# Number of Romex wires in one hole

**URL:** <https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751>\
**Category:** Electrical Inspections\
**Created:** [October 6, 2007, 7:45pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751 "2007-10-06T19:45:23Z")\
**Posts on this page:** 19\
**Page:** 1

<div class="post-metadata">

**Author:** ![rnapper](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rnapper/32/57038_2.png) [@rnapper](https://forum.nachi.org/u/rnapper)\
**Post date:** [October 6, 2007, 7:45pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/1 "2007-10-06T19:45:23Z")

</div>

Guys need some quick help. How many romex wires can be in one 1 1/2 in hole in a wood top plate. I have a circuit panel inside a garage, new construction, with the hole at the top plate completely stuffed with 12/2 romex. I have attempted to add the picture, but don’t think it went through.

---

<div class="post-metadata">

**Author:** ![Speedy\_Petey](https://avatars.discourse-cdn.com/v4/letter/s/f6c823/32.png) [@Speedy\_Petey](https://forum.nachi.org/u/Speedy_Petey)\
**Post date:** [October 6, 2007, 7:55pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/2 "2007-10-06T19:55:33Z")

</div>

There is no limit. Some might say this is bundling, but I seriously doubt the wires are tightly grouped together for more than 24" in this instance.

---

<div class="post-metadata">

**Author:** ![rnapper](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rnapper/32/57038_2.png) [@rnapper](https://forum.nachi.org/u/rnapper)\
**Post date:** [October 6, 2007, 8:03pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/3 "2007-10-06T20:03:54Z")

</div>

thanks

---

<div class="post-metadata">

**Author:** ![Marc\_D.Shunk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/marc_d.shunk/32/958_2.png) [@Marc\_D.Shunk](https://forum.nachi.org/u/Marc_D.Shunk)\
**Post date:** [October 6, 2007, 10:43pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/4 "2007-10-06T22:43:41Z")

</div>

As many as you can without damaging the jackets of the cables.

---

<div class="post-metadata">

**Author:** ![pdoane](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pdoane/32/909_2.png) [@pdoane](https://forum.nachi.org/u/pdoane)\
**Post date:** [October 7, 2007, 12:38am UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/5 "2007-10-07T00:38:15Z")

</div>

Spock: An illogical approach to electricity does have its advantages on occasion, Captain. :mrgreen:

---

<div class="post-metadata">

**Author:** ![tdietrich1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tdietrich1/32/1561_2.png) [@tdietrich1](https://forum.nachi.org/u/tdietrich1)\
**Post date:** [October 7, 2007, 12:55am UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/6 "2007-10-07T00:55:48Z")

</div>

You need to address derating issues when stuffing holes with cables.

tom

---

<div class="post-metadata">

**Author:** ![Speedy\_Petey](https://avatars.discourse-cdn.com/v4/letter/s/f6c823/32.png) [@Speedy\_Petey](https://forum.nachi.org/u/Speedy_Petey)\
**Post date:** [October 7, 2007, 1:33am UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/7 "2007-10-07T01:33:31Z")

</div>

> [@tdietrich1](#):
>
> You need to address derating issues when stuffing holes with cables.
> 
> tom

Care to support this claim?

---

<div class="post-metadata">

**Author:** ![Marc\_D.Shunk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/marc_d.shunk/32/958_2.png) [@Marc\_D.Shunk](https://forum.nachi.org/u/Marc_D.Shunk)\
**Post date:** [October 7, 2007, 2:36am UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/8 "2007-10-07T02:36:55Z")

</div>

> [@tdietrich1](#):
>
> You need to address derating issues when stuffing holes with cables.
> 
> tom

Electrical Myth #47

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [October 7, 2007, 4:24am UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/9 "2007-10-07T04:24:59Z")

</div>

You only need to derate if they stuff insulation in that hole 334.80. Do you have an energy code?

---

<div class="post-metadata">

**Author:** ![tdietrich1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tdietrich1/32/1561_2.png) [@tdietrich1](https://forum.nachi.org/u/tdietrich1)\
**Post date:** [October 7, 2007, 1:04pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/10 "2007-10-07T13:04:49Z")

</div>

> [@Marc D. Shunk](#):
>
> Electrical Myth #47

Not around here(NE Pa) I’ve been getting word from other electricians that fire inspectors are looking at not just top and bottom plates, but studs and joists. So when drilling hole and running wires, we break our runs up to minimize bundling, and how many #14’s and #12’s go through holes. We can get the order to fire caulk every hole, as they want. The Myth is that this is coming from California, I think it’s being lobbied by fire caulk makers. 😉

tom

---

<div class="post-metadata">

**Author:** ![Marc\_D.Shunk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/marc_d.shunk/32/958_2.png) [@Marc\_D.Shunk](https://forum.nachi.org/u/Marc_D.Shunk)\
**Post date:** [October 7, 2007, 1:41pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/11 "2007-10-07T13:41:13Z")

</div>

> [@tdietrich1](#):
>
> Not around here(NE Pa) I’ve been getting word from other electricians that fire inspectors are looking at not just top and bottom plates, but studs and joists.

Hey, I’m in PA too, and we all work out of the same set of rules. Bundling is not bundling until it’s for 24 inches or more. I’d appeal the red tag for multiple cables in a top or bottom plate in a heartbeat, and I’d have to win. The code text is very clear on that matter.

