I called out a furnace that did not have a sediment trap after the shut off valve.The HVAC guy said it did not needed one because the gas piping rose so high off the ground that it was useless. Any one ever heard that before?

---

<div class="post-metadata">

**Author:** ![clambert2](https://avatars.discourse-cdn.com/v4/letter/c/f08c70/32.png) [@clambert2](https://forum.nachi.org/u/clambert2)\
**Post date:** [February 28, 2012, 1:30pm UTC](https://forum.nachi.org/t/sediment-traps/67133/2 "2012-02-28T13:30:06Z")

</div>

Most manufacturers require them regardless . State that one is needed let him say one is not in his letterhead and if anything happens he is the one who will pay

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [February 28, 2012, 3:15pm UTC](https://forum.nachi.org/t/sediment-traps/67133/3 "2012-02-28T15:15:39Z")

</div>

Of all the possible reasons why it may not be necessary to have a sediment trap, this would not be one.

---

<div class="post-metadata">

**Author:** ![kbrittain](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kbrittain/32/59414_2.png) [@kbrittain](https://forum.nachi.org/u/kbrittain)\
**Post date:** [February 28, 2012, 3:56pm UTC](https://forum.nachi.org/t/sediment-traps/67133/4 "2012-02-28T15:56:09Z")

</div>

> [@clambert2](#):
>
> Most manufacturers require them regardless . State that one is needed let him say one is not in his letterhead and if anything happens he is the one who will pay

Let us know if he will do this or not.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [February 28, 2012, 4:47pm UTC](https://forum.nachi.org/t/sediment-traps/67133/5 "2012-02-28T16:47:19Z")

</div>

Code doesn’t provide that exception.

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [February 28, 2012, 5:41pm UTC](https://forum.nachi.org/t/sediment-traps/67133/6 "2012-02-28T17:41:09Z")

</div>

It is best to be at the appliance however it can be on the final drop to the appliance according to the CSA installation code.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [February 28, 2012, 5:50pm UTC](https://forum.nachi.org/t/sediment-traps/67133/7 "2012-02-28T17:50:08Z")

</div>

> [@kwood](#):
>
> It is best to be at the appliance however it can be on the final drop to the appliance according to the CSA installation code.

Should be after the appliance shut-off by the common sense rule. Otherwise, it couldn’t be cleaned out without shutting off gas at the main.

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [February 28, 2012, 5:56pm UTC](https://forum.nachi.org/t/sediment-traps/67133/8 "2012-02-28T17:56:29Z")

</div>

Yes I agree with that reasoning.

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [February 28, 2012, 6:53pm UTC](https://forum.nachi.org/t/sediment-traps/67133/9 "2012-02-28T18:53:31Z")

</div>

Thanks guys. I asked if he would put that writing and he said yes. He thinks I am an idiot for writing it up. Oh well I did my job.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [February 28, 2012, 7:04pm UTC](https://forum.nachi.org/t/sediment-traps/67133/10 "2012-02-28T19:04:35Z")

</div>

> [@jjimenez](#):
>
> Thanks guys. I asked if he would put that writing and he said yes. He thinks I am an idiot for writing it up. Oh well I did my job.

Tell him he’s incompetent.

2009 IRC G2419.4 (408.4) Sediment trap. Where a sediment trap is not  
incorporated as part of the appliance,\*\* a sediment trap shall be  
installed downstream of the appliance shutoff valve\*\* as close to  
the inlet of the appliance as practical. The sediment trap shall  
be either a tee fitting having a capped nipple of any length  
installed vertically in the bottom-most opening of the tee or  
other device approved as an effective sediment trap. Illuminating  
appliances, ranges, clothes dryers and outdoor grills need  
not be so equipped.

Commentary: In addition to the code requirement, most appliance  
manufacturers require the installation of a sediment  
trap (dirt leg) to protect the appliance from debris in the  
gas. Note that a drip leg is not the same as a sediment  
trap (see Section G2419.2). Sediment traps are necessary  
to protect appliance gas controls from the dirt, soil,  
pipe chips, pipe joint tapes and compounds and construction  
site debris that enter the piping during installation  
and repairs. Hazardous appliance operation could  
result from debris entering gas controls and burners.  
Despite the fact that utilities supply clean gas, debris  
can enter the piping prior to and during installation on  
the utility side of the system and on the customer side.

