So I ran across this on an inspection. My recommendation is to get it covered immediately. I cannot find a single reason for conductor connections to be open to the elements or accidental contact with a person. Electrician says he doesn’t think he needs to correct anything. This is on the sidewalk that leads to the building entrance, and skirts the edge of the parking lot where people are walking in. Gotta love the beer cup left on top of the conduit direcly above them also.
If those conductors get hot they’re a problem. If they corrode due to the salt water rain here in Florida (less than 1000 LF from the beach) they’re a problem. If some one with nefarious intentions decides to do something to cause issues they’re a problem. There are so many reasons to require them to be covered.
All I can say from Oklahoma is I see bare grounding conductors running to grounding electrodes with bare clamps at every house. New construction are installing grounding busses below the meter for other utilities to connect to.
IMO not a problem as long as they’re UV rated cables, although the corrosion could eventually be an issue and best practice would be to cover them, I wouldn’t consider those grounds any kind of safety issue.
Not an issue unless this is installed in a corrosive environment. Grounding electrode conductors are often installed as open conductors and are permitted by the NEC to be exposed.
I my area I’d want to see them covered,
to reduce the temptation for some idiot to mess with them, removing bolts because they’re high on meth or fentanyl or whatever.