Did a house yesterday that was a “kit House”. 100% metal walls, rafters, etc. My question lies in regards to the wind mitigation and the truss to wall connection, how should this be rated? Anyone else ran across this and had any luck? The owner/builder states the home is rated for 150MPH wind load, which I am waiting on certification papers to verify.

 ![SAM_0186.jpg](https://global.discourse-cdn.com/internachi/original/3X/f/8/f80459f5b4e90822fbb1033aa7b2a1bfbc19bc5c.jpeg)

 ![SAM_0187.jpg](https://global.discourse-cdn.com/internachi/original/3X/b/2/b2c5d2a7c6fd825475194402e31762f057c161a8.jpeg)

 ![SAM_0184.jpg](https://global.discourse-cdn.com/internachi/original/3X/2/4/2417e45be9bf87653c93d605898a9dea5fd942ee.jpeg)

---

<div class="post-metadata">

**Author:** ![mmeeker](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mmeeker/32/59432_2.png) [@mmeeker](https://forum.nachi.org/u/mmeeker)\
**Post date:** [January 26, 2012, 2:40pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/2 "2012-01-26T14:40:01Z")

</div>

I to would love to know what you all think. Steve since it is a kit house maybe the manufacturer or the folks who sold it would have the drawings and engineering info. They then should have the NOA’s and such.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [January 26, 2012, 2:42pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/3 "2012-01-26T14:42:44Z")

</div>

Don’t know about down there, but up here it’s nothing but a fancy manufactured home, and would pay through the nose for insurance. One little “puff” and it’s G-O-N-E !!!

---

<div class="post-metadata">

**Author:** ![shord](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/shord/32/250118_2.png) [@shord](https://forum.nachi.org/u/shord)\
**Post date:** [January 26, 2012, 3:18pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/4 "2012-01-26T15:18:35Z")

</div>

I am waiting to see what type of engineering documentation it has with it. Apparently he could get different kits with different wind loads. It certainly is not the norm. And as with all home owner built homes… it scares me.

---

<div class="post-metadata">

**Author:** ![evandeven](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/evandeven/32/373798_2.png) [@evandeven](https://forum.nachi.org/u/evandeven)\
**Post date:** [January 26, 2012, 4:37pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/5 "2012-01-26T16:37:25Z")

</div>

> [@shord](#):
>
> Did a house yesterday that was a “kit House”. 100% metal walls, rafters, etc. My question lies in regards to the wind mitigation and the truss to wall connection, how should this be rated? Anyone else ran across this and had any luck? The owner/builder states the home is rated for 150MPH wind load, which I am waiting on certification papers to verify.

Where is this? There are several of these homes just north of Hillsborough blvd near the turnpike.

I would guess you would have to get the specs from the build and then…it will be up to the underwriter.☹

---

<div class="post-metadata">

**Author:** ![khunt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/khunt/32/89347_2.png) [@khunt](https://forum.nachi.org/u/khunt)\
**Post date:** [January 26, 2012, 6:18pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/6 "2012-01-26T18:18:15Z")

</div>

Looks to me like it meets the definition of a clip to me…

> [@](#):
>
> Secured to truss/rafter with a minimum of three (3) nails, and  
> Attached to the wall top plate of the wall framing, or embedded in the bond beam, with less than a ½" gap from the blocking or truss/rafter and blocked no more than 1.5” of the truss/rafter, and free of visible severe corrosion.
> 
> B. Clips  
> Metal connectors that do not wrap over the top of the truss/rafter, or…

Only issue might be the word “nails”. Would have to prove whatever is attaching those is equivalent the the strength of a nail…

---

<div class="post-metadata">

**Author:** ![bhoagland](https://avatars.discourse-cdn.com/v4/letter/b/a183cd/32.png) [@bhoagland](https://forum.nachi.org/u/bhoagland)\
**Post date:** [January 26, 2012, 9:08pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/7 "2012-01-26T21:08:15Z")

</div>

Provide the specs, fill out the form per the specs, it’s any system that provides the required uplift, if COed by the AHJ and you provide the required specs and observed the installation per specs you should be good to go.

---

<div class="post-metadata">

**Author:** ![jdeese](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jdeese/32/171047_2.png) [@jdeese](https://forum.nachi.org/u/jdeese)\
**Post date:** [January 27, 2012, 1:14am UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/8 "2012-01-27T01:14:26Z")

</div>

For the roof to wall system I would think this could be marked as structural. It looks like the “roof to wall” system is bolted. Or it could be marked as “other”

For the deck fasteners they should be screws no?

---

<div class="post-metadata">

**Author:** ![pcampbell](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pcampbell/32/1621_2.png) [@pcampbell](https://forum.nachi.org/u/pcampbell)\
**Post date:** [January 27, 2012, 3:05am UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/9 "2012-01-27T03:05:12Z")

</div>

Just WTF will it take to get new ppl to set up with their info., esp. LOCATION?!?

