look at these signs of moisture in and under this panel.  
Meter is directly behind this panel on the exterior wall.  
We’ve had a little rain lately.

no moisture in the panel at time of inspection.  
moisture meter showed the stains below the panel to be completely dry.

i’m obviously calling it out, but how many would defer and say an electrician’s evaluation is necessary.

![100.jpg](https://global.discourse-cdn.com/internachi/original/3X/c/a/ca9d947e010022bb452561c4a44908412afcb6d0.jpeg)

![100.jpg](https://global.discourse-cdn.com/internachi/original/3X/6/7/67180f424dc578d89a098c0cb781cb23165f9e21.jpeg)

---

<div class="post-metadata">

**Author:** ![Marc\_D.Shunk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/marc_d.shunk/32/958_2.png) [@Marc\_D.Shunk](https://forum.nachi.org/u/Marc_D.Shunk)\
**Post date:** [June 8, 2007, 12:40am UTC](https://forum.nachi.org/t/moisture-signs-in-panel/17249/2 "2007-06-08T00:40:20Z")

</div>

Either condensation from warm/code air exchange through the meter to panel nipple or the meter hub or weatherhead is leaking. Not irreparable, but well worth documenting.

---

<div class="post-metadata">

**Author:** ![cbrands](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cbrands/32/2086_2.png) [@cbrands](https://forum.nachi.org/u/cbrands)\
**Post date:** [June 8, 2007, 12:47am UTC](https://forum.nachi.org/t/moisture-signs-in-panel/17249/3 "2007-06-08T00:47:39Z")

</div>

> [@Marc D. Shunk](#):
>
> Either condensation from warm/code air exchange through the meter to panel nipple or the meter hub or weatherhead is leaking. Not irreparable, but well worth documenting.

underground service, so weatherhead is out.

but in either situation, it appears an electrician’s evaluation is in order.

panel is in a laundry room with a clothes dryer, gas water heater, and gas furnace.

i wonder if this occured sometime during the last 10 winters. 1996 home.

warm and toasty inside…10 degrees outside.

---

<div class="post-metadata">

**Author:** ![cwillick1](https://avatars.discourse-cdn.com/v4/letter/c/c37758/32.png) [@cwillick1](https://forum.nachi.org/u/cwillick1)\
**Post date:** [June 8, 2007, 1:02am UTC](https://forum.nachi.org/t/moisture-signs-in-panel/17249/4 "2007-06-08T01:02:43Z")

</div>

laundry rooms create moisture that panel is not air tight. i would suspect the moisture is settling inside the panel

---

<div class="post-metadata">

**Author:** ![Marc\_D.Shunk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/marc_d.shunk/32/958_2.png) [@Marc\_D.Shunk](https://forum.nachi.org/u/Marc_D.Shunk)\
**Post date:** [June 8, 2007, 1:08am UTC](https://forum.nachi.org/t/moisture-signs-in-panel/17249/5 "2007-06-08T01:08:00Z")

</div>

> [@cbrands](#):
>
> underground service, so weatherhead is out.
> 
> but in either situation, it appears an electrician’s evaluation is in order.
> 
> panel is in a laundry room with a clothes dryer, gas water heater, and gas furnace.
> 
> i wonder if this occured sometime during the last 10 winters. 1996 home.
> 
> warm and toasty inside…10 degrees outside.

Yeah, probably the nipple needs sealed to prevent air transfer.

---

<div class="post-metadata">

**Author:** ![cbrown1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cbrown1/32/250162_2.png) [@cbrown1](https://forum.nachi.org/u/cbrown1)\
**Post date:** [June 8, 2007, 1:48am UTC](https://forum.nachi.org/t/moisture-signs-in-panel/17249/6 "2007-06-08T01:48:05Z")

</div>

Maybe it is because the meter cans are not flashed on the out side!

---

<div class="post-metadata">

**Author:** ![gnovian](https://avatars.discourse-cdn.com/v4/letter/g/898d66/32.png) [@gnovian](https://forum.nachi.org/u/gnovian)\
**Post date:** [June 8, 2007, 4:19pm UTC](https://forum.nachi.org/t/moisture-signs-in-panel/17249/7 "2007-06-08T16:19:14Z")

</div>

I would recommend it be further evaluated by a licensed electrician.

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [June 8, 2007, 5:30pm UTC](https://forum.nachi.org/t/moisture-signs-in-panel/17249/8 "2007-06-08T17:30:40Z")

</div>

You should really be sealing any raceway that passes from inside to outside. People usually get away with it but you do have the possibility of drawing moisture in from outside to condense or cold air that condenses the moisture on the inside, depending on season.  
This is covered in 300.7

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [June 8, 2007, 5:35pm UTC](https://forum.nachi.org/t/moisture-signs-in-panel/17249/9 "2007-06-08T17:35:44Z")

</div>

here ya go Greg…300.7 for them to view…🙂

\*\*300.7 Raceways Exposed to Different Temperatures.

(A) Sealing. \*\*Where portions of a cable, raceway, or sleeve  
are known to be subjected to different temperatures and  
where condensation is known to be a problem, as in cold  
storage areas of buildings or where passing from the interior  
to the exterior of a building, the raceway or sleeve shall  
be filled with an approved material to prevent the circulation  
of warm air to a colder section of the raceway or  
sleeve. An explosionproof seal shall not be required for this  
purpose.

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [June 8, 2007, 8:29pm UTC](https://forum.nachi.org/t/moisture-signs-in-panel/17249/10 "2007-06-08T20:29:55Z")

</div>

This effect is also why a perfectly sealed (all water tight pipe joints) underground raceway will eventually collect water. Thermal cycling pulls moisture in and it condenses in the cool ground.  
You should probably be using duct seal in them too if you wanted it dry but nobody does. You need wet location wiring anyway.