This may be a question for another message board but I thought I’d ask.
We installed a replacement furnace in my house and can only get 7" of water column on the manifold side of the valve. The install manual says it needs between 10" and 12".
Local rep says the valve needs to be replaced…we replace it with two new ones…still only 7" of water column with none of the valves adjustable (tighten screw or loosen and no difference in pressure).
We put a newer model of the gas valve on, per the local rep, with no change in performance.
Local rep then says he called the factory and they say run it with the nice blue flame we have and forget it…I am wondering.
Basically you observe the gas consumption over a period of time(10 -30 minutes should be enough)
The burner has to be running full out and all other gas appliances turned off or at least not operating.
Then you have to know the BTU per cu ft. of your local gas supply and calulate from there.(should be appx 1000 BTU.cu.ft.)
example:
100,000 BTU/Hr rated input.
Burner on full for 15 minutes.
Used 25 cu ft.
25/ 1/4 hr x 1000= 100,000 BTU/Hr
Larry it sounds to me as if you are having line drop. What is the size of your supply line and what is the distance from the tank to the furnace.
I ran a one inch line from my tank to the furnace approximately 75 feet and had to adjust the regulator at the tank in order to get 11 inches at the gas valve on the furnace. you can still have a blue flame with less inches of water column but the BTU output will drop and the furnace will run longer to do its job.
I think we may have it figured out. It appears that the regulator on the tank is bad and fluctuating. We were able to get 11", by adjusting that, but not continually. It is running at 9 1/2" of water column now.
Tech from the LP gas company is coming out on Monday next to “upgrade the equipment”.
Thanks, Michael. This certainly has been a learning experience for me and I really appreciate my 75 year old friend that has a lifetime of HVAC experience that seems to get misplaced here and there.
Good find Larry. Now have a co/combustion test done on the flue gases. A few years back found bad co readings when the main blower came on. Someone at the factory left a screw out. Would have never known unless I had tested.
Can you explain the process a little more? What are “bad” (I’m thinking any inside the home is bad) co readings?..and did you find them at registers if they showed when the blower came on?..or was it something excessive at the flue pipe (flue gases)?