Hey everyone,

I’ve been running into a recurring question regarding vent termination clearances on Rinnai RL75e exterior-mounted tankless units, specifically in relation to operable windows.

From my understanding, manufacturer guidelines reference minimum clearances to openings. However, in the field I’m seeing installations where the unit is mounted very close to windows (sometimes directly below or adjacent). I’ve also come across conflicting information in different manuals—some indicating 12" clearance to operable windows, while others (for similar outdoor models in different years) reference up to 4’.

I’ve reviewed the manuals and even spoken with Rinnai technical support, but I’m still having difficulty confidently interpreting and applying these clearance requirements in real-world scenarios.

For those with experience:

  • How are you interpreting clearance requirements to operable windows and doors?

  • Are you defaulting to manufacturer specs only, or deferring to fuel gas code / AHJ requirements?

  • Is there a consistent standard you follow when documentation varies?

Appreciate any insight—this has been a gray area for me for a while.

Not sure why a diagram is not clear?? Rinnai, and others, do a good job of displaying this.

Well, the AHJ has the final say; and they most often defer to the manufacturer. I tend to lean toward the most conservative. Note: In my area, there are many municipalities. Local enforcement varies, so I am most likely to use the manufacturer’s recommendations when that information is available.

The manufacturer’s clearances in the document are pretty clear. I would have more concern about the height above grade! It looks like it is almost sitting on the ground!

Did you measure from the corner of the window to the unit? That would be the distance you need to work with. But, just eyeballing it, I would say it looks like it is OK from the window. But the grade clearance is in question!

Can we please see the manufacturer’s label for that unit?

No, it’s well off the ground.

Your looking at the pipe shroud or cover, that attaches to the bottom of the unit to hide the plumbing.

Rinnai Pipe Cover.pdf (256.0 KB)

Adam, here is the data label.

1 Like

The manual for this unit appears to indicate that the vent clearance should be at least 4 feet from the side or bottom of an operable window.

In the future I’d recommend putting a tape measure in your photo from the vent to the operable window.

2 Likes

Looks like the only way to know is by looking up the manufacturers specs for the particular appliance. And even looking at the diagram and specs posted by Adam, US vs Canada requirements is kind of odd how in Canada a Direct Vent (indoor unit) clearance to operable window/door is 36 inches vs 6-12 inches if other than direct vent (outside unit)…completely opposite from what is the requirement in US. What’s up with that?