---

<div class="post-metadata">

**Author:** ![tdietrich1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tdietrich1/32/1561_2.png) [@tdietrich1](https://forum.nachi.org/u/tdietrich1)\
**Post date:** [October 7, 2007, 2:19pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/12 "2007-10-07T14:19:20Z")

</div>

> [@Marc D. Shunk](#):
>
> The code text is very clear on that matter.

So is 90.4

So now just incase, I drill an extra hole everytime I get to 9 cc’s 14# and 12# and 6 for #10.

tom

---

<div class="post-metadata">

**Author:** ![Marc\_D.Shunk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/marc_d.shunk/32/958_2.png) [@Marc\_D.Shunk](https://forum.nachi.org/u/Marc_D.Shunk)\
**Post date:** [October 7, 2007, 2:39pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/13 "2007-10-07T14:39:38Z")

</div>

> [@tdietrich1](#):
>
> So is 90.4

90.4 isn’t permission to make stuff up.

---

<div class="post-metadata">

**Author:** ![Speedy\_Petey](https://avatars.discourse-cdn.com/v4/letter/s/f6c823/32.png) [@Speedy\_Petey](https://forum.nachi.org/u/Speedy_Petey)\
**Post date:** [October 7, 2007, 2:48pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/14 "2007-10-07T14:48:27Z")

</div>

> [@Marc D. Shunk](#):
>
> 90.4 isn’t permission to make stuff up.

You better beileve it!

---

<div class="post-metadata">

**Author:** ![Speedy\_Petey](https://avatars.discourse-cdn.com/v4/letter/s/f6c823/32.png) [@Speedy\_Petey](https://forum.nachi.org/u/Speedy_Petey)\
**Post date:** [October 7, 2007, 2:57pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/15 "2007-10-07T14:57:25Z")

</div>

The rule about derating cables through firestopped holes is new in 2005. This is _ONLY_ for holes that are (or to be) firestopped.

So here again we are caught with the _“when was the hosue built”_ problem and\* “what code was it under when it was built”\*.

---

<div class="post-metadata">

**Author:** ![tdietrich1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tdietrich1/32/1561_2.png) [@tdietrich1](https://forum.nachi.org/u/tdietrich1)\
**Post date:** [October 7, 2007, 3:07pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/16 "2007-10-07T15:07:04Z")

</div>

Good points Speedy,

I’m addressing both worse case, if I get hounded by the fire inspector, and then by the electrical inspector, so commenting specific on my work.

However, the OP says New Construction, Russel is in Texas (they adopted the 2005 NEC about the same time we [Pa]), through a TOP Plate(so fire caulking[or other method] should be required if not by fire codes, the NEC implied), so 334.80 seems to apply here(in this post).

Seems the term “bundling” is open for discussion, it was mentioned a distance was required, but I was instructed by an inspector, the actual text for derating[related 310] is ‘bundled more than 24"’ if just ‘bundled’ is mentioned, no distance is implied. So any bundling is bundling [related to 334], therefore bound by a hole in wood is bundling.

tom

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [October 8, 2007, 12:44pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/17 "2007-10-08T12:44:48Z")

</div>

Ironically enough when you do get involved with the derating of the NM Cable for the examples you all are giving…and end up using 90 degree for derating it in most cases with 14 AWG and 12 AWG wont effect the ampacity.

Basically if we had (4) 14-2 NM Cables thru the firestop…(4) current carry conductors so apply 310.15(b)(2)(a) and 80% would still be fine…for 15A breaker…without getting too detailed in it…so really it is not nearly an issue as other factors…

For example…how many inspectors make electricians adjust the ampacity in areas where the attics get VERY HOT…again without doing the math would it matter much on smaller NM Cable…probably not.

Where more than two NM cables containing two or  
more current-carrying conductors are bundled together and  
pass through wood framing that is to be fire- or draftstopped  
using thermal insulation or sealing foam, the allowable  
ampacity of each conductor shall be adjusted in  
accordance with Table 310.15(B)(2)(a).

Now…I really dont like how this is written…I had one argument a 14-2 contains only (1) current carry conductor and because how that reads it says…more than (2) NM Cables containing two or more current-carry conductors…but a 14-2 only has (1) current carry conductor…lol…I know…I know…but thats how debates get going.

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [October 8, 2007, 3:54pm UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/18 "2007-10-08T15:54:52Z")

</div>

In residential you really don’t have that much firestopping, it is mostly draft stopping. That is why I asked about your “energy code”. Generally the only fire rated assembly in R3 is a ceiling over a garage if there is living space above. Some local codes also want 1hr between a garage and the rooms next to it but that is not how the IRC/Florida Building Codes read. It is assumed draft stopping also slows the spread of fire products and thus does slow the spread of fire. If this is that spray in foam YMMV since it is flammable. They are taking a long hard look at that in Florida as we speak.  
For the purposes of 334.80 it is a distinction without a difference. If the hole has insulation in it you must look at derating. It really just gets back to the original question. How many wires are in one hole. This pretty much tells the installer not to jam all the Romex in one big hole. Drill several smaller ones.

---

<div class="post-metadata">

**Author:** ![brian\_winkle](https://avatars.discourse-cdn.com/v4/letter/b/f0a364/32.png) [@brian\_winkle](https://forum.nachi.org/u/brian_winkle)\
**Post date:** [October 9, 2007, 5:32am UTC](https://forum.nachi.org/t/number-of-romex-wires-in-one-hole/20751/19 "2007-10-09T05:32:21Z")

</div>

Here in Pima County, Arizona fire caulking is now required on all top plate penetrations for residential. And yes, de rating in these holes is being enforced. We are buying smaller bits and drilling more holes.