I came across this fuse box a couple days ago, and I had a couple questions about some of the components.
ORANGE: All of the grounds inside the panel were twisted together into 1, and then attached to the interior on the right side of the panel using a screw and a lug through a knockout not intended for this purpose. I believe this thus grounds everything to the panel and can be a hazard. I just wanted confirmation and additional information that anybody could offer.
RED: I am unsure of what those components of the fuse box do. They are similar in appearance to the clamp on a bus bar in which you attach the connection to the grounding rod. Some clarification would be much appreciated on the function of these components and any potential issues with them that are visible in the picture.
GREEN: The arrow is pointing at what I believe is the actual clamp I previously mentioned; except, all of the neutrals are wired into the “bus bar,” if that’s what it is, with no grounds. Instead of a ground, there is a neutral attached to the clamp that leads directly to what ever is on the other side of the wire.
When this fuse box was originally installed there were likely no grounding conductors. It appears that someone replaced the branch circuits with grounded cables within the home at some point. Knowing that they needed to isolate the grounds and neutrals at what I am presuming is a distribution subpanel and only having one buss bar, they rightly chose to make that the neutral buss. Twisting all the ground wires together and grounding the enclosure are all code-compliant (as far as I am aware). So, whoever did this, they did the best they could with what they had and did a decent job of it. If the electrical receptacles within the home are all testing as properly grounded, then I would not be concerned about this wiring.
They’re not doing anything from what’s visible in the photo. Can you provide a photo of the entire fuse panel? Was there a panel label anywhere?
EGC’s can be pigtailed providing that the pigtail is sized for the largest EGC in the splice. Although twisting the EGC’s together may make a decent mechanical connection a wirenut or some other listed connector is required. Simple twisting of the bare conductors is not a code complaint way to make the splice.
A modern panel would require a separate EGC bus for the termination of all of the EGC’s but given the age of the fuse panel it may have been compliant to pigtail a single conductor to the enclosure when this was installed.
It’s presumptuous for others to say that the wiring and the panel were installed at different times. Fuse panels were being as late as the late sixties, early seventies and black jacketed Romex was being used as early as the sixties. It’s possible that both were installed at the same time.
Junior, what year was the structure built? Is this a sub-panel? If so, is it in the same structure as the service panel?
Most/all of what you describe is common for the (increasingly) rare fuse boxes I run across. I never spend much time sorting out all the 75+ year installs and conditions. I write it up as outdated equipment that will be difficult to obtain homeowner’s insurance on.