Hi All,

Found this panel this morning full of debris and rust/corrosion on wiring.

There isn’t a main disconnect breaker for the main service panel. Does the six disconnects rule apply here ?

The panel is a GE TL2020RH if that matters.

 ![IMG_6023](https://global.discourse-cdn.com/internachi/original/3X/e/a/ead744d407a911d761ea2fcc297a64899f8c619a.jpeg)

This panel feeds a sub panel inside the home.

Thanks  
Tom

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [January 30, 2020, 5:18pm UTC](https://forum.nachi.org/t/no-service-disconnect/160711/2 "2020-01-30T17:18:38Z")

</div>

Looks like it does.

---

<div class="post-metadata">

**Author:** ![tcameron](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tcameron/32/175531_2.png) [@tcameron](https://forum.nachi.org/u/tcameron)\
**Post date:** [January 30, 2020, 5:54pm UTC](https://forum.nachi.org/t/no-service-disconnect/160711/3 "2020-01-30T17:54:37Z")

</div>

Thanks Roy…

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [January 30, 2020, 11:09pm UTC](https://forum.nachi.org/t/no-service-disconnect/160711/4 "2020-01-30T23:09:07Z")

</div>

What is the 100 amp breaker for?

---

<div class="post-metadata">

**Author:** ![mparks2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks2/32/172915_2.png) [@mparks2](https://forum.nachi.org/u/mparks2)\
**Post date:** [January 31, 2020, 1:00am UTC](https://forum.nachi.org/t/no-service-disconnect/160711/5 "2020-01-31T01:00:13Z")

</div>

Which one?

---

<div class="post-metadata">

**Author:** ![tcameron](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tcameron/32/175531_2.png) [@tcameron](https://forum.nachi.org/u/tcameron)\
**Post date:** [January 31, 2020, 1:34am UTC](https://forum.nachi.org/t/no-service-disconnect/160711/6 "2020-01-31T01:34:20Z")

</div>

One is for the inside panel, the other for a shed…

---

<div class="post-metadata">

**Author:** ![kshepard](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kshepard/32/59504_2.png) [@kshepard](https://forum.nachi.org/u/kshepard)\
**Post date:** [January 31, 2020, 2:23am UTC](https://forum.nachi.org/t/no-service-disconnect/160711/7 "2020-01-31T02:23:12Z")

</div>

That rule always applies but this panel is not in violation of that. Those two 30-amps are handle-tied so 6 hand movements would shut it all down.

---

<div class="post-metadata">

**Author:** ![rmayo](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmayo/32/59218_2.png) [@rmayo](https://forum.nachi.org/u/rmayo)\
**Post date:** [January 31, 2020, 5:14am UTC](https://forum.nachi.org/t/no-service-disconnect/160711/8 "2020-01-31T05:14:59Z")

</div>

Agree with Kenton

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [January 31, 2020, 2:06pm UTC](https://forum.nachi.org/t/no-service-disconnect/160711/9 "2020-01-31T14:06:59Z")

</div>

Kenton is correct.

> [@tcameron](#):
>
> There isn’t a main disconnect breaker for the main service panel. Does the six disconnects rule apply here ?

Let me rephrase this for you.

“There isn’t a service disconnect. Does the six-throw rule apply here?”

“Main” and “service” are synonymous, so calling something a main service is redundant.

The only clarification I would make to Kentons post is with the statement of “six hand movements.” It’s a common term, but can be misleading.

The rule is **“six or less breakers/switches or sets of breakers/switches.”** In theory, that could be one “hand movement.”