**Originally Posted By: mpettitt**  
**This post was automatically imported from our archived forum.**

* * *
  
1983 2 x 4 wood framed central florida home on slab, 1800 sq. ft. living, dual pane windows, 4 inches of cellulose insulation in attic. This home has a 4 ton A/C split system, 97 model (not a heat pump, just A/C with electric heat). My thoughts were always 1 ton for every 500 to 600 sq. ft. which would put it at about a 3 or 3.5 ton which is what I’m use to seeing. Any thoughts on this and if oversized how I might word it in the report.  
  
  
Thanks again, Mike  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [November 17, 2005, 12:00am UTC](https://forum.nachi.org/t/oversized-a-c/192919/2 "2005-11-17T00:00:00Z")

</div>

**Originally Posted By: bking**  
**This post was automatically imported from our archived forum.**

* * *
  
It may be oversized but not an obvious defect without exhaustive testing therefore it is not in your best interest to stir up an issue without being convinced without a doubt.  
  

  
Just state the size and the typical size (if you want to) in the report and do not list it in the summary as a problem unless you honestly believe it is.  

* * *
  

--  
[www.BAKingHomeInspections.com](http://www.BAKingHomeInspections.com)

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [November 19, 2005, 12:00am UTC](https://forum.nachi.org/t/oversized-a-c/192919/3 "2005-11-19T00:00:00Z")

</div>

**Originally Posted By: dandersen**  
**This post was automatically imported from our archived forum.**

* * *
  
Got a pic of the house?  
  

  
In the open, or under a hammock?  
How much glass?  
  
Ton per sq. ft. is a "wild **a$%** guess" at best.   
  
However, this IS a big defect when the unit does not handle the latent heat and mold grown on everything in the house.  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [November 19, 2005, 12:00am UTC](https://forum.nachi.org/t/oversized-a-c/192919/4 "2005-11-19T00:00:00Z")

</div>

**Originally Posted By: dvalley**  
**This post was automatically imported from our archived forum.**

* * *
  
It’s not an HI responsibility but here’s a little asistance.  
  

  
[![](upload://me4MtRe3nGBGET8vgZY42XGj9kl.gif)](http://www.a-wall.com/ACcalc.php)  

* * *
  

--  
David Valley  
MAB Member  
  
Massachusetts Certified Home Inspections  
[http://www.masscertified.com](http://www.masscertified.com)  
  
"Some cause happiness wherever they go; others, whenever they go."

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [November 19, 2005, 12:00am UTC](https://forum.nachi.org/t/oversized-a-c/192919/5 "2005-11-19T00:00:00Z")

</div>

**Originally Posted By: Monte Lunde**  
**This post was automatically imported from our archived forum.**

* * *
  
Mike,  
  

  
I hope that you have a bigger concern with only 4 inches of cellulose insulation in attic.  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [November 28, 2005, 12:00am UTC](https://forum.nachi.org/t/oversized-a-c/192919/6 "2005-11-28T00:00:00Z")

</div>

**Originally Posted By: jfeig**  
**This post was automatically imported from our archived forum.**

* * *
  
The only real problems with a way oversize AC system is that it will be less energy efficient and less able to keep the humidity low without making the space to cold.  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [November 29, 2005, 12:00am UTC](https://forum.nachi.org/t/oversized-a-c/192919/7 "2005-11-29T00:00:00Z")

</div>

**Originally Posted By: Blaine Wiley**  
**This post was automatically imported from our archived forum.**

* * *
  
The HVAC contractors around here use 400 to 500 sq. ft. as a “rule of thumb”, so at 4 tons you’re in the ball park.  
  

  
Did the home have vaulted or high ceilings?  
  
Monte: We seldom see more than 4" of any kind of insulation on homes built prior to the 90's! And we still build with single pane windows!!!! lol  

* * *