Question about barometric dampers (commercial building)

If a mechanical room has a barometric damper on the flue stack or chimney. Does that mean there is no need for and exhaust and fresh air system?

In short, no.
A barometric damper on the flue only prevents outside air from blowing down through the flue and into the mechanical room.

1 Like

And a barometric backdraft damper performs no heat recovery, like a heat recovery ventilation system would. It’s basically a window that opens when the pressure in the building is lower than outside. It does help reduce radon and CO though.

1 Like

No. The damper regulates chimney draft.
Still require sufficient combustion air.

A barometric damper on a flue stack regulates chimney draft. Opening wider to let in room air when the pull becomes too strong, preventing excessive heat loss, flame impingement, and CO risks by ensuring consistent negative pressure for efficient, safe combustion, often found on oil/gas boilers with tall stacks.

1 Like

Perplexed by that statement. Barometric damper reduce redon.
Barometric dampers are used in combustion related furnaces and boilers flues to regulate draft of combusted gases. The balancing damper balances the natural pull of hot gases up the flue with a room air pressure.

1 Like

Assuming the barometric damper configuration is pulling makeup air from outside, it reduces radon in two ways:

  1. Radon is literally sucked into a home by low pressure, generally caused by the stack effect of a home/building or the Venturi effect of wind passing across the top of a chimney or an open window. If you increase the pressure in the home (which is the purpose of a barometric backdraft damper), you pull in less radon.

Side note: Radon mitigation systems also increase the pressure in a home relative to the soil under it by pulling a vacuum under the slab (sort of lowering the water as opposed to raising the bridge).

  1. The radon concentration in air is diluted by makeup air (which a backdraft damper provides if used to bring outside air into a home or a cold air plenum).

Side note: Radon testing is done under “closed house” conditions because openings (windows) reduce the radon level by also diluting its concentration in air.

2 Likes

Thank you for the adjunct hypothesis, Nick.

1 Like

I should amend my comment. There are two common types of dampers on flues, in my experience, usually on boilers. I rarely see a barometric damper, which is the illustration below.

I like simple explanations. When the boiler is firing, hot combustion gases rise up the flue creating draft. These hot gases contain humidity which is a by-product of combustion. The draft creates a slight suction that opens the barometric damper to draw room air into the flue to dilute the combustion gases and reduce the opportunity for the humidity in the combustion gases to condense in the flue.

The other type of damper that is most common is a flue damper. The two types that I see are

  1. automatic dampers with a solenoid activator that opens the damper when the boiler fires

2. a balanced flue damper that opens when hot combustion gases rise up the flue and push it open.

My earlier comment is relative to this type of flue damper.
Neither a barometric damper or flue damper remove or alter the need for adequate combustion air and both are part of the exhaust system. My two cents…use the term “combustion air” instead of “fresh air” as “combustion air” is more accurate for why outside air is sometimes brought into the mechanical room.

1 Like

Many, if not most, HVAC techs around here use “make up air” describing it as a “replacement” of air that was used up.

1 Like

I sometimes hear “make up air” too.