Hey all, I need help sizing some wire. I don’t have any wire guages and I came across a 20 Amp and 30 Amp breaker in the main panel that both appeared to have the same sized wire. I can’t tell if the wire coming out of the 30 Amp is 10AWG wire or not. I was hoping a seasoned professional may have some insight. My thinking is the wire for the 30 Amp may be too small. They had a 30 Amp breaker in the sub panel and the wires on that breaker were larger than what I’m seeing in the main panel. Thanks for any insights.
What does it service?
They both service AC units.
Do you have photos of the AC unit data plates/labels?
Evening, Anthony. Hope to find you well.
I concur.
Both 20 amp circuit breaker and the 30 amp circuit breaker are terminated with cables that appear the same AWG. All 3 breakers on the right hand side of the sub/remote panel are terminated with cables that appear the same AWG.
Neutral Bus Bar is bonded to the enclosure.
Hope that helps.
Just saying…
The sub panel must be within sight of the exterior AC cabinet and not more than 50’ ft away.
Lockability.
Labeling. The sub panel and the specific breaker must be permanently and clearly labeled as the “Heat Pump Disconnect” or "A/C
Hey Robert, sorry for my confusing things. The 30 Amp in the sub panel feeds the dryer. The photos are of the Main Panel. My concern was the 20 Amp and 30 Amp wiring in the Main Panel.
No worries.
The enclosure with the backfed main breaker?
All 3 breakers on the right hand side of the main enclosure are terminated with cables that appear the same AWG.
The Minimum Circuit Amps (at arrows) tells you the minimum wiring size.
The (underlined) Max breaker tells you the max Breaker value.
These two parameters frequently result in wiring “doesn’t look right”. Also wire sizes are sometimes increased to account for higher drops on longer runs.
To the 30A Breaker question the label shows the Minimum Circuit Amps as 18.1 so the wiring could be lesser gauge than what you would typically expect on a 30A breaker.
I can’t tell from your photos what the installed gauges are but hopefully this helps with a resolution.
The data plate tells you the minimum circuit amps and the maximum breaker size. This will probably be the only time that you will see wire sizes that don’t match the breaker size.
The first photo has a minimum 18.1 amps and a 30 amp max breaker. This means that the electrician could have used either a #12 or a #10 and either a 20-amp, 25-amp or 30-amp 2-pole breaker.
The second has a minimum 11.7 amps and a max 20 amp breaker. The electrician could have used a #14 or #12 and either a 15-amp or 20-anp 2-pole breaker.
What I’ve been able to determin in my research is that having both wires the same is not a problem as long as you go with the larger wire (10-gauge). I figured that since I’ve always considered it relatively ok if the wire was too large for the breaker. The breaker may trip more often, but it’s not going to burn up. In this case, I’m thinking the wire is 12-guage, not 10. However, as I first mentioned, I can’t tell.
My advice is to stay in your own lane. It is not your job to assess adequacy of design. I have been asked too often for a second opinion in situations such as this one. I cannot remember a single occasion when either the conductor or the breaker was improperly sized.
Electrical installations are probably the most highly regulated in all the construction industry. Electricians are better trained than any other construction trade. I am not saying that electricians never make mistakes, but there is a system of checks and balances that rarely fails.
Read and understand your SOP. Don’t try to be something that you are not.
Hey @sfetty , so if I understand you correctly, with the 18.1 minimum requirement on the 30 Amp max breaker I could use a 12-gauge wire since a 12-gauge wire is rated for 20 Amps. Is that correct?
Yes Richard laid out other possible scenarios too.
The system fails when an HVAC installer just re-uses the existing circuit breaker. Time and time again I see new higher SEER condensing units that only require a 15 or 20-amp breaker on an existing 30-amp breaker.
@gwells My SOP states
"Electrical System
(a) The inspector shall:
1. inspect:
(i) the service drop.
(ii) the service entrance conductors, cables, and raceways.
(iii) the service equipment and main disconnects.
(iv) the service grounding.
(v) the interior components of service panels and sub panels.
(vi) the conductors.
(vii) the overcurrent protection devices.
(viii) a representative number of installed lighting fixtures, switches, and receptacles.
(ix) the ground fault circuit interrupters.
2. describe:
(i) the amperage and voltage rating of the service.
(ii) the location of main disconnect(s) and sub panels.
(iii) the wiring methods."
So, I believe I’m in the bounds of the SOP. While I understand “sticking with the SOP” I run my business to provide as much information to my clients as I can. Yes, there are times when I’m outside the SOP, but I’m will to roll those dice. Consider your advice noted.
Hey @rbleich not to slight you in any way, I was just responding to the responses as they came in and Dave’s came in before yours. I appreciate your explaination and providing alternative scenarios. I know I’ll be using what you posted in further inspections. Thanks!
It seems to me that you should report any discrepancies in your scenario according to your SOP.
Although George is well versed on this subject.
Sorry to bother you once again, Anthony.
The above you mention is clearly a limitation.
You admit it. “I can’t tell.”
Write up your report as you see it.
Suspect: Concern of the 20 Amp and 30 Amp wiring in the Main Panel. Unknown AWG.
Refer to a licensed electrical contractor to determine if the ampacity meets the current OCPD operational standards.
As well. I see nothing about Ampacity. Ampacity is the maximum electrical current in amps a wire or cable can safely carry continuously without exceeding its temperature limits.
2. describe:
(i) the amperage and voltage rating of the service.
(ii) the location of main disconnect(s) and sub panels.
(iii) the wiring methods."
Amperage and ampacity are related, but they are not the same thing.
- Amperage is the actual amount of electrical current flowing through a wire or circuit at any given time. Think of this as the actual traffic on a highway.
- Ampacity is the maximum safe amount of current a wire or electrical device can continuously carry without overheating. Think of this as the speed limit or maximum capacity of that highway.