---

<div class="post-metadata">

**Author:** ![dwalsh1](https://avatars.discourse-cdn.com/v4/letter/d/43a26b/32.png) [@dwalsh1](https://forum.nachi.org/u/dwalsh1)\
**Post date:** [January 27, 2012, 3:15am UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/10 "2012-01-27T03:15:54Z")

</div>

You tell me, not that I am “new”. I have checked and my info is all there on the profile page but does not show up on the MB. I’d love to know.

---

<div class="post-metadata">

**Author:** ![lmaxwell](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lmaxwell/32/171351_2.png) [@lmaxwell](https://forum.nachi.org/u/lmaxwell)\
**Post date:** [June 29, 2013, 1:28pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/11 "2013-06-29T13:28:48Z")

</div>

This home has no wind mitigation credits because roof to rafters attachment.

---

<div class="post-metadata">

**Author:** ![wsmith3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wsmith3/32/60103_2.png) [@wsmith3](https://forum.nachi.org/u/wsmith3)\
**Post date:** [June 29, 2013, 4:57pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/12 "2013-06-29T16:57:26Z")

</div>

> [@shord](#):
>
> Did a house yesterday that was a “kit House”. 100% metal walls, rafters, etc. My question lies in regards to the wind mitigation and the truss to wall connection, how should this be rated? Anyone else ran across this and had any luck? The owner/builder states the home is rated for 150MPH wind load, which I am waiting on **certification papers to verify**.

Answer in the question. I would not be a bit surprised that the insurance underwriter (being so well versed in construction) will accept this as a valid installation. The SIGNED AND SEALED engineering docs. should be acceptable and should have been delivered to the owner.  
Keep us informed please.

---

<div class="post-metadata">

**Author:** ![btoye](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/btoye/32/58400_2.png) [@btoye](https://forum.nachi.org/u/btoye)\
**Post date:** [June 29, 2013, 7:13pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/13 "2013-06-29T19:13:58Z")

</div>

I think the underwriter would have accepted the RTW as a clip, and the RDA as 8d equivalent (spacing unknown without photo), even without engineering docs. This thread is a year and half old.

---

<div class="post-metadata">

**Author:** ![wcollier](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcollier/32/180057_2.png) [@wcollier](https://forum.nachi.org/u/wcollier)\
**Post date:** [June 30, 2013, 1:57am UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/14 "2013-06-30T01:57:31Z")

</div>

> [@lmaxwell](#):
>
> This home has no wind mitigation credits because roof to rafters attachment.

Please cite your source

---

<div class="post-metadata">

**Author:** ![jmurray4](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jmurray4/32/2301_2.png) [@jmurray4](https://forum.nachi.org/u/jmurray4)\
**Post date:** [July 2, 2013, 5:46am UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/15 "2013-07-02T05:46:33Z")

</div>

> [@wcollier](#):
>
> Please cite your source

That a very polite way of asking what wtf are you smoking?

---

<div class="post-metadata">

**Author:** ![wcollier](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcollier/32/180057_2.png) [@wcollier](https://forum.nachi.org/u/wcollier)\
**Post date:** [July 2, 2013, 10:33am UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/16 "2013-07-02T10:33:26Z")

</div>

I did not realize it was an old thread till later. Probably won’t ever get an answer.:mrgreen:

---

<div class="post-metadata">

**Author:** ![jshishilla](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jshishilla/32/1188_2.png) [@jshishilla](https://forum.nachi.org/u/jshishilla)\
**Post date:** [July 2, 2013, 12:05pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/17 "2013-07-02T12:05:40Z")

</div>

Meeker answered the question, you need docs from the designer

---

<div class="post-metadata">

**Author:** ![slagueux](https://avatars.discourse-cdn.com/v4/letter/s/b9bd4f/32.png) [@slagueux](https://forum.nachi.org/u/slagueux)\
**Post date:** [July 6, 2013, 3:59am UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/18 "2013-07-06T03:59:33Z")

</div>

You can get the Residential Steel Framing Manual (for architects, engineers and builders) from the American Iron and Steel Institut.

For having worked in Florida many years as a light steel gauge framer, I can tell you that none of that on the pics would meet wind uplift code requirements.

---

<div class="post-metadata">

**Author:** ![Jim\_Mullen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jim_mullen/32/2240_2.png) [@Jim\_Mullen](https://forum.nachi.org/u/Jim_Mullen)\
**Post date:** [July 7, 2013, 3:22pm UTC](https://forum.nachi.org/t/metal-studs-and-trusses-for-wind-mitigation/66180/19 "2013-07-07T15:22:39Z")

</div>

As a builder, I believe that the insurer (especially if it’s our beloved Citizens!) is going to consider this a “mobile home”, therefore no wind credits. The owner could argue the fact with all the proper engineering docs, as this has to have had sufficient engineering to be allowed in our state to begin with, but unfortunately “they” make the rules and have the final say. ;(