Yesterday I observed this on an inspection. The pex pipes are connecting directly to the heater. I thought that 18” of copper was needed first. I was looking for input on whether it is a defect or not? Since this is new construction and it is a GE smart heat pump water heater.
John
what is your reasoning for copper being needed in this scenario?
Will the pex degrade or melt in your scenario?
it doesn’t have to be copper. But I remember from my classes hearing that pex shouldn’t connect directly to the water heater because it could melt. I’m just trying to learn more.
That is correct, but not in the picture you posted. I’m trying to make you think this through so that you can learn.
What is the main difference between your picture and this one?
Start by reading the manufacturer’s installation instructions. Page 25
https://static.pcrichard.com/docs/PH50S10BPY_Specifications-Sheet_01.pdf
How much copper, I believe, varies by state.
But in many/most places, the code is 18"
The main difference would be the hot flue in that picture. I now realize that the pex is ok because it’s was an electric water heater, which doesn’t need a flue or produce as much heat.
…the manufacturer doesn’t prohibit it.
If that is PEX at the TPR valve, it should be secured.
I don’t see a problem with this water heater installation with the exception of the TPR valve pipe. It should be 1 inch PEX if you follow the IRC
Agreed. I will add to your comment. GA follows IPC 2024 and this is the statement.
Be one nominal size larger than the size of the relief valve outlet, where the relief valve discharge piping is installed with insert fittings. The outlet end of such tubing shall be fastened in place.
Maybe you meant Chapter 5 Water Heaters: Georgia Plumbing Code 2024 | UpCodes
You’re right. Georgia has some amendments. Went info effect Jan. 1, 2026
Georgia Plumbing Code 2024 Adopts With Amendments
International Plumbing Code 2024 (IPC 2024)
and Your jourisdiction may have something to say about it also, I live in a 2018 build with an electric water heater and they were required to stub out copper from the tank before changing to pex…location matters…
Yes it does. Several locals in my area also require 12 to 18-inch metal pipe on electric WH.
This is a requirement on gas water heaters with a flue.
I believe you’re right…The code doesn’t seem to differentiate between gas or electric water heaters in that requirement. It also seems to apply to tankless water heaters. On older homes it likely not a big deal if it’s an electric water heater but on new construction it seems to be a fair call out especially on a gas water heater…that flue pipe can get hot and melt the pex…
Look in PEX manufacturer installation instructions for that prohibition.