Nested Knockout Problem at Main Panel

I found the outer ring of this nested knockout was completely free and loose. Meaning the cable coming through the clamp is moving. In fact, the cable clamp, seen in the picture below, is resting against the electrical panel. Now I’m no electrician, but I’m pretty sure I need to call this out, and recommend a licensed electrician make repairs to the panel. If the client asks, what is the correct fix for this? I assume this is a fire hazard as well, pests can enter the box, etc. How would ya’ll report on this? I’m in California, if that matters.

I’m not going to comment on the correct fix, because I’m not an electrician. But in my report it would go in my “Improper Workmanship at Panel” narrative. There would be a picture with a brief description of the issue, and a recommendation to consult with a qualified electrical contractor for repair.

3 Likes

That’s a form of eccentric knock out called a tangential KO common on Sq D panels. Not that it matters but is it a Square D panel? Yes you’re correct it needs to be call out and corrected. So what you’re looking at is the SE cable connector is not connected correctly to the panel enclosure because the rings of the eccentric or tangential knock outs are broken.

3 Likes

Thank you for reaffirming where my head was at on this subject.

1 Like

Yes, SquareD, you called it. Thanks for the detail that I can maybe add to my narrative on this one. Appreciate it.