Missing GEConductor

I spent about 5 minutes searching for the GEC onsite within panel and had to just take pictures and move on, the grounding screw is set back, they had jumper wires over water heater. This condo unit was 26 years old, is the GEC really not here or am I completely missing it. I cannot see SEC underground and must shoot under concrete slab floor and then shoot up to panel.

I don’t see one. Was there an exterior disconnect? Do you have a picture of the meter area?

Uh individual condo units have subpanels so they shouldn’t have a GEC(grounding electrode conductor). GEC is supposed to be installed at the main panel or shut off, which is typically at the outside of the whole building at the meter bank and exterior shut offs.

4 Likes

Ryan I attempt to record with camera then take pictures as needed with my phone, but I sometimes go back and snap photos from videos once I get them transfered to my phone. Does this picture help, i have not downloaded videos to my phone yet and with that camera that’s the best place I could pause it.

I did not notice anything outdoors, I sent Ryan a couple pics from my video

I’m going to guess that the GEC originates in the meter box in your installation. However, you will not be able to confirm this typically. I have a a call out I use when I can’t confirm the GES (Grounding Electrode System), but I suspect it is present and I just can’t see it. It’s kind of a “cover my butt” callout. Feel free to use if desired.

The GES (grounding electrode system) installation could not be verified.

The GES is a safety component of the electrical system. It diverts electrical current to a safe ground in the event of an electrical system malfunction or lightening strike to the home. Typically the GES consists of a bare, heavy gauge wire (the grounding electrode conductor, or GEC) routed from the main panel to outdoor ground rods, or routed to metal rods encased in concrete, or to a metallic water pipe that enters the building underground.

The fact that the inspector was not able to verify the GES may not mean that it is absent or that it is incorrect. It only means that the inspector could not visually verify a proper installation due to visual limitations, such as a finished basement.

Recommendation: Consult with a qualified electrical contractor to determine if the GES is adequately installed.

1 Like

Yes I am thinking I will need to fall in along those lines, if that was a sub panel then that green screw above the main breaker would have needed to have been pulled out. There are a couple other things I am mentioning in the panel also maybe after I get the electrical report done it won’t look so bad for me to refer repairs and further evaluation by electrician.

If in this installation, it is allowed to have the grounds and neutrals connected, then the green screw needs to stay installed. Even if the installation is wrong, removing the green screw would not be desirable until a 4th conductor is installed with the service and the grounds and neutrals are separated. I only mention this because you don’t necessarily want to suggest that removing the green screw will make this installation ok. Removing it would actually be more dangerous than having it installed if other changes aren’t made.

2 Likes

Did they use EMT?

3 Likes

I did not see any throughout the home

That looks more like a townhouse set up than a condo. You should check around the meters to see if you can find the GEC

Edit:

Follow the cable/internet wiring near the outside meters. Typically, the telecommunications guy will connect the ground wire for the cable system to the GEC of the house.

3 Likes

I may just run back out there tomorrow real quick, it just so happened to be a condo unit 5 minutes from me.

(post deleted by author) LOL!

Let us know what you find. Just curious did you write up the door bell transformer?

1 Like

Here’s a possible clue…

7 Likes

Here’s another possible clue, it looks like there may be a grounding conductor coming out of the bottom of the meter panel and going into a hole in the side of the structure, possibly to the water main or an Ufer ground.

2 Likes

Yes Robert I did, I knew they are not supposed to be inside the panel but honestly I did not know why. But researched and found out it’s because low voltage could be affected by higher voltage wires if insulation for some reason gets wore off.

Yes it has to do with the fact the the low voltage output of the transformer is using class 2 wiring which is not permitted within the panel along with the line voltage conductors.

Although it’s a minor issue the EGC and neutral for the transformer are connected to to a bare conductor. They should be separated with an insulated conductor being used for the neutral.

3 Likes

Ok it took me a minute but I understand what you are saying, are those two black conductors coming off of that transformer just pigtails somebody installed on them or are those factory pigtails? If they are not factory pigtails, I’m not sure why they wouldn’t have just used a white insulated pigtail and wrapped it up to the bus bar on its own.

You guys on this forum amaze me everyday how you see this stuff through my blurry photos. You caught it and I see it after I cleared up my video to photos. I still feel I am missing something that I am not seeing it coming into the electric panel though? I have a hard time believing that the electrical contractor and I’m sure there was an inspection at the time would have overlooked it.

1 Like