# Odd Installation for tankless water heater

**URL:** <https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204>\
**Category:** Plumbing Inspections\
**Created:** [February 3, 2025, 11:55pm UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204 "2025-02-03T23:55:00Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![yzhang](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/yzhang/32/57038_2.png) [@yzhang](https://forum.nachi.org/u/yzhang)\
**Post date:** [February 3, 2025, 11:55pm UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/1 "2025-02-03T23:55:00Z")

</div>

![20250130-46](https://global.discourse-cdn.com/internachi/original/4X/d/8/7/d873b68f3ed8a24802b7be80263e5f85e5fa8135.jpeg)

This is the first time I’ve ever seen the water pipes for the tankless water heater installed this way on a new construction. Usually, the hot and cold water pipes are completely separate, but at this house they are connected by the valve in the middle. There is also typically a separate shut off valve on the cold water pipe right after it comes out of the drywall, but none here. This is a rinnai RE180i BTW. Not really sure what they are trying to do here? Any ideas?

---

<div class="post-metadata">

**Author:** ![ddagostino](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ddagostino/32/60136_2.png) [@ddagostino](https://forum.nachi.org/u/ddagostino)\
**Post date:** [February 4, 2025, 12:09am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/2 "2025-02-04T00:09:50Z")

</div>

Looks like a bypass valve.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [February 4, 2025, 12:38am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/3 "2025-02-04T00:38:22Z")

</div>

> [@ddagostino](#):
>
> Looks like a bypass valve

Agree, but not sure why.

---

<div class="post-metadata">

**Author:** ![mroberts21](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mroberts21/32/285622_2.png) [@mroberts21](https://forum.nachi.org/u/mroberts21)\
**Post date:** [February 4, 2025, 2:05am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/4 "2025-02-04T02:05:50Z")

</div>

> [@lkage](#):
>
> Agree, but not sure why.

Can you do the flush or a full service without interrupting water in the home? Yes, I realize you’d get no hot.

---

<div class="post-metadata">

**Author:** ![ruecker](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ruecker/32/357170_2.png) [@ruecker](https://forum.nachi.org/u/ruecker)\
**Post date:** [February 4, 2025, 2:12am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/5 "2025-02-04T02:12:27Z")

</div>

A poor man’s mixing valve? Not sure why you would do it on a tankless, but you never know.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [February 4, 2025, 2:13am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/6 "2025-02-04T02:13:52Z")

</div>

> [@ruecker](#):
>
> A poor man’s mixing valve?

Or part of a recirculating system? 🤷

---

<div class="post-metadata">

**Author:** ![bnesbitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bnesbitt/32/56701_2.png) [@bnesbitt](https://forum.nachi.org/u/bnesbitt)\
**Post date:** [February 4, 2025, 2:33am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/7 "2025-02-04T02:33:49Z")

</div>

Looks like a system that does space heating plus domestic, with one tankless, where that bypass is used. Also looks like a relatively small gas line for tankless. More pictures?

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [February 4, 2025, 2:50am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/8 "2025-02-04T02:50:00Z")

</div>

> [@yzhang](#):
>
> rinnai RE180i BTW

Images further back please, Yu.

---

<div class="post-metadata">

**Author:** ![yzhang](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/yzhang/32/57038_2.png) [@yzhang](https://forum.nachi.org/u/yzhang)\
**Post date:** [February 4, 2025, 4:27am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/9 "2025-02-04T04:27:03Z")

</div>

> [@ddagostino](#):
>
> Looks like a bypass valve.

Thought about that too..but couldn’t continue down that line of thinking because what are we really bypassing here though? yea its odd.

> [@mroberts21](#):
>
> Can you do the flush or a full service without interrupting water in the home? Yes, I realize you’d get no hot.

yea..normally you get no water coming out on the hot side if you shut water off just to the water heater for service. Now you get cold water coming out the hot side for the plumbing in the house? Not sure that really helps that much, unless people like taking cold showers?

> [@bnesbitt](#):
>
> Looks like a system that does space heating plus domestic, with one tankless, where that bypass is used. Also looks like a relatively small gas line for tankless. More pictures?

