# Rafters not meeting ridge board....

**URL:** <https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727>\
**Category:** Structural Inspections\
**Created:** [January 20, 2006, 12:12am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727 "2006-01-20T00:12:19Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [January 20, 2006, 12:12am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/1 "2006-01-20T00:12:19Z")

</div>

Hey Guys,

Got one for ya…

I was in an attic today and the rafters running to the center board ( ridge ) were in contact with the board as normal…However, on the other side the rafters down about 15-20 along the center of the house stopped about 2" short of reaching the ridge board…so to make it reach they nailed on 1’ blocks to make up the last 2" and nailed them to the joists down every one…

Now this was done years ago, no signs of sagging…and while I did see a whole house exhaust fan directly in the center of the area in the main floors ceiling…that should not effect the fact the roof rafters holding the roof do not contact the center board correctly…

Any thoughs on that…?

![rafter-calkins.jpg](https://global.discourse-cdn.com/internachi/original/3X/7/1/7168fc585af17d46d4673c63433ee682221762aa.jpeg)

---

<div class="post-metadata">

**Author:** ![mcyr](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mcyr/32/173319_2.png) [@mcyr](https://forum.nachi.org/u/mcyr)\
**Post date:** [January 20, 2006, 1:24am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/2 "2006-01-20T01:24:25Z")

</div>

_Far from the standard of practice, wouldn’t you think?_  
\*\*  
\*Hope they don’t get 2’ of snow on the roof, they are at the mercy of the nails of the scap and fatigue over the years will win. \*  
\*\*  
\*This roof system that looks like a 4 to 6 inch slope is at the mercy of the shear of the nails used and eventually will let go. \*  
\*\*  
\*It is not right would be the answer. \*  
\*\*  
\*Marcel \*

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [January 20, 2006, 4:07am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/3 "2006-01-20T04:07:20Z")

</div>

I agree…I told the buyer this…and his reply was…heck I am old Paul…I will be dead before it is a concern of mine…I said…oh well…it is in my report so thats up to you…

So the guy loved me…but did not care about any concerns I reported…wants to buy the house anyway without suggesting the buyer fix anything…go figure…lol

---

<div class="post-metadata">

**Author:** ![rsonneson](https://avatars.discourse-cdn.com/v4/letter/r/b487fb/32.png) [@rsonneson](https://forum.nachi.org/u/rsonneson)\
**Post date:** [January 20, 2006, 4:18am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/4 "2006-01-20T04:18:01Z")

</div>

You did your job and he did not see a need to make it a isssue. Sounds like a reasonable man.

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [January 20, 2006, 4:38am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/5 "2006-01-20T04:38:17Z")

</div>

I tell you…the guy was about the nicest man I have ever met on a inspection. Really cared about the house and I think he will get the things I mentioned looked at…but regardless I could tell he really wanted the house and so I am happy for him…overall the issues can be corrected if he chooses to do so.

---

<div class="post-metadata">

**Author:** ![lewens](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lewens/32/518_2.png) [@lewens](https://forum.nachi.org/u/lewens)\
**Post date:** [January 20, 2006, 1:30pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/6 "2006-01-20T13:30:24Z")

</div>

This is the kind of stuff that made me quit the trade.  
Larry

---

<div class="post-metadata">

**Author:** ![lagudo](https://avatars.discourse-cdn.com/v4/letter/l/e79b87/32.png) [@lagudo](https://forum.nachi.org/u/lagudo)\
**Post date:** [January 20, 2006, 2:00pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/7 "2006-01-20T14:00:05Z")

</div>

Why didn’t they just add another block between the ridge board and the rafter to take up the void instead of sistering a piece of wood against the rafter. The rafters on that side of the house are bearing on nails instead of wood. I would want to make a big deal of it. If this is what you can see , who knows what you can’t see. With that said , I would want to add a block to take up that void between the rafter and the ridge.

Louis Agudo  
Home Sweet Home Inspection Services

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [January 20, 2006, 4:14pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/8 "2006-01-20T16:14:34Z")

</div>

I hear ya Louis…I made note and explained my concerns and refered to a licensed contractor or structural engineer on the correct changes.

---

<div class="post-metadata">

**Author:** ![ckratzer](https://avatars.discourse-cdn.com/v4/letter/c/f04885/32.png) [@ckratzer](https://forum.nachi.org/u/ckratzer)\
**Post date:** [January 20, 2006, 7:09pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/9 "2006-01-20T19:09:31Z")

</div>

> [@lewens](#):
>
> This is the kind of stuff that made me quit the trade.  
> Larry

Why would you let someone elses poor craftsmanship influence your desire to stay or leave the trade?

Is this not the exact reason you would want to stay?

Just curious.

---

<div class="post-metadata">

**Author:** ![ckratzer](https://avatars.discourse-cdn.com/v4/letter/c/f04885/32.png) [@ckratzer](https://forum.nachi.org/u/ckratzer)\
**Post date:** [January 20, 2006, 7:16pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/10 "2006-01-20T19:16:10Z")

</div>

The ridge board is also under-sized and should be the next size up so that the rafters bear fully on.  
The rafters look to be 2x6. The ridge board in this case should be 2x8.

