2007 crawl space. What do you see wrong?

![073112 115.JPG](https://global.discourse-cdn.com/internachi/original/2X/f/fa7489022108e2377750a8c06e5a00c32afaec85.jpeg) ![073112 119.JPG](https://global.discourse-cdn.com/internachi/original/2X/e/ef242a0b9eca85f3845a15d56c0ae96a98eaa35a.jpeg)

![073112 119.JPG](https://global.discourse-cdn.com/internachi/original/2X/e/ef242a0b9eca85f3845a15d56c0ae96a98eaa35a.jpeg)

---

<div class="post-metadata">

**Author:** ![bjeffrey](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bjeffrey/32/174340_2.png) [@bjeffrey](https://forum.nachi.org/u/bjeffrey)\
**Post date:** [August 3, 2012, 1:35pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/2 "2012-08-03T13:35:26Z")

</div>

Shim board poorly placed, poorly secured and should be flat grain. What else did I miss?

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [August 3, 2012, 1:38pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/3 "2012-08-03T13:38:35Z")

</div>

The foundation straps are not designed for a 2x8. They are not designed for use with roofing button caps. The only thing actually anchored, half-asz, is the sill plate…the house framing is only connected by gravity or perhaps a toe nail to the sill plate.

---

<div class="post-metadata">

**Author:** ![jhaynes](https://avatars.discourse-cdn.com/v4/letter/j/ce7236/32.png) [@jhaynes](https://forum.nachi.org/u/jhaynes)\
**Post date:** [August 3, 2012, 4:59pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/4 "2012-08-03T16:59:11Z")

</div>

Just love pier and curtain construction…lol.

This obviously is a code issue and I wouldn’t have a problem pointing it out, along with the required paperwork that one has to provide when they talk about code.

If you opt not to mention code then you would be putting yourself behind the 8 ball in this argument in that most home prior to the 1980’s have little to no anchor system what so ever…in those cases I do not write them up or mention it for the matter.

While I do believe code should be adhered to…at the same time, if God decides He wants that house moved…it will move be it tornado, hurricane or earthquake. (smile)

Being this home was built in the last 20 years, I would cite the relevant code and let the client decide.

regards

Jeff

PS. Other then coaching at the high school during the week, I am backing off on coaching during the weekend…let me know if your interested riding to the mountains or beech during the fall.

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [August 3, 2012, 8:42pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/5 "2012-08-03T20:42:53Z")

</div>

> [@bjeffrey](#):
>
> Shim board poorly placed, poorly secured and should be flat grain. What else did I miss?

What do you mean by “flat grain”?

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [August 5, 2012, 6:05pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/6 "2012-08-05T18:05:47Z")

</div>

1.) The beam on the pier resting on the shim.  
The shim on the pier is angled or positioned the wrong way. The grain will make it cup and splinter.  
The second photo had a floor joist. I can not see the bearing and I see no blocking.  
Is the a footer for the pier?

I am not that educated on hurricane of earthquake straps myself.  
Locks wrong.

---

<div class="post-metadata">

**Author:** ![jhaynes](https://avatars.discourse-cdn.com/v4/letter/j/ce7236/32.png) [@jhaynes](https://forum.nachi.org/u/jhaynes)\
**Post date:** [August 6, 2012, 11:23am UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/7 "2012-08-06T11:23:35Z")

</div>

What the heck are you guys talking about shims…the board under the girder is a SILL plate…just like any sill plates on the exterior of the foundation.

Flat grain…oh please…

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [August 6, 2012, 12:33pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/8 "2012-08-06T12:33:32Z")

</div>

I referred this to a PE I know. The client spoke with the PE who would charge about $550 to design a repair. He estimated the repair would cost $2,000. PE told the client the house was unlikely to blow away, but that the issue could haunt him on resale. The client’s agent is poo pooing the report. Client tells me he is very unhappy with his agent and plans to walk if seller’s won’t fix it.

