Here’s a good read on reversed polarity of bootleg grounds and the 3 light testers many of us use:

> **[Friends of Gary - Mike](http://www.rvdoctor.com/2001/07/friends-of-gary-mike.html)**
>
> Failures in Outlet Testing By Mike Sokol I’ve done it…. You’ve done it… We’ve all done it…. plugged a simple 3-light tester into a...

---

<div class="post-metadata">

**Author:** ![jmckee](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jmckee/32/211009_2.png) [@jmckee](https://forum.nachi.org/u/jmckee)\
**Post date:** [September 1, 2012, 12:41pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/2 "2012-09-01T12:41:40Z")

</div>

good information…thanks Linas

---

<div class="post-metadata">

**Author:** ![canderson5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/canderson5/32/1814_2.png) [@canderson5](https://forum.nachi.org/u/canderson5)\
**Post date:** [September 1, 2012, 1:46pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/3 "2012-09-01T13:46:31Z")

</div>

Good info, also be aware of the number of grounds in the panel. If the age of the house is 70’s or earlier, most of the circuits are 2 conductor and the outlets are mostly three-prong which test grounded, then you’ve got bootleg grounds(aka pirate or false grounds). Start with the panel so you know what to expect when checking outlets.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [September 1, 2012, 3:24pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/4 "2012-09-01T15:24:31Z")

</div>

As always, Mike provides great information. The SureTest will indicate a false-ground and it will also indicate reversed polarity. However, when both conditions exist, the SureTest gives “priority” to the FG condition, and will not indicate the RP.

---

<div class="post-metadata">

**Author:** ![hcarvajal](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/hcarvajal/32/209279_2.png) [@hcarvajal](https://forum.nachi.org/u/hcarvajal)\
**Post date:** [September 3, 2012, 1:02am UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/5 "2012-09-03T01:02:16Z")

</div>

Here’s a nice website for this and other residential eletrical issues as well.

[http://www.thecircuitdetective.com/index.htm](http://www.thecircuitdetective.com/index.htm)

Bert

---

<div class="post-metadata">

**Author:** ![tspargo](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tspargo/32/253654_2.png) [@tspargo](https://forum.nachi.org/u/tspargo)\
**Post date:** [September 3, 2012, 4:52am UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/6 "2012-09-03T04:52:51Z")

</div>

Was just about to post that my suretest must be on it’s way out… as I recently found a RP bootleg and it only showed F… I used an AC tick to discern…

ALMOST POSTED… and [found this video](http://youtu.be/_04HmpFBxdQ) from Mike S, I guess my suretest is working just fine 😃

Also a relevant tip… Equipment Grounds required @ receptacles per 1962 NEC… a few years later was to be a full size EG as well…

IMO, flippers are creating some of the most interesting electrical defects… I mean they really just throw anybody in there with a box of duplex outlets and single pole (only single pole / no 3 way :D) switches…

Reverse polarity bootleg… Imagine going to test one in a garage… with a metal plate. zooowww

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [September 3, 2012, 12:20pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/7 "2012-09-03T12:20:58Z")

</div>

> [@tspargo](#):
>
> Was just about to post that my suretest must be on it’s way out… as I recently found a RP bootleg and it only showed F… I used an AC tick to discern…
> 
> ALMOST POSTED… and [found this video](http://youtu.be/_04HmpFBxdQ) from Mike S, I guess my suretest is working just fine 😃
> 
> Also a relevant tip… Equipment Grounds required @ receptacles per 1962 NEC… a few years later was to be a full size EG as well…
> 
> IMO, flippers are creating some of the most interesting electrical defects… I mean they really just throw anybody in there with a box of duplex outlets and single pole (only single pole / no 3 way :D) switches…
> 
> Reverse polarity bootleg… Imagine going to test one in a garage… with a metal plate. zooowww

Good video Tim. Interesting that the SureTest shows only the FG even when there is RP. This now leaves me wondering what I actually found when I came across (what I thought was) this same condition 😃

I edited my previous post to correct the misinformation…

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [September 3, 2012, 12:27pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/8 "2012-09-03T12:27:57Z")

</div>

Thanks Linas. One of my weak suites.  
Nice to see you laughing in your photo.  
All the best.