Nope, not that fancy. Only a single tankless for the hot water in the house. House has a gas furnace/electric AC for heating/cooling purposes.

> [@bcawhern1](#):
>
> Or part of a recirculating system? 🤷

Nope, no recirculating system no pump. No water softener. That’s why it makes no sense to me.

> [@ryoung7](#):
>
> Images further back please, Yu.

 ![20250130-42](https://global.discourse-cdn.com/internachi/original/4X/f/8/9/f89b874460d5c1e8ae338f98ec33c839b86a2a45.jpeg)

This is as far as I got in the garage. Left of the water heater is the main water shut off to the house, PRV, and shut off for exterior hose bibs.

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [February 4, 2025, 4:42am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/10 "2025-02-04T04:42:30Z")

</div>

Thank you. Much appreciated.

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [February 4, 2025, 11:46am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/11 "2025-02-04T11:46:03Z")

</div>

The bypass is probably built in at the request of the client to winterize the plumbing system.

---

<div class="post-metadata">

**Author:** ![eluke](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/eluke/32/177534_2.png) [@eluke](https://forum.nachi.org/u/eluke)\
**Post date:** [February 4, 2025, 3:33pm UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/12 "2025-02-04T15:33:29Z")

</div>

I have a tank less in my home, I assume it is for flushing out the heater without shutting down the whole house and just flushing the unit.

---

<div class="post-metadata">

**Author:** ![bnesbitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bnesbitt/32/56701_2.png) [@bnesbitt](https://forum.nachi.org/u/bnesbitt)\
**Post date:** [February 4, 2025, 4:16pm UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/13 "2025-02-04T16:16:49Z")

</div>

> [@yzhang](#):
>
> This is as far as I got in the garage.

Where does that condensate line go? Remember condensate eats through everything, but plants like it.

---

<div class="post-metadata">

**Author:** ![yzhang](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/yzhang/32/57038_2.png) [@yzhang](https://forum.nachi.org/u/yzhang)\
**Post date:** [February 4, 2025, 4:31pm UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/14 "2025-02-04T16:31:00Z")

</div>

That’s just the pressure relief pipe run to the floor. Not a condensing unit

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [February 4, 2025, 5:03pm UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/15 "2025-02-04T17:03:34Z")

</div>

Looks good from here.

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [February 4, 2025, 8:22pm UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/16 "2025-02-04T20:22:10Z")

</div>

> [@bnesbitt](#):
>
> Where does that condensate line go?

Where do you see a condensate line?

---

<div class="post-metadata">

**Author:** ![bnesbitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bnesbitt/32/56701_2.png) [@bnesbitt](https://forum.nachi.org/u/bnesbitt)\
**Post date:** [February 4, 2025, 8:40pm UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/17 "2025-02-04T20:40:01Z")

</div>

> [@mwilles](#):
>
> Where do you see a condensate line?

The OP stated that’s a TPR instead. I had thought condensate, based purely on the type of pipe used. Thus my question switches to the usual technical concerns about TPR in plastic.

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [February 4, 2025, 11:58pm UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/18 "2025-02-04T23:58:53Z")

</div>

> [@bnesbitt](#):
>
> concerns about TPR in plastic

What’s your concern?

---

<div class="post-metadata">

**Author:** ![bnesbitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bnesbitt/32/56701_2.png) [@bnesbitt](https://forum.nachi.org/u/bnesbitt)\
**Post date:** [February 5, 2025, 12:13am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/19 "2025-02-05T00:13:20Z")

</div>

> [@mwilles](#):
>
> What’s your concern?

It’s not my concern, though it commonly comes up here. The plastic pipe is not rated for the temperature of the potential outflow (212F +) from a malfunctioning water heater.

---

<div class="post-metadata">

**Author:** ![mgoldenberg](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgoldenberg/32/89265_2.png) [@mgoldenberg](https://forum.nachi.org/u/mgoldenberg)\
**Post date:** [February 5, 2025, 12:19am UTC](https://forum.nachi.org/t/odd-installation-for-tankless-water-heater/252204/20 "2025-02-05T00:19:35Z")

</div>

> [@bnesbitt](#):
>
> The plastic pipe is not rated for the temperature of the potential outflow

It is CPVC OK  
What say you @mwilles