I sent photos to the building dept. head for that jurisdiction. Never heard back from him. It should be a crime to be derelict in your duties as a BO. Really ticks me off that this kind of crap passes inspection.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 6, 2012, 12:53pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/9 "2012-08-06T12:53:50Z")

</div>

> [@jhaynes](#):
>
> What the heck are you guys talking about shims…the board under the girder is a SILL plate…just like any sill plates on the exterior of the foundation.
> 
> Flat grain…oh please…

So… the issue of an improper anchor still remains…

[http://blog.amerifirst.com/Portals/27489/images/sill-plate-203k-renovation.jpg](http://www.ehow.com/how_4522487_replace-house-foundation-sill-plate.html)

 ![](https://global.discourse-cdn.com/internachi/original/3X/7/d/7d89f366344e4c8633c9eec5085e946800194b7d.jpeg)

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [August 6, 2012, 1:11pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/10 "2012-08-06T13:11:15Z")

</div>

> [@jjonas](#):
>
> [http://blog.amerifirst.com/Portals/27489/images/sill-plate-203k-renovation.jpg](http://www.ehow.com/how_4522487_replace-house-foundation-sill-plate.html)

While that may meet “code”, all it does is anchor the sill plate. The walls can move off the sill plate since the illustration doesn’t show a connection between the walls and plate.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [August 6, 2012, 1:13pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/11 "2012-08-06T13:13:03Z")

</div>

A better, but never seen, method (taken from the 2009 IRC):

 ![Strapping.jpg](https://global.discourse-cdn.com/internachi/original/2X/5/5522f34e1806c40a44c6873c26971cb2e57365c7.jpeg) ![Strapping2.jpg](https://global.discourse-cdn.com/internachi/original/2X/e/e78ad01841cc1e808774a6f91da77e27bc30f122.jpeg)

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 6, 2012, 1:17pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/12 "2012-08-06T13:17:19Z")

</div>

> [@jfunderburk](#):
>
> While that may meet “code”, all it does is anchor the sill plate. The walls can move off the sill plate since the illustration doesn’t show a connection between the walls and plate.

The point of my post being… Mr. Haynes made the distinction between this being a “Sill Plate” as opposed to being a “Shim”. I pointed out that even as a sill plate, it was still missing proper anchoring. Call the plate whatever you wish, it is still wrong!

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [August 6, 2012, 2:00pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/13 "2012-08-06T14:00:28Z")

</div>

Having never seen that style or type of pier work to carry the structure I thought it might be a add-on.  
Opps I am bad.  
IMO; The sill plate anchorage (straps) are not worth the material they are built with.  
Jeffrey your sill plate anchorage is for concrete foundation.  
The CMU pier must be full and caped for Moisture, Termite entry and to give the pier strength…  
We went over this 4 months ago.  
Sorry about the shim hypotheses. I though it was an standalone pier and forgot about the floor joist on the opposing side enabling stability.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 6, 2012, 2:07pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/14 "2012-08-06T14:07:44Z")

</div>

> [@ryoung7](#):
>
> Having never seen that style or type of pier work to carry the structure I thought it might be a add-on.  
> Opps I am bad.  
> IMO; The sill plate anchorage (straps) are not worth the material they are built with.  
> Jeffrey your sill plate anchorage is for concrete foundation.  
> The CMU pier must be full and caped for Moisture, Termite entry and to give the pier strength…  
> We went over this 4 months ago.  
> Sorry about the shim hypotheses. I though it was an standalone pier and forgot about the floor joist on the opposing side enabling stability.

All of that is irrelevent Robert. Don’t be so literal. Stick with the “intent” of the post. The fasteners used in the OP’s photo are WRONG! Period! The pier can be made out of any material… the fasteners are still wrong.

> [@](#):
>
> The point of my post being… Mr. Haynes made the distinction between this being a “Sill Plate” as opposed to being a “Shim”. I pointed out that even as a sill plate, it was still missing proper anchoring. Call the plate whatever you wish, it is still wrong!

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [August 6, 2012, 2:09pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/15 "2012-08-06T14:09:25Z")

</div>

> [@jjonas](#):
>
> **The pier can be made out of any material** … the fasteners are still wrong.

