This is my first metal roof inspection and I wanted to make sure I didn’t miss anything. I think there are defects in all 3 of these images, but just wanted to verify before sending the report.

Image #1


Ridge Cap Openings

Openings were observed beneath portions of the metal roof ridge cap. The openings may be associated with a ridge ventilation system; however, the presence and proper installation of appropriate closure or ventilation materials beneath the cap could not be verified during the visual inspection. Recommend evaluation by a Qualified Roofing Contractor to confirm the ridge assembly is properly installed and protected against wind-driven rain, debris, and pest intrusion.

Image #2

Irregular Metal Roof Hip Caps

Gaps and raised/irregular sections were observed along the metal roof hip caps. Proper closure materials beneath the caps could not be verified during the visual inspection. The observed openings may allow wind-driven rain, debris, or pest intrusion if appropriate closures and flashing are not present. Recommend evaluation and correction as necessary by a Qualified Roofing Contractor in accordance with the roofing manufacturer’s installation requirements.

Image #3

Metal Roof – Valley Deficiencies

Deficiencies and apparent previous repairs were observed at a metal roof valley/intersection, including irregularly cut and fitted flashing components and substantial sealant application. This area receives concentrated roof drainage, and the adequacy of the underlying flashing and weather-resistant installation could not be determined during the visual inspection. Improperly installed or deteriorated valley flashing may allow moisture intrusion and concealed damage. Recommend evaluation and proper repair of the roof intersection by a Qualified Roofing Contractor in accordance with the roofing manufacturer’s installation requirements.

I think you are on the right track. It seems lake an odd roof.

Can you share pictures of farther back (more over all view) and maybe a bird’s eye view or two from above?

1 Like

It appears that your commentary covers the open gaps at the ridge caps where venting typically happens. It looks like some caps are loose also and need re-attaching.

This picture appears that the pentagonal roofs ridge intersects at the apex of the two main roof valleys. And that is a difficult transition to make with metal roofing. I don’t think it was a repair. It looks like a poorly detailed transitional intersection of 3 planes, 2 valleys and a ridge…all metal. So there will be continued maintenance to keep it water tight at a minimum.

Were you able to see details at the end of valley roof intersection and behind the chimney in this picture?

3 Likes

There was no cricket; the chimney was about 30.5" wide and did have sealant. I did already call those out :slight_smile:

1 Like


This is the underneath portion of the other arrow you drew

I can’t blow that up to see underneath. I was more interested in the top portion and it looks like they used an additional sheet of metal on top of the bottom of the valley which is appropriate.

If you handled the uphill side of the chimney, kickout flashing and covered the loose metal in different areas you appear to have it covered.

Nice job with what I can see from Michigan.

:+1:

2 Likes

I normally like to itemize each deficiency. Something like this I would go with the multiple deficiencies were observed and recommend a full evaluation and repair by a qualified contractor.

2 Likes

I did do each one as their own defect