Sediment traps are designed to cause the gas flow to  
change direction 90 degrees (1.57 rad) at the sediment  
collection point, thus causing the solid or liquid contaminants  
to drop out of the gas flow [see Commentary Figure  
G2419.4(1)]. The nipple and cap should not be  
placed in the branch opening of a tee fitting because  
this would not create a change in direction of flow and  
would allow debris to simply pass/jump over the capped  
nipple collection point. Commentary Figure G2419.4(2)  
illustrates a relatively ineffective sediment trap, however,  
such configurations are not expressly prohibited  
by this section. The code does not specify a minimum  
length for the capped nipple, therefore, it could be from  
a close nipple on up. Three to 6 inches (76 to 152 mm)  
is the customary length. The capped nipple must be in a  
vertical plane to allow the sediments to fall in by gravity.  
The sediment trap must be as close to the appliance inlet  
as practical to be able to capture sediment from all of  
the piping upstream of the appliance connection. The  
sediment trap must be downstream of the appliance  
shutoff valve to allow the trap to be serviced after closing  
the upstream shutoff valve. Manufactured sediment  
traps are available that have the configuration of a  
straight section of pipe and are equipped with cleanout  
openings. Although it would be wise to install sediment  
traps at all appliance connections, they are not mandated  
by code for gas lights, ranges, clothes dryers and  
outdoor grills. These appliances are also susceptible to  
harm from debris in gas, especially ranges and clothes  
dryers, and the appliance manufacturer may require  
sediment traps where the code does not. The code’s  
logic is that these exempt appliances are manually operated  
rather than automatically operated; therefore,  
the user would be in attendance and aware of a  
problem.

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [February 28, 2012, 7:11pm UTC](https://forum.nachi.org/t/sediment-traps/67133/11 "2012-02-28T19:11:42Z")

</div>

Too bad we can’t use this like you can Joe.☹

---

<div class="post-metadata">

**Author:** ![jjimenez](https://avatars.discourse-cdn.com/v4/letter/j/a87d85/32.png) [@jjimenez](https://forum.nachi.org/u/jjimenez)\
**Post date:** [February 29, 2012, 12:17am UTC](https://forum.nachi.org/t/sediment-traps/67133/12 "2012-02-29T00:17:51Z")

</div>

Thanks Joe that really helps

---

<div class="post-metadata">

**Author:** ![cevans](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cevans/32/244194_2.png) [@cevans](https://forum.nachi.org/u/cevans)\
**Post date:** [February 29, 2012, 12:35am UTC](https://forum.nachi.org/t/sediment-traps/67133/13 "2012-02-29T00:35:57Z")

</div>

> [@jjimenez](#):
>
> I called out a furnace that did not have a sediment trap after the shut off valve.The HVAC guy said it did not needed one because the gas piping rose so high off the ground that it was useless. Any one ever heard that before?

Just ask him to point that exception out for you in the manufacturer’s installation specifications.

---

<div class="post-metadata">

**Author:** ![rcooke](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rcooke/32/57038_2.png) [@rcooke](https://forum.nachi.org/u/rcooke)\
**Post date:** [February 29, 2012, 2:53am UTC](https://forum.nachi.org/t/sediment-traps/67133/14 "2012-02-29T02:53:51Z")

</div>

**[http://www.questargas.com/brochures/59060\_401.pdf](http://www.questargas.com/brochures/59060_401.pdf)**]([http://www.questargas.com/brochures/59060\_401.pdf](http://www.questargas.com/brochures/59060_401.pdf))

136 pages of good info … Roy  
**Questar Gas Company**  
[FONT=Times New Roman][FONT=Times New Roman]Good Practices for  
Gas Piping  
and  
Appliance Installations  
[/FONT][/FONT]