# Plumbing at disposal

**URL:** <https://forum.nachi.org/t/plumbing-at-disposal/61088>\
**Category:** Plumbing Inspections\
**Created:** [July 20, 2011, 11:32pm UTC](https://forum.nachi.org/t/plumbing-at-disposal/61088 "2011-07-20T23:32:00Z")\
**Posts on this page:** 8\
**Page:** 1

<div class="post-metadata">

**Author:** ![scroenne](https://avatars.discourse-cdn.com/v4/letter/s/8c91f0/32.png) [@scroenne](https://forum.nachi.org/u/scroenne)\
**Post date:** [July 20, 2011, 11:32pm UTC](https://forum.nachi.org/t/plumbing-at-disposal/61088/1 "2011-07-20T23:32:00Z")

</div>

At my inspection today, I have the drain line coming out of the disposal dropping down into a P-trap configuration made out of pressure fitted piping. The pipe then rises 4" to a T fitting to meet up with the other bowl drain line and then travels through an approved p-trap right next to it and then into the horizontal pipe to the wall drain. There are two P-traps side by side. It doesn’t look right to me. Sorry no picture. Thoughts?

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [July 20, 2011, 11:38pm UTC](https://forum.nachi.org/t/plumbing-at-disposal/61088/2 "2011-07-20T23:38:27Z")

</div>

A pic would sure help. As long as each fixture only drains through ONE trap, it is acceptable (in my area). As for the materials… what are you calling a “pressure fitting”? Also unclear on the fall/rise of the waste lines.

Do you not take pics of defects or concerns?

---

<div class="post-metadata">

**Author:** ![roconnor](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/roconnor/32/1762_2.png) [@roconnor](https://forum.nachi.org/u/roconnor)\
**Post date:** [July 21, 2011, 4:17am UTC](https://forum.nachi.org/t/plumbing-at-disposal/61088/3 "2011-07-21T04:17:09Z")

</div>

> [@jjonas](#):
>
> As long as each fixture only drains through ONE trap, it is acceptable (in my area).

I assume your area is on UPC based codes … but most areas are on IRC based codes that permit 2 fixtures on one trap and trap arm/vent.

It’s hard to tell from the description, but it sounds like that may be a double traped installation, which would not be acceptable. That looks like this …  
.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [July 21, 2011, 4:23am UTC](https://forum.nachi.org/t/plumbing-at-disposal/61088/4 "2011-07-21T04:23:35Z")

</div>

> [@roconnor](#):
>
> I assume your area is on UPC based codes … but most areas are on IRC based codes that permit 2 fixtures on one trap and trap arm/vent.
> 
> It’s hard to tell from the description, but it sounds like that may be a double traped installation, which would not be acceptable. That looks like this …  
> .

Uhh… Isn’t that what I said?

> [@](#):
>
> Originally Posted by **jjonas** [http://nachi.cachefly.net/forum/images/2006/buttons/viewpost.gif](http://www.nachi.org/forum/f22/plumbing-disposal-62685/#post804814)  
> _As long as each fixture only drains through ONE trap, it is acceptable (in my area)._

I didn’t say each fixture must drain through a seperate trap.

Musta been the accent! 😉

---

<div class="post-metadata">

**Author:** ![roconnor](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/roconnor/32/1762_2.png) [@roconnor](https://forum.nachi.org/u/roconnor)\
**Post date:** [July 21, 2011, 4:27am UTC](https://forum.nachi.org/t/plumbing-at-disposal/61088/5 "2011-07-21T04:27:49Z")

</div>

> [@jjonas](#):
>
> … **each** fixture only drains through **ONE** trap, it is acceptable …

I took that to mean your area required a trap for each fixture (two fixtures and two traps) … my misunderstanding if that wasn’t the intent … 😉

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [July 21, 2011, 4:29am UTC](https://forum.nachi.org/t/plumbing-at-disposal/61088/6 "2011-07-21T04:29:53Z")

</div>

> [@roconnor](#):
>
> I took that to mean your area required a trap for each fixture (two fixtures and two traps) … my misunderstanding if that wasn’t the intent … 😉

Like I said, musta been the accent. My intent was to indicate that a fixture is not allowed to drain through more than one trap. Better? 😉

---

<div class="post-metadata">

**Author:** ![scroenne](https://avatars.discourse-cdn.com/v4/letter/s/8c91f0/32.png) [@scroenne](https://forum.nachi.org/u/scroenne)\
**Post date:** [July 21, 2011, 12:06pm UTC](https://forum.nachi.org/t/plumbing-at-disposal/61088/7 "2011-07-21T12:06:16Z")

</div>

Thanks guys, I take tons of pictures to put in my reports. I was not able to load the picture for this application. The pipe leaves the disposal downward 4" over 4" up 4" to a T fitting. Next to that is the P-trap that goes to the wall drain. When looking at it, it looks like 2 P-traps right next to each other. Food from the disposal travels through 2 P-traps then to the horizontal drain that leads to the wall. When I tested the right drain, (disposal side) I could see water make its way to the left drain. It just doesn’t look right to me. It doesn’t look like a standard set up when installing a disposal. Stan

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [July 21, 2011, 2:36pm UTC](https://forum.nachi.org/t/plumbing-at-disposal/61088/8 "2011-07-21T14:36:10Z")

</div>

> [@scroenne](#):
>
> Food from the disposal travels through 2 P-traps then to the horizontal drain that leads to the wall.

This makes it wrong under any model code.