Good afternoon all. I inspected a home built in 1978 yesterday and the 100 AMP Eaton main panel looked fairly new. The two hot SEC’s were #2 AL and the neutral SEC was #4 AL. I wrote it up as a deficiency that the neutral SEC is undersized. The SEC’s should all be the same size, correct?

---

<div class="post-metadata">

**Author:** ![bhull1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bhull1/32/180000_2.png) [@bhull1](https://forum.nachi.org/u/bhull1)\
**Post date:** [February 19, 2023, 4:28pm UTC](https://forum.nachi.org/t/secs-different-sizes/225874/2 "2023-02-19T16:28:20Z")

</div>

The neutral is sometimes one size smaller.

> **[When are you allowed to downsize the neutral?](https://forums.mikeholt.com/threads/when-are-you-allowed-to-downsize-the-neutral.146412/)**
>
> Are there any situations where you are allowed to downsize the neutral in residential, commercial, or industrial jobs? Thank you for your help.

---

<div class="post-metadata">

**Author:** ![aevans14](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/aevans14/32/305090_2.png) [@aevans14](https://forum.nachi.org/u/aevans14)\
**Post date:** [February 19, 2023, 4:30pm UTC](https://forum.nachi.org/t/secs-different-sizes/225874/3 "2023-02-19T16:30:03Z")

</div>

10-4. So in a 100 AMP Panel a #4 AWG Aluminum Neutral SEC is acceptable?

---

<div class="post-metadata">

**Author:** ![bhull1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bhull1/32/180000_2.png) [@bhull1](https://forum.nachi.org/u/bhull1)\
**Post date:** [February 19, 2023, 4:30pm UTC](https://forum.nachi.org/t/secs-different-sizes/225874/4 "2023-02-19T16:30:41Z")

</div>

Wow, you read that link already?

---

<div class="post-metadata">

**Author:** ![aevans14](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/aevans14/32/305090_2.png) [@aevans14](https://forum.nachi.org/u/aevans14)\
**Post date:** [February 19, 2023, 4:38pm UTC](https://forum.nachi.org/t/secs-different-sizes/225874/5 "2023-02-19T16:38:27Z")

</div>

Thank you for sharing. Understood now.

For services, the neutral is sized to carry the maximum unbalanced current (white) or the minimum size for a fault

A neutral for a service can be downsized as small as the grounding electrode conductor if the load calculates that low,

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [February 19, 2023, 4:52pm UTC](https://forum.nachi.org/t/secs-different-sizes/225874/6 "2023-02-19T16:52:09Z")

</div>

> [@aevans14](#):
>
> For services, the neutral is sized to carry the maximum unbalanced current (white) or the minimum size for a fault
> 
> A neutral for a service can be downsized as small as the grounding electrode conductor if the load calculates that low

Thats correct. You need to bring the neutral to the service disconnect even if you will not be using it for any loads. The minimum size would be the same as the GEC for a water pipe electrode.

---

<div class="post-metadata">

**Author:** ![aevans14](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/aevans14/32/305090_2.png) [@aevans14](https://forum.nachi.org/u/aevans14)\
**Post date:** [February 20, 2023, 1:57am UTC](https://forum.nachi.org/t/secs-different-sizes/225874/7 "2023-02-20T01:57:07Z")

</div>

Makes perfect sense. Thank you guys for clarifying.

---

<div class="post-metadata">

**Author:** ![mparks3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks3/32/277434_2.png) [@mparks3](https://forum.nachi.org/u/mparks3)\
**Post date:** [February 20, 2023, 2:38am UTC](https://forum.nachi.org/t/secs-different-sizes/225874/8 "2023-02-20T02:38:28Z")

</div>

> [@rmeier2](#):
>
> The minimum size would be the same as the GEC for a water pipe electrode.

You lost me there.