120v lights may not have been allowed in the old Sarasota/Charlotte addendums but they all went away when we adopted the Florida Unified Building Code.
Florida, the whole state, is on the NEC, unmodified. The NEC allows 120v lights.
Gee whiz link.
http://www2.iccsafe.org/florida_building_code/
Pool code is chapter 1 article 424
As for the pump. You need the twist lock and GFCI if the receptacle is within 5' of the tub. You are right about the 3' cord but it can be a regular plug..
*** 2002 NEC
680.21(A)(5) Cord-and-Plug Connections. Pool-associated motors shall be permitted to employ cord-and-plug connections. The flexible cord shall not exceed 900 mm (3 ft) in length. The flexible cord shall include an equipment grounding conductor sized in accordance with 250.122 and shall terminate in a grounding-type attachment plug.
680.22 Area Lighting, Receptacles, and Equipment.
(A) Receptacles.
(1) Circulation and Sanitation System, Location. Receptacles that provide power for water-pump motors or for other loads directly related to the circulation and sanitation system shall be located at least 3.0 m (10 ft) from the inside walls of the pool, or not less than 1.5 m (5 ft) from the inside walls of the pool if they meet all of the following conditions:
(1) Consist of single receptacles
(2) Employ a locking configuration
(3) Are of the grounding type
(4) Have GFCI protection
(5) GFCI Protection. All 125-volt receptacles located within 6.0 m (20 ft) of the inside walls of a pool or fountain shall be protected by a ground-fault circuit interrupter. Receptacles that supply pool pump motors and that are rated 15 or 20 amperes, 120 volt through 240 volts, single phase, shall be provided with GFCI protection.
As long as the receptacle for your pump is 20' from the pool or inside an enclosure, it does not need GFCI.
If you are looking at above ground pools these probably come into play but I would think most inground owners want to install the pump away from the pool so you don't hear it.