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [September 3, 2012, 12:29pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/9 "2012-09-03T12:29:12Z")

</div>

> [@tspargo](#):
>
> Was just about to post that my suretest must be on it’s way out… as I recently found a RP bootleg and it only showed F… I used an AC tick to discern…
> 
> ALMOST POSTED… and [found this video](http://youtu.be/_04HmpFBxdQ) from Mike S, I guess my suretest is working just fine 😃
> 
> Also a relevant tip… Equipment Grounds required @ receptacles per 1962 NEC… a few years later was to be a full size EG as well…
> 
> IMO, flippers are creating some of the most interesting electrical defects… I mean they really just throw anybody in there with a box of duplex outlets and single pole (only single pole / no 3 way :D) switches…
> 
> Reverse polarity bootleg… Imagine going to test one in a garage… with a metal plate. zooowww

Thanks Mr. Spargo.

---

<div class="post-metadata">

**Author:** ![mauger](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mauger/32/178937_2.png) [@mauger](https://forum.nachi.org/u/mauger)\
**Post date:** [September 4, 2012, 7:03pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/10 "2012-09-04T19:03:45Z")

</div>

That is a good article, Hey Guys, you should consider signing up for Mike’s (not me) news letter. Theres good stuff in it.

---

<div class="post-metadata">

**Author:** ![mgratton](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgratton/32/58251_2.png) [@mgratton](https://forum.nachi.org/u/mgratton)\
**Post date:** [September 12, 2012, 6:37pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/11 "2012-09-12T18:37:22Z")

</div>

Wouldn’t a hot ground reverse be just as dangerous?

 ![IMG_0065.jpg](https://global.discourse-cdn.com/internachi/original/3X/5/3/53ae21ce4fe8cef380a0f5fbf027d3582828c59e.jpeg)

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [September 13, 2012, 7:01am UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/12 "2012-09-13T07:01:52Z")

</div>

Yep worked on my last inspect.  
Thanks again.

---

<div class="post-metadata">

**Author:** ![Mike\_Sokol](https://avatars.discourse-cdn.com/v4/letter/m/aca169/32.png) [@Mike\_Sokol](https://forum.nachi.org/u/Mike_Sokol)\
**Post date:** [July 19, 2013, 11:15am UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/13 "2013-07-19T11:15:28Z")

</div>

> [@ldapkus1](#):
>
> Here’s a good read on reversed polarity of bootleg grounds and the 3 light testers many of us use:  
> [The RV Doctor: Friends of Gary - Mike](http://www.rvdoctor.com/2001/07/friends-of-gary-mike.html)

Hi Guys…

I’m Mike Sokol, the author of the above article about RPBG outlets (Reverse Polarity Bootleg Grounds). Thanks for posting it here as I think it’s something serious to look out for, especially in pre-70’s homes that have had “quick upgrades”.

FYI: I’ve just published a feature article on this topic in the July issue of EC&M Magazine which hits the streets on July 28th. It goes into much more detail about how RPBG outlets are measured and additional dangers to electrical gear that’s cross-connected between an RPBG outlet and a properly wired outlet. Hint: it ain’t pretty… Here’s a link to the early release online version. [Failures in Outlet Testing Exposed | EC&M](http://ecmweb.com/contractor/failures-outlet-testing-exposed?page=1)

Please contact me with any comments or suggestions.

Mike Sokol  
[www.NoShockZone.org](http://www.NoShockZone.org)  
[mike@noshockzone.org](mailto:mike@noshockzone.org)

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [July 19, 2013, 5:14pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/14 "2013-07-19T17:14:56Z")

</div>

> [@Mike\_Sokol](#):
>
> Hi Guys…
> 
> I’m Mike Sokol, the author of the above article about RPBG outlets (Reverse Polarity Bootleg Grounds). Thanks for posting it here as I think it’s something serious to look out for, especially in pre-70’s homes that have had “quick upgrades”.
> 
> FYI: I’ve just published a feature article on this topic in the July issue of EC&M Magazine which hit the streets on July 28th. It goes into much more detail about how RPBG outlets are measured and additional dangers to electrical gear that’s cross-connected between an RPBG outlet and a properly wired outlet. Hint: it ain’t pretty… Here’s a link to the early release online version. [Failures in Outlet Testing Exposed | EC&M](http://ecmweb.com/contractor/failures-outlet-testing-exposed?page=1)
> 
> Please contact me with any comments or suggestions.
> 
> Mike Sokol  
> [www.NoShockZone.org](http://www.NoShockZone.org)  
> [mike@noshockzone.org](mailto:mike@noshockzone.org)

All the best Mike.  
Thanks for the invite.

