I inspected a 2001 built home. There was an oily substance dripping from the ungrounded wires connected to the breakers. There was no oil on the neutral or ground wires or anywhere else in the panel. Could this be the result of the wire sheathing breaking down? Thanks.
Personally, I’ve never seen it.
Here’s what AI has to say about it.
The presence of an oily substance dripping from wires in an electrical panel is typically caused by plasticizer migration, a chemical breakdown of the wire’s insulation. This is most common in older PVC-insulated cables where the additives used to keep the plastic flexible leach out over time.
Primary Causes
- Plasticizer Leaching: PVC insulation contains plasticizers to make it pliable. Over decades, or when exposed to heat and humidity, these chemicals can separate from the polymer and “wick” along the copper strands, eventually dripping out at connection points.
- “Green Goo” Reaction: If the dripping liquid is green and sticky, it is the plasticizer reacting with the copper conductor. This is frequently seen in wiring from the mid-1960s to early 1980s.
- Breakdown of Lubricants: In some cases, the “oil” is actually grease from inside a circuit breaker that has liquified due to excessive heat or age.
- Anti-Oxidation Paste: If you have aluminum wiring, the substance may be Noalox or a similar anti-corrosive paste that has separated or was over-applied.
- External Wicking: Liquids from a source at the other end of the wire—such as oil from a leaking transformer or even water entering through a poorly sealed exterior meter—can travel inside the wire jacket via capillary action and drip into the panel.
Safety and Risks
- Fire Hazard: While the oil itself is often non-conductive, its presence indicates the insulation is becoming brittle and prone to cracking. It can also seep into breakers, causing mechanical failure or poor electrical contact that leads to overheating.
- Compromised Connections: The oil acts as a lubricant, which may cause wire terminations to slip or loosen over time.
- Toxicity: Older residues (pre-1979) may potentially contain PCBs (polychlorinated biphenyls), which are toxic; avoid direct skin contact.
Recommended Actions
- Professional Inspection: Have a licensed electrician assess the panel to determine if the wire insulation is still safe or if it requires a partial or full rewire.
- Avoid Cleaning: Do not attempt to wipe the wires while they are energized. Cleaning the residue does not stop the underlying chemical breakdown.
- Check for Overloading: Since heat accelerates this process, ensure your circuits are not consistently overloaded.
Thanks. I had already decided to refer it. I had never seen it before either. I appreciate the response.
What did it taste like?
Was there a conduit?
No there wasn’t.
Note: Suspect oily substance on ground conductors situated in the panel board.
Although professional-grade wire pulling lubricants can be common for pulling circuit cables through conduit, to reduce friction and conductor tension. There were no conduit behind the panel board.
Recommend a licensed electrical contractor further review the oily substance on circuit cables and make any recommendations therein.
Limitations. Visible Circuit cables behind the panel board enclosure.
Would a non-professional be able to turn on a light switch to review if the cables were conducting?
Sorry. Thanks Jeff.
Should have paid attention to my post instead of rushing it out.
Are all the circuits NM conductors?
You beat me to it …![]()
Yes they were
Olive oil. I took some for my salad.
Oh man, I can see the look on the homeowner’s face already when the electrician says their wiring plasticizer fluid is empty and the home needs to be rewired. ![]()
1001 on the list of things an electrician never thought they’d say, LOL ![]()