structure, not just the roof and not just this structure's roof.  
  
The height is measured on the high side of the roof where the chimney comes through the roof.  
  
3-2/10  
  
If different. let them prove it is less.  

* * *
  

--  
Jerry Peck  
South Florida

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [May 16, 2004, 12:00am UTC](https://forum.nachi.org/t/manufactured-fireplaces-nfpa-211/175575/4 "2004-05-16T00:00:00Z")

</div>

**Originally Posted By: dbowers**  
**This post was automatically imported from our archived forum.**

* * *
  
Peter - Manufactured Fireplaces are ALLOWED and REQUIRED to be installed in accordance with the manufacturers instructions. The 3/2/10 rule is intended for masonry fireplaces - however if the Mfg. Installation instructions are not available - the 3/2/10 is a good guideline to use.  
  
  
Dan Bowers  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [May 16, 2004, 12:00am UTC](https://forum.nachi.org/t/manufactured-fireplaces-nfpa-211/175575/5 "2004-05-16T00:00:00Z")

</div>

**Originally Posted By: jpeck**  
**This post was automatically imported from our archived forum.**

* * *
  

| **dbowers wrote:** |
| Peter - Manufactured Fireplaces are ALLOWED and REQUIRED to be installed in accordance with the manufacturers instructions. The 3/2/10 rule is intended for masonry fireplaces - however if the Mfg. Installation instructions are not available - the 3/2/10 is a good guideline to use.  
  
Dan Bowers |

   
   
Just curious, Dan, have you seen any manufactured fireplace with LESS height required? Yes, they are allowed (and required, as you said) to be installed in accordance with the manufacturer's installation instructions, but I have not seen any which provide for less that that height.  
   
Of course, not only have I not seen them all, I see very few. Call it out at 3-2/10 and let them prove otherwise. Unless, of course, you happen to have the installation instructions there to read.  

* * *
   

--  
Jerry Peck  
South Florida

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [May 17, 2004, 12:00am UTC](https://forum.nachi.org/t/manufactured-fireplaces-nfpa-211/175575/6 "2004-05-17T00:00:00Z")

</div>

**Originally Posted By: LJ Johnson**  
**This post was automatically imported from our archived forum.**

* * *
  
Jerry and DAn - You’re both right from what I can tell. I called 2 different code officials today and looked in the IRC code book. It specifically uses the 3-2-10 rule with masonry fireplaces, and specifically says under prefab fireplaces that they are to be installed per manufacturers installation instructions - no mention of 3-2-10 or other heights.  
  
  
Now if I had the manufaturers specs available thats what I'd use - if not its seems safe to drop back to 3-2-10 and let others sort it out or dispute that if they want.  
  
LJ  

* * *