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [July 19, 2013, 10:50pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/15 "2013-07-19T22:50:25Z")

</div>

I did a commercial that had bootlegged a bunch of outlets. So glad my Client did not purchase the place.

---

<div class="post-metadata">

**Author:** ![Mike\_Sokol](https://avatars.discourse-cdn.com/v4/letter/m/aca169/32.png) [@Mike\_Sokol](https://forum.nachi.org/u/Mike_Sokol)\
**Post date:** [July 19, 2013, 11:31pm UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/16 "2013-07-19T23:31:40Z")

</div>

I’ve been going through rewiring my 1926 house room by room, and found that all the old rooms with grounded outlets had been bootleg grounded during a 1970’s remodel. And about 25% of those bootleg outlets turned to to also be reverse polarity. Of course, the reverse polarity problem is accentuated by knob & tube wiring because K&T wiring is typically black, and it appears that the 1926 electricians would sometimes switch the neutral side for lighting, etc…

There also was a pre-fab addition done on my house sometime in the 80’s, and while installing a new sub-panel recently I found that they ran 4-wire cable and decided to use the red wire for the safety ground. Now, this was a pre-fab house put together at a “factory” so I’ve got to assume that’s how it’s always been wired.

So I think that adding a NCVT Proximity Check (Non Contact Voltage Tester) for a hot-ground check is a great addition to any 3-light or Ground impedance tester such as an Amprobe INSP-3 or Ideal SureTest.

To figure out how this all works, I built a portable demonstration rig which allows me to bias any outlet or sound gear with a potential up to 150-volts or current loop up to 30 amps. B&K Precision was kind enough to donate some AC power supplies which work great for this demo. And I’ve also added a 3-volt/30-amp soldering transformer for ground loop current injection to test sound systems for hum problems. See [http://www.bkprecision.com/education/projects/mike-sokol-electrical-shock-prevention-in-sound-systems.html](http://www.bkprecision.com/education/projects/mike-sokol-electrical-shock-prevention-in-sound-systems.html) for my NoShockZone test bench.

Mike Sokol

> **[No~Shock~Zone](http://noshockzone.org/)**
>
> Electrical Safety for Everyone

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [July 20, 2013, 2:04am UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/17 "2013-07-20T02:04:44Z")

</div>

> [@kwood](#):
>
> So glad my Client did not purchase the place.

It’s not our job to get emotionally invested in the clients decision.

I have no preference one way or another on whether they purchase the property, only that they are fully aware of its condition prior to making the decision.

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [July 20, 2013, 2:22am UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/18 "2013-07-20T02:22:23Z")

</div>

I care for every Client I have done an Inspection for and in some cases have sleepless nights because someone has ignored my advice. In most cases this is just someone that can’t see the immediate danger.  
I have seen the emotions you display right here on the open MB and have no doubt in my mind that all you care about is your next inspection.  
Also when opening your Website I receive a direct warning from my Virus protection.  
Testimonies are needed if you want my advice.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [July 20, 2013, 2:55am UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/19 "2013-07-20T02:55:55Z")

</div>

> [@kwood](#):
>
> I care for every Client I have done an Inspection for and in some cases have sleepless nights because someone has ignored my advice. In most cases this is just someone that can’t see the immediate danger.

You are quite the tool Kevin. Once you have actually performed enough inspections, you will understand what I’m talking about. If you truly “cared” for your clients, you’d refer them to a competent inspector.

---

<div class="post-metadata">

**Author:** ![Mike\_Sokol](https://avatars.discourse-cdn.com/v4/letter/m/aca169/32.png) [@Mike\_Sokol](https://forum.nachi.org/u/Mike_Sokol)\
**Post date:** [July 20, 2013, 3:06am UTC](https://forum.nachi.org/t/reverse-polarity-bootleg-ground-and-3-light-testers/71655/20 "2013-07-20T03:06:48Z")

</div>

I’m Mike Sokol, the producer of these videos and articles about what I consider to be a very important topic… Reverse Polarity Bootleg Ground outlets. In fact, I’ve dedicated hundreds of hours to this one topic because I think that proper testing for RPBG’s can and will save lives. And as someone hinted earlier in this thread, this info might even save your own life someday.

However, I see that this thread is quickly degenerating into a bunch of name calling and mud slinging. While I"m only a guest here, I have in fact posted and answered questions on hundreds of pro-audio and RV forums, and I rarely see this sort of behavior. I’m asking you all to PLEASE act like gentleman and stay on topic. Is that asking too much?