Is this a defect, since all the strands don’t fit under the screw?

 ![IMG_2137](https://global.discourse-cdn.com/internachi/original/4X/9/2/2/922cc76580342eebc14eef96571fc48258047499.jpeg)

Also is this the bonding screw? Looks like it to me.

 ![IMG_2136](https://global.discourse-cdn.com/internachi/original/4X/a/4/0/a40e11966e35d2856321ec496249eb648cff8e51.jpeg)

Thanks,

Diane

---

<div class="post-metadata">

**Author:** ![yzhang](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/yzhang/32/57038_2.png) [@yzhang](https://forum.nachi.org/u/yzhang)\
**Post date:** [February 25, 2026, 8:39pm UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/2 "2026-02-25T20:39:44Z")

</div>

1. yes correct that connection is no good. Also, I don’t think I’ve ever seen screws like that used to connect any wiring. Do you have a zoomed out picture?

2. No that’s just another grounding bus bar. Do you have a picture of the whole panel?

---

<div class="post-metadata">

**Author:** ![dsnider5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dsnider5/32/250149_2.png) [@dsnider5](https://forum.nachi.org/u/dsnider5)\
**Post date:** [February 25, 2026, 9:43pm UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/3 "2026-02-25T21:43:07Z")

</div>

![IMG_2135 (1)](https://global.discourse-cdn.com/internachi/original/4X/b/3/3/b336c2e91a07d0bae713bede21df8238eecd7222.jpeg)

Thanks Yu for getting back to me! Here is a photo of the whole panel. I thought that was the bonding screw because it was green.

Diane

---

<div class="post-metadata">

**Author:** ![rkenney](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rkenney/32/405447_2.png) [@rkenney](https://forum.nachi.org/u/rkenney)\
**Post date:** [February 25, 2026, 9:55pm UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/4 "2026-02-25T21:55:34Z")

</div>

Apparently from your panel picture that is merely the ground for a 50A four wire circuit (possibly an oven). The “bonding screw” referenced in so many posts will connect (bond) the neutral to the equipment ground (often simply to the cabinet which is grounded). It may be that bond occurs above the main breaker (not visible in your picture) where the neutral and bare ground wire disappear.

---

<div class="post-metadata">

**Author:** ![dhorton2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhorton2/32/178593_2.png) [@dhorton2](https://forum.nachi.org/u/dhorton2)\
**Post date:** [February 26, 2026, 3:32am UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/5 "2026-02-26T03:32:36Z")

</div>

Your picture is of the grounding bus bar. This does not need a bonding screw, because it is literally welded to the box. It is bonded. And it looks like there is a grounding bus on both sides of the panel that they used for all grounding conductors. It is the neutral bus bars that appear to not be bonded to the panel.

However, since this appears to be a distribution panel, there should be a 4 wire feed to the panel, and this only has a 3 wire on that backfed breaker.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [February 27, 2026, 2:24pm UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/6 "2026-02-27T14:24:34Z")

</div>

> [@dsnider5](#):
>
> Is this a defect, since all the strands don’t fit under the screw?.

Yes it should be terminated like the white neutral conductor in the upper left of the full view photo of the panel within a proper terminal. There is actually a spare terminal on the upper right side that they could have used.

Was this the service? I see what appears to be a bare GEC in the center of the panel which may indicate that this is not a sub-panel.

---

<div class="post-metadata">

**Author:** ![dsnider5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dsnider5/32/250149_2.png) [@dsnider5](https://forum.nachi.org/u/dsnider5)\
**Post date:** [February 27, 2026, 6:34pm UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/7 "2026-02-27T18:34:44Z")

</div>

This is the main panel, but as Daniel pointed out, the neutral bus bars don’t appear to be bonded to the panel.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [February 27, 2026, 6:38pm UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/8 "2026-02-27T18:38:06Z")

</div>

> [@dsnider5](#):
>
> This is the main panel, but as Daniel pointed out, the neutral bus bars don’t appear to be bonded to the panel..

Do you have a photo of the neutral bus above the top circuit breakers?

---

<div class="post-metadata">

**Author:** ![dsnider5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dsnider5/32/250149_2.png) [@dsnider5](https://forum.nachi.org/u/dsnider5)\
**Post date:** [March 2, 2026, 7:27pm UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/9 "2026-03-02T19:27:16Z")

</div>

I’ve attached 3 more photos, the photo of the neutral bus above the top circuit breakers, the diagram, and another of the electrical panel:

 ![electrical bonding](https://global.discourse-cdn.com/internachi/original/4X/d/a/f/daf3cbca4ea3a37a67416dcbae35bfb3a8c578eb.jpeg)

 ![IMG_2139](https://global.discourse-cdn.com/internachi/original/4X/d/c/a/dca302a577250bb2b71d0ef0a7eefc4635d8de39.jpeg)

 ![IMG_2158](https://global.discourse-cdn.com/internachi/original/4X/2/9/f/29fcebf6f60947a7d8112582b5fa2d41fdb0806b.jpeg)

Based on the diagram, I think the bonding screw is there, although not conventional in that its not green. What do you all think?

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [March 2, 2026, 7:33pm UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/10 "2026-03-02T19:33:22Z")

</div>

> [@dsnider5](#):
>
> Based on the diagram, I think the bonding screw is there, although not conventional in that its not green. What do you all think?

The panel nameplate shows the the bonding screw (or the main bonding jumper) in the fourth hole down on the right neutral bar. If you look in the original photo from the OP you can see that the screw is there so the neutral is properly bonded. The green color may have faded with age.

---

<div class="post-metadata">

**Author:** ![yzhang](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/yzhang/32/57038_2.png) [@yzhang](https://forum.nachi.org/u/yzhang)\
**Post date:** [March 3, 2026, 8:56pm UTC](https://forum.nachi.org/t/questions-about-the-electrical-panel/265338/11 "2026-03-03T20:56:45Z")

</div>

![Bonding Screw](https://global.discourse-cdn.com/internachi/original/4X/6/3/0/630d8c8fc6e3a3cbf85f4921d0e80069726e061b.jpeg)