Question use of Flexible Metalllic Tubing

Originally Posted By: Monte Lunde
This post was automatically imported from our archived forum.



This is in a commercial building. This future bar was wired with 3/8 Flexible Metallic Tubing instead of EMT or Rigid Conduit. I thought that Flexible Metallic Tubing and Flexible Metal Conduit could not exceed 6’ in there use. Is this a proper method of wiring for a commercial building?



Monte Lunde CCI, CCPM, CRI


Viking Construction Services Inc.

Originally Posted By: bkelly1
This post was automatically imported from our archived forum.



It probably has a ground in it. May be a b/x cable, or an armor clad roll of flex that already has wires in it. Yes it is very common. Though here the b/x brand is no longer allowed.


Originally Posted By: Monte Lunde
This post was automatically imported from our archived forum.



No there is not any ground in it. The bx or AC is acting has the ground. I should have stated that in the original post. That is why I was asking about the length.



Monte Lunde CCI, CCPM, CRI


Viking Construction Services Inc.

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



If it is type AC there is no limit on length. The bonding strip will shunt out the leading edge wave of the fault.


Originally Posted By: Monte Lunde
This post was automatically imported from our archived forum.



Ben & Greg


Thank You, for your answers. I will not worry about it any more.


--
Monte Lunde CCI, CCPM, CRI