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [January 20, 2006, 8:29pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/11 "2006-01-20T20:29:10Z")

</div>

Cheremie,

```
In the case of the image above...even if it was a 2x8 the rafter would not reach the ridge board.....this was done all down the left side for about 20 rafters.....
```

---

<div class="post-metadata">

**Author:** ![ckratzer](https://avatars.discourse-cdn.com/v4/letter/c/f04885/32.png) [@ckratzer](https://forum.nachi.org/u/ckratzer)\
**Post date:** [January 20, 2006, 8:36pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/12 "2006-01-20T20:36:44Z")

</div>

Paul, my comment was more in the line of “in addition to…” the obvious short rafters.😉

---

<div class="post-metadata">

**Author:** ![gmartin2](https://avatars.discourse-cdn.com/v4/letter/g/e99b99/32.png) [@gmartin2](https://forum.nachi.org/u/gmartin2)\
**Post date:** [January 20, 2006, 9:08pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/13 "2006-01-20T21:08:22Z")

</div>

‘measure twice, cut once’

---

<div class="post-metadata">

**Author:** ![mcyr](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mcyr/32/173319_2.png) [@mcyr](https://forum.nachi.org/u/mcyr)\
**Post date:** [January 20, 2006, 10:16pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/14 "2006-01-20T22:16:53Z")

</div>

🙂 🙂  
Larry E. , What is the reason you gave up the trade?

I am curious now.  
\*\*  
\*Cherimie got me going on this, so it is not my fault. ha. ha. \*  
\*\*  
\*Marcel \*

---

<div class="post-metadata">

**Author:** ![Jay\_Moge](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jay_moge/32/93_2.png) [@Jay\_Moge](https://forum.nachi.org/u/Jay_Moge)\
**Post date:** [January 21, 2006, 1:38am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/15 "2006-01-21T01:38:33Z")

</div>

i don’t get it, i cut it **3 times** boss, and it’s still too short.

---

<div class="post-metadata">

**Author:** ![jsieg](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jsieg/32/2298_2.png) [@jsieg](https://forum.nachi.org/u/jsieg)\
**Post date:** [January 21, 2006, 2:15am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/16 "2006-01-21T02:15:57Z")

</div>

Boss “Try cutting from the other end. Do I have to tell you how to do every thing?”

---

<div class="post-metadata">

**Author:** ![Jay\_Moge](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jay_moge/32/93_2.png) [@Jay\_Moge](https://forum.nachi.org/u/Jay_Moge)\
**Post date:** [January 21, 2006, 2:29am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/17 "2006-01-21T02:29:02Z")

</div>

“whooob whooob whoooob whooooob”…“gnaaaa gnaaaaa gnaaaaa”

sure wish i had the 3 stoogies clip to go with it.

---

<div class="post-metadata">

**Author:** ![rroeske](https://avatars.discourse-cdn.com/v4/letter/r/c0e974/32.png) [@rroeske](https://forum.nachi.org/u/rroeske)\
**Post date:** [February 7, 2006, 8:10pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/18 "2006-02-07T20:10:44Z")

</div>

The framer forgot his board stretcher that day.

Agreed the depth of the ridge board should match the cut end of the rafter for full bearing and nailing. The question is how well the sistered piece is secured to the rafter end. If straight nailed it provides little strength to the joint. The strength of the roof is more the rafters bearing against each other. The ridge board only provides a nailing surface and prevents lateral movement while providing a straight horizontal line for the rafter ends.  
Some house are built without ridge boards.

I would write it up as “nonconventional framing” and look for how well the nailing secures everything together. If it appears weak - recommend evaluation by a structural engineer.

A better way might have been to sister a board to the ridge board and then secure the rafter ends to this “doubled ridge”, where they are short.

---

<div class="post-metadata">

**Author:** ![mcyr](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mcyr/32/173319_2.png) [@mcyr](https://forum.nachi.org/u/mcyr)\
**Post date:** [February 8, 2006, 2:29am UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/19 "2006-02-08T02:29:09Z")

</div>

The ridgeboard in conventional framing of a roof provides very little lateral stability in the struture, it provides ease in the framing of the strurture.  
The sheathing will provide the lateral moment creating a diaphram.

Trusses will not have ridge boards but require some sort of lateral bracing as required by the Truss Manufacturer.  
The rafters in conventional framing are in compression and the collar ties are in tension. If a knee wall is provided, then lateral bracing could be added to provide counteraction to movement.

Hope this helps.

Marcel

---

<div class="post-metadata">

**Author:** ![jfarsetta](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfarsetta/32/327_2.png) [@jfarsetta](https://forum.nachi.org/u/jfarsetta)\
**Post date:** [February 8, 2006, 12:12pm UTC](https://forum.nachi.org/t/rafters-not-meeting-ridge-board/727/20 "2006-02-08T12:12:47Z")

</div>

Marcel is correct. Depencding on the pitch of the roof, the ridge may serve as little more than a spacer or nailer, and some homes are constructed without a ridge beam.

In lower sloping roof structures, a ridge may serve as an actual supporting member.

There is nothing wrong with the framing in the photo.