Is it OK to bunch all the neutral and grounds together?
Ken,
You’ve got to be shi+tin me. What a mess…
You have no choice but to…Defer it to a licensed Electrician
I now. I just thought I would share.
How did your report read Ken?
I’m doing right now have not gotten to that part yet. How would you word it?
Simple …
There are a number of concerns within the main electrical panel requiring repair by an licenced electrician. These repairs should be carried out prior to close of title.
Left Image:
The bundle of bare conductors are equipment grounding conductors are not properly terminated on a bonded terminal bar designed to be used for this purpose. I was unable to verify the incorrect connection because of the loosely wrapped tape.
Right Image:
The splicing of the neutral (grounded conductors) using a split bolt in this manner is not recognized, they are required to terminate on their own (isolated from the metal cabinet.
Then have re-inpsected. (Just another way for more income.)
It looks like they’ve got both, EGC and neutrals bundled together in a ball-like fashion. Pathetic…