FYI. Foundation straps are not approved for use in red clay brick piers or curtain walls.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 6, 2012, 2:13pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/16 "2012-08-06T14:13:23Z")

</div>

> [@jfunderburk](#):
>
> FYI. Foundation straps are not approved for use in red clay brick piers or curtain walls.

Irrelevent!

What don’t you understand" Fasteners are the NAILS, not the straps! There is nowhere in any instance where the nails used in the OP’s pic’s come even close to being approved for structural! Nothing else matters at this point. The piers could be perfect in all respects, but with those nails, it is simply crap!

> **[Pakuya.com is available at DomainMarket.com](https://www.domainmarket.com/buynow/pakuya.com)**
>
> Domain for Sale. Pakuya.com. Request Price. What Are the
> Advantages of a Super Premium .Com Domain? Increased Traffic. Search Engine Ranking. Brand Recognition.
> Immediate Presence. Higher Profits. Great Investment. #1 in Premium Domains. 300,000 of...

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [August 6, 2012, 2:16pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/17 "2012-08-06T14:16:14Z")

</div>

> [@jjonas](#):
>
> Irrelevent!
> 
> What don’t you understand" Fasteners are the NAILS, not the straps! There is nowhere in any instance where the nails used in the OP’s pic’s come even close to being approved for structural! Nothing else matters at this point. The piers could be perfect in all respects, but with those nails, it is simply crap!

I agree with you but thought it necessary to respond to the implication of your comment that a pier could be made of any type of material.

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [August 6, 2012, 7:21pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/18 "2012-08-06T19:21:51Z")

</div>

> [@jjonas](#):
>
> All of that is irrelevent Robert. Don’t be so literal. Stick with the “intent” of the post. The fasteners used in the OP’s photo are WRONG! Period! The pier can be made out of any material… the fasteners are still wrong.

OK.  
\*\* Realtor tells client this is not a big issue.  
**ONE HAS TO GENERATE THE HYPOTHESES TO INSURE THE REALTOR IS INCORRECT.I noted all the issues.  
Jeffrey.  
Irreverence would be not forming a working hypotheses on why the realtor is wrong. And in so many ways I suspect.  
Cost of repairing the issue being number one!!  
The anchorage is wrong.The pier is suspect.**  
Not trying to be funny but;\*\* to point out irrelevant is your Concrete anchorage is inappropriate.  
Mr. Funderburk’s 18 ga. plate connectors are approved.

OR j style anchorage bolts

The photos may be code but I suspect no.  
Typical MAB23 Installation in Concrete Block (MAB15 similar) MAB23 provides a two block embedment, if required by the[local code jurisdiction.](http://www.strongtie.com/ftp/catalogs/c-2011/C-2011-p033-p036.pdf)

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [August 6, 2012, 7:31pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/19 "2012-08-06T19:31:20Z")

</div>

> [@jfunderburk](#):
>
> I agree with you but thought it necessary to respond to the implication of your comment that a pier could be made of any type of material.

Like I told Robert, don’t be so literal.

Looking at the post just above, you can see why I stated this.

Btw… a pier \*\*can \*\*be built with red clay brick, you just can’t use a “traditional” strap with it. 😉

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [August 6, 2012, 7:40pm UTC](https://forum.nachi.org/t/realtor-tells-client-this-is-not-a-big-issue/70999/20 "2012-08-06T19:40:22Z")

</div>

> [@jjonas](#):
>
> Irrelevent!
> 
> What don’t you understand" Fasteners are the NAILS, not the straps! There is nowhere in any instance where the nails used in the OP’s pic’s come even close to being approved for structural! Nothing else matters at this point. The piers could be perfect in all respects, but with those nails, it is simply crap!
> 
> [Pakuya.com is available at DomainMarket.com. Call 888-694-6735](http://www.pakuya.com/upload/20111203/plastic_cap_roofing_nails.jpg)

Too be far you are only looking at 4 button fasteners Jeffrey.

I have seen fasteners in the field used to hold a object in place while the correct fasteners are anchored. I personally used the technique when working alone in tight spaces.  
We can not see the top of the plate where the correct anchorage would be with LMAZ/MA/MAB/MASB Mudsill Anchors or other types. Even J bolts.