Question about ridge vent with cathedral ceilings and limited soffit intake

Looking for some input from other inspectors regarding roof ventilation.

The home has a gable roof with cathedral ceilings (no attic space). The roof assembly currently has a ridge vent installed, but there are no obvious continuous soffit vents. The soffits have a few older round metal vents, but it is unclear whether those actually open into the rafter bays or if they are blocked by insulation.

The ceiling insulation appears to be faced fiberglass installed in the rafter cavities. I have not yet confirmed whether vent baffles/chutes are present in each bay to maintain an air channel from the eave to the ridge.

My understanding is that with cathedral ceilings, each rafter bay should have a continuous ventilation channel from soffit intake to ridge exhaust, and that ridge vents generally require balanced low intake to function properly.

Questions for those with more experience with this configuration:

• Can a ridge vent function effectively if soffit intake is minimal or unclear?

• Would small round soffit vents typically provide enough intake for ridge ventilation in a cathedral assembly?

• If the soffit vents do not connect directly to the rafter bays (blocked by insulation, no baffles), would the ridge vent provide any meaningful ventilation?

Just looking for some professional opinions and best practices for this type of roof assembly.

Thanks.

The soffit is often somewhat open like a plenum. Meaning one soffit vent may serve several/all bays.

No, you need both intake and outtake.

That’s a math problem. Did you take measurements?

4 Likes

The BSC (Building Science Corp) has information on this and many other attic and crawlspace conditions we see. https://buildingscience.com/

Thanks Brian.

I agree with you on needing intake and outtake.

Unfortunately, the soffit isn’t like the one in the article you posted. The soffit runs at the same angle as the rafters. This makes me believe there are individual rafter bays rather than being open like a plenum. But I can’t determine if they’re compartmentalized or if there are air gaps going from one rafter bay to another.

As for measuring I have a 37 foot ridge. Assuming 16 in on-center rafters, that’s 58 presumed individual rafter bays.

1 Like

i’d assume 24” centers on the rafters. that’s what they normally are. 16” is for walls.