# No step or counter flashing used

**URL:** <https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151>\
**Category:** Roofing Inspections\
**Created:** [October 17, 2019, 12:46am UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151 "2019-10-17T00:46:01Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![smorris1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/smorris1/32/59905_2.png) [@smorris1](https://forum.nachi.org/u/smorris1)\
**Post date:** [October 17, 2019, 12:46am UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/1 "2019-10-17T00:46:01Z")

</div>

These builders are tucking the shingles underneath the brick and filling with mortar instead of using step flashing and counter flashing, I do not like this, I’m seeing daylight showing through into attic where this is being done. Has anyone else seen this and is this an acceptable application for a NEW house  
 ![DSCN8442](https://global.discourse-cdn.com/internachi/original/3X/2/7/27349f0c1b83f6cda5c790d4e3f99da227b24c43.jpeg) ![DSCN8443](https://global.discourse-cdn.com/internachi/original/3X/3/3/335152bfa1468c9d3d55ac1836c7e6760edb8604.jpeg) ![DSCN8516](https://global.discourse-cdn.com/internachi/original/3X/3/4/340fd73c6208231ca7fbb43ef91acce790ea53ae.jpeg)

---

<div class="post-metadata">

**Author:** ![srechkin](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/srechkin/32/180448_2.png) [@srechkin](https://forum.nachi.org/u/srechkin)\
**Post date:** [October 17, 2019, 12:54am UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/2 "2019-10-17T00:54:54Z")

</div>

OSB, missing proper flashing, missing drain for the brick (adhered veneer?), what can go wrong after few years 😃

Not clear if the daylight is at the ridge or sidewall.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [October 17, 2019, 1:49am UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/3 "2019-10-17T01:49:22Z")

</div>

I wonder what they were planning to use for flashing when this roof is eventually torn off and replaced?

---

<div class="post-metadata">

**Author:** ![asleezer](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/asleezer/32/57038_2.png) [@asleezer](https://forum.nachi.org/u/asleezer)\
**Post date:** [October 17, 2019, 3:03am UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/4 "2019-10-17T03:03:30Z")

</div>

Just wrong…

---

<div class="post-metadata">

**Author:** ![cevans](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cevans/32/244194_2.png) [@cevans](https://forum.nachi.org/u/cevans)\
**Post date:** [October 17, 2019, 7:28am UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/5 "2019-10-17T07:28:19Z")

</div>

Acceptability is not the inspector’s prerogative to determine. It’s improper and doesn’t conform to building standards or roofing manufacturer installation standards.

---

<div class="post-metadata">

**Author:** ![mcyr](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mcyr/32/173319_2.png) [@mcyr](https://forum.nachi.org/u/mcyr)\
**Post date:** [October 17, 2019, 12:03pm UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/6 "2019-10-17T12:03:53Z")

</div>

I believe we all know that this is all wrong for obvious reasons and should be noted accordingly. The proper way of execution would look similar to this;  
 ![brick-block-px_figure-1](https://global.discourse-cdn.com/internachi/original/3X/2/0/206433d3742db08ce5c0bc6cfab47e4b5fead525.jpeg) ![7-brick-support-roof-steel-angle](https://global.discourse-cdn.com/internachi/original/3X/8/6/867c7d881b78784e7248978459c2e8da7eb83da6.jpeg)

---

<div class="post-metadata">

**Author:** ![smorris1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/smorris1/32/59905_2.png) [@smorris1](https://forum.nachi.org/u/smorris1)\
**Post date:** [October 17, 2019, 12:20pm UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/7 "2019-10-17T12:20:08Z")

</div>

Thanks for the diagram

---

<div class="post-metadata">

**Author:** ![smorris1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/smorris1/32/59905_2.png) [@smorris1](https://forum.nachi.org/u/smorris1)\
**Post date:** [October 17, 2019, 12:22pm UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/8 "2019-10-17T12:22:01Z")

</div>

I think I saw flashing underneath the brick from inside the attic, but still not proper

---

<div class="post-metadata">

**Author:** ![mcyr](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mcyr/32/173319_2.png) [@mcyr](https://forum.nachi.org/u/mcyr)\
**Post date:** [October 17, 2019, 12:40pm UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/9 "2019-10-17T12:40:47Z")

</div>

You’re welcome.

---

<div class="post-metadata">

**Author:** ![kshepard](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kshepard/32/59504_2.png) [@kshepard](https://forum.nachi.org/u/kshepard)\
**Post date:** [November 4, 2019, 12:23am UTC](https://forum.nachi.org/t/no-step-or-counter-flashing-used/157151/10 "2019-11-04T00:23:48Z")

</div>

You shouldn’t be able to see any flashing from inside the attic (also, you’re asking about a sidewall and your 3rd photo showing daylight is of a ridge condition). Underlayment should extend up the sidewalls about 6". Housewrap should extend down over the top of the underlayment at the sidewalls. Sidewall flashing and counterflashing should be installed as shown in Marcel’s image and typically would be step flashing unless you’re in Florida or a designated high-wind area.