Does anyone know when the requirement for T.P.R. valves to be 6 inches from the ground went into effect? I usually only see it on newer homes.
it doesnt matter how old the house is , if it doesnt terminate near the floor recommend a repair for safety…
I agree with James and it was likely put into effect before that water heater was manufactured ![]()
Within 6 inches. not 6 inches.
“Terminate not more than 6 inches (152 mm) and not less than two times the discharge pipe diameter above the floor or waste receptor flood level rim.”
There are other rules as well. If you are going to quote code, do not paraphrase. It can get you in trouble. words matter.
P2804.6.1Requirements for discharge pipe.
The discharge piping serving a pressure-relief valve, temperature-relief valve or combination valve shall:
- Not be directly connected to the drainage system.
- Discharge through an air gap located in the same room as the water heater.
- Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
- Serve a single relief device and shall not connect to piping serving any other relief device or equipment.
- Discharge to the floor, to the pan serving the water heater or storage tank, to a waste receptor or to the outdoors.
- Discharge in a manner that does not cause personal injury or structural damage.
- Discharge to a termination point that is readily observable by the building occupants.
- Not be trapped.
- Be installed to flow by gravity.
- Terminate not more than 6 inches (152 mm) and not less than two times the discharge pipe diameter above the floor or waste receptor flood level rim.
- Not have a threaded connection at the end of the piping.
- Not have valves or tee fittings.
- Be constructed of those materials indicated in Section P2906.5 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.
- Be one nominal size larger than the size of the relief-valve outlet, where the relief-valve discharge piping is installed with insert fittings. The outlet end of such tubing shall be fastened in place.
Thanks for the replies. I guess it is a mystery as to when the requirement for the T.P.R. valve to be within 6 inches of the ground went into effect.
Do you mean which IRC, UPC or IPC code cycle? Or manufacturer installation requirements? Or local/state code requirements?
How about giving us “the rest of the story”? When we get these type of questions/comments about our replies… there is ALWAYS more to the story that we are never told until pushed for!!
(My gut says this is related to the “Garage - Water Heater height off floor” requirement)!
I am referring to building code. I am curious as to when the change was made to the building code.
Which building code? Which state?
Sorry, I forgot this is not a local forum. I am in Phoenix,
Arizona and presume it would be part of the plumbing code. I just was wanting to know approximately what year the requirement for the T.P.R valve discharge was requried to be within 6 inches of the ground.