# Service Drop over the Roof

**URL:** <https://forum.nachi.org/t/service-drop-over-the-roof/22218>\
**Category:** Electrical Inspections\
**Created:** [November 24, 2007, 8:41pm UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218 "2007-11-24T20:41:53Z")\
**Posts on this page:** 9\
**Page:** 1

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [November 24, 2007, 8:41pm UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218/1 "2007-11-24T20:41:53Z")

</div>

Rather than relocating the cable to an alternative location, the Utility Company added an insulater to the cable to prevent damage from rubbing on the roof surface.

---

<div class="post-metadata">

**Author:** ![wdecker](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wdecker/32/174659_2.png) [@wdecker](https://forum.nachi.org/u/wdecker)\
**Post date:** [November 24, 2007, 9:11pm UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218/2 "2007-11-24T21:11:35Z")

</div>

Those crazy POCOs :mrgreen:

---

<div class="post-metadata">

**Author:** ![tdietrich1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tdietrich1/32/1561_2.png) [@tdietrich1](https://forum.nachi.org/u/tdietrich1)\
**Post date:** [November 24, 2007, 10:49pm UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218/3 "2007-11-24T22:49:53Z")

</div>

I see bugs. Was there a seal on the meter base?

tom

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [November 24, 2007, 10:57pm UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218/4 "2007-11-24T22:57:27Z")

</div>

No Drip Loop.

Cable over and in Contact with the Roof.

Bugs???

---

<div class="post-metadata">

**Author:** ![dduffy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dduffy/32/554_2.png) [@dduffy](https://forum.nachi.org/u/dduffy)\
**Post date:** [November 24, 2007, 11:01pm UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218/5 "2007-11-24T23:01:15Z")

</div>

Joe, you need to start your own Travesty section here…😃

I’m beginning to wonder who is finding crazier $hit…You—or Me?..:twisted: …:lol:

…😃 …](\*,)

---

<div class="post-metadata">

**Author:** ![tdietrich1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/tdietrich1/32/1561_2.png) [@tdietrich1](https://forum.nachi.org/u/tdietrich1)\
**Post date:** [November 24, 2007, 11:09pm UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218/6 "2007-11-24T23:09:41Z")

</div>

Split bolt connectors. They fail over time, so they are only used till the poco installs insulated crimps. So I flag this in my reports as an issue worth asking the seller about, and the poco for verifying job order is closed.

tom

---

<div class="post-metadata">

**Author:** ![gbeaumont](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gbeaumont/32/1094_2.png) [@gbeaumont](https://forum.nachi.org/u/gbeaumont)\
**Post date:** [November 24, 2007, 11:25pm UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218/7 "2007-11-24T23:25:04Z")

</div>

> [@jhagarty](#):
>
> No Drip Loop.
> 
> Cable over and in Contact with the Roof.
> 
> Bugs???

Hi Joe, that is all messed up, but as the utility company is their own AHJ all you can do is write it up, I have the same situation here at my own home, the utility sleived the service drop through an Aok tree, rather than cut it back.

Regards

Gerry

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [November 24, 2007, 11:25pm UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218/8 "2007-11-24T23:25:42Z")

</div>

> [@dduffy](#):
>
> Joe, you need to start your own Travesty section here…😃
> 
> I’m beginning to wonder who is finding crazier $hit…You—or Me?..:twisted: …:lol:
> 
> …😃 …](\*,)

Truly a Travesty. This was an inspect of a professional installation and apparently approved / completed by the Electric Utility Provider.

---

<div class="post-metadata">

**Author:** ![tallen](https://avatars.discourse-cdn.com/v4/letter/t/f04885/32.png) [@tallen](https://forum.nachi.org/u/tallen)\
**Post date:** [November 25, 2007, 12:22am UTC](https://forum.nachi.org/t/service-drop-over-the-roof/22218/9 "2007-11-25T00:22:08Z")

</div>

> [@jhagarty](#):
>
> Rather than relocating the cable to an alternative location, the Utility Company added an insulater to the cable to prevent damage from rubbing on the roof surface.

😃 I don’t think so joe…:mrgreen: