# Pool grounding?

**URL:** <https://forum.nachi.org/t/pool-grounding/184444>\
**Category:** Public Archive\
**Created:** [March 15, 2005, 12:00am UTC](https://forum.nachi.org/t/pool-grounding/184444 "2005-03-15T00:00:00Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [March 15, 2005, 12:00am UTC](https://forum.nachi.org/t/pool-grounding/184444/1 "2005-03-15T00:00:00Z")

</div>

**Originally Posted By: waksell**  
**This post was automatically imported from our archived forum.**

* * *
  
I inspected an above ground, metal structure pool the other day. The pump had a 20’ cord [3 prong] plugged into a GFI. Shouldn’t the pump have a seperate ground wire to a hose bib or a ground rod? And shouldn’t the pool structure be grounded?  

* * *

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [March 15, 2005, 12:00am UTC](https://forum.nachi.org/t/pool-grounding/184444/2 "2005-03-15T00:00:00Z")

</div>

**Originally Posted By: jpope**  
**This post was automatically imported from our archived forum.**

* * *
  
Bonded is the word you’re looking for.  
  
  
Yes, all components should be bonded.  

* * *
  

--  
Jeff Pope  
JPI Home Inspection Service  
"At JPI, we'll help you look better"  
(661) 212-0738

---

<div class="post-metadata">

**Author:** ![system](https://global.discourse-cdn.com/internachi/original/3X/d/f/df7ced6a9ca05e7c93fa949dfc12a8c10d06c887.png) [@system](https://forum.nachi.org/u/system)\
**Post date:** [March 15, 2005, 12:00am UTC](https://forum.nachi.org/t/pool-grounding/184444/3 "2005-03-15T00:00:00Z")

</div>

**Originally Posted By: rdzierba**  
**This post was automatically imported from our archived forum.**

* * *
  
ICC E4102.2 Flexible Cords states;  
  
  
“…for other than storable pools, the flexible cord shall not exceed 3 feet in length…”  
  
  
There is also a requirement that the receptacle can only be from 5-10 feet away from the pool wall… .  

* * *