I am in the process of the R5 Residential COMBO Cert. I passed the B1 exam and have failed the M1 Exam twice, both times I’ve gotten hung up on the math equations in Combustion Air. Any advice is greatly appreciated.
Thank you,
Bob Greenaway
I am in the process of the R5 Residential COMBO Cert. I passed the B1 exam and have failed the M1 Exam twice, both times I’ve gotten hung up on the math equations in Combustion Air. Any advice is greatly appreciated.
Thank you,
Bob Greenaway
What is it with the math equations you are experiencing issues with?
I can do the math, it’s knowing which equation to use that I am having trouble with. An example is a question asking the volume of makeup air needed if you have two appliances in a room of a given dimension. Another involved a 40-gallon hot water heater in a room of a given dimension.
I appreciate the response, thank you
Example (from: furnace make up air requirements per btu rating - Google Search)
How much combustion air is needed for an 80000 BTU furnace?
In this example we’ll say that the furnace has an input rating of 80,000 BTU/hr and the water heater has an input rating of 40,000 BTU/hr. So the combined input rating is 120 when measured in 1,000 BTU/hr. So the room needs to have a volume of 120 x 50, or at least 6,000 ft3. (Or, a room 25’ x 32’ x 8’ high’…6,000 ft3/8 = 750 ft2/ 25’ = 32’) I think I got that right.
Thank you very much, that was the part I wasn’t putting together💪