# Service Conductors--3 in from the mast-4 in the Main Panel

**URL:** <https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669>\
**Category:** Misc. Discussion\
**Created:** [November 5, 2019, 3:01am UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669 "2019-11-05T03:01:07Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![gzahner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gzahner/32/177091_2.png) [@gzahner](https://forum.nachi.org/u/gzahner)\
**Post date:** [November 5, 2019, 3:01am UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/1 "2019-11-05T03:01:07Z")

</div>

![2019-10-4-104](https://global.discourse-cdn.com/internachi/original/3X/0/6/06593fd49f149842a51308760b2a487e42a6a3ec.jpeg) ![2019-10-4-112](https://global.discourse-cdn.com/internachi/original/3X/f/4/f4c5a38f88b5bc34737bf1e162204864d164e347.jpeg)

Hi All–  
Can you help me with this. I am relatively new and the gooseneck shows 3 conductors coming in from the power pole. But in the panel there are 4. White, Black, Red and Bare Neutral. Can someone explain this to me please. Thank you!!

---

<div class="post-metadata">

**Author:** ![dtearle](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dtearle/32/59716_2.png) [@dtearle](https://forum.nachi.org/u/dtearle)\
**Post date:** [November 5, 2019, 3:18am UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/2 "2019-11-05T03:18:31Z")

</div>

Disregard this message

---

<div class="post-metadata">

**Author:** ![gzahner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gzahner/32/177091_2.png) [@gzahner](https://forum.nachi.org/u/gzahner)\
**Post date:** [November 5, 2019, 3:20am UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/3 "2019-11-05T03:20:05Z")

</div>

Thanks. So that helps. Are u still confused where the 4th conductor is coming from?

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [November 5, 2019, 3:56am UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/4 "2019-11-05T03:56:25Z")

</div>

The multi strand aluminum is the grounding electrode conductor that terminates at meter socket.  
The multi strand aluminium is Not the neutral.

FYI: The neutral must have a jacket, can not be bare.

---

<div class="post-metadata">

**Author:** ![gzahner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gzahner/32/177091_2.png) [@gzahner](https://forum.nachi.org/u/gzahner)\
**Post date:** [November 5, 2019, 4:00am UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/5 "2019-11-05T04:00:18Z")

</div>

So is this ok? just a different way of doing it?

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [November 5, 2019, 4:04am UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/6 "2019-11-05T04:04:55Z")

</div>

Yes, it’s a very common way to do it.

The Black and Red cables are the ungrounded “hot” conductors.  
The White cable is the grounded conductor.  
The bare aluminum is the grounding electrode conductor.

The **grounding** electrode **conductor** is permitted to **terminate** at any point on the line side of the disconnecting means, including the **meter** socket enclosure when it is determined to be accessible and when acceptable to the serving utility - 250.24(A)(1).

---

<div class="post-metadata">

**Author:** ![gzahner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gzahner/32/177091_2.png) [@gzahner](https://forum.nachi.org/u/gzahner)\
**Post date:** [November 5, 2019, 4:10am UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/7 "2019-11-05T04:10:58Z")

</div>

Thank you so much. It’s interesting here in this part of NW Missouri I’ve never seen this. Did a ‘favor’ inspection for a Realtor down at the Ozarks Lake 3 hours away and saw this. First time. Thanks for the guidance!!

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [November 5, 2019, 11:39am UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/9 "2019-11-05T11:39:57Z")

</div>

> [@gzahner](#):
>
> Hi All–  
> Can you help me with this. I am relatively new and the gooseneck shows 3 conductors coming in from the power pole. But in the panel there are 4. White, Black, Red and Bare Neutral. Can someone explain this to me please. Thank you!!

There is something missing, since the panel has no main and is a MLO there must be a service disconnect between it and the drop. Also the conductors are not the same type. The bare aluminum is the EGC (equipment grounding conductor) run with the feeder to the panel.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 5, 2019, 12:00pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/10 "2019-11-05T12:00:12Z")

</div>

> [@rmeier2](#):
>
> MLO

What the heck is that?  
I wish you guys would stop doing that,.😜

---

<div class="post-metadata">

**Author:** ![gzahner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gzahner/32/177091_2.png) [@gzahner](https://forum.nachi.org/u/gzahner)\
**Post date:** [November 5, 2019, 1:20pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/11 "2019-11-05T13:20:24Z")

</div>

HI-There is a main disconnect. It is right out the door and behind this panel and in particular below the meter. Does this help?

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 5, 2019, 1:23pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/12 "2019-11-05T13:23:43Z")

</div>

So we are looking at a sub panel …  
That clears it all up.

---

<div class="post-metadata">

**Author:** ![gzahner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gzahner/32/177091_2.png) [@gzahner](https://forum.nachi.org/u/gzahner)\
**Post date:** [November 5, 2019, 1:25pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/13 "2019-11-05T13:25:25Z")

</div>

The main disconnect has nothing in it but the disconnect. So then this would be termed a sub panel?

---

<div class="post-metadata">

**Author:** ![jdepiero](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jdepiero/32/356888_2.png) [@jdepiero](https://forum.nachi.org/u/jdepiero)\
**Post date:** [November 5, 2019, 1:26pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/14 "2019-11-05T13:26:04Z")

</div>

MLO is main lug only

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 5, 2019, 1:30pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/15 "2019-11-05T13:30:12Z")

</div>

> [@gzahner](#):
>
> The main disconnect has nothing in it but the disconnect. So then this would be termed a sub panel?

Anything pass the first point of disconnect.

---

<div class="post-metadata">

**Author:** ![gzahner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gzahner/32/177091_2.png) [@gzahner](https://forum.nachi.org/u/gzahner)\
**Post date:** [November 5, 2019, 1:31pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/16 "2019-11-05T13:31:36Z")

</div>

Ok. I remember that now. Everybody who helped me on this thread THANK YOU VERY MUCH!!

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 5, 2019, 1:34pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/17 "2019-11-05T13:34:13Z")

</div>

Next time show all panels.

---

<div class="post-metadata">

**Author:** ![gzahner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gzahner/32/177091_2.png) [@gzahner](https://forum.nachi.org/u/gzahner)\
**Post date:** [November 5, 2019, 1:37pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/18 "2019-11-05T13:37:12Z")

</div>

Got it!!😁😀

---

<div class="post-metadata">

**Author:** ![gzahner](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gzahner/32/177091_2.png) [@gzahner](https://forum.nachi.org/u/gzahner)\
**Post date:** [November 5, 2019, 2:05pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/19 "2019-11-05T14:05:11Z")

</div>

![2019-10-4-107](https://global.discourse-cdn.com/internachi/original/3X/e/7/e7c57f65c1d149422236162e0064104209804b7f.jpeg)

fyi–here is the other panel.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 5, 2019, 2:23pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/20 "2019-11-05T14:23:57Z")

</div>

Yep ! The main.  
If you would have opened it up you would have solved your question.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [November 5, 2019, 3:01pm UTC](https://forum.nachi.org/t/service-conductors-3-in-from-the-mast-4-in-the-main-panel/157669/21 "2019-11-05T15:01:21Z")

</div>

> [@rlewis5](#):
>
> What the heck is that?  
> I wish you guys would stop doing that,.😜

Sorry about that. 🙂

> [@gzahner](#):
>
> HI-There is a main disconnect. It is right out the door and behind this panel and in particular below the meter. Does this help?

Yes that helps explain why there are four conductors at the sub-panel.