# Service Grounding with Pex

**URL:** <https://forum.nachi.org/t/service-grounding-with-pex/84449>\
**Category:** General Inspection Discussion\
**Created:** [February 13, 2014, 2:04am UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449 "2014-02-13T02:04:33Z")\
**Posts on this page:** 12\
**Page:** 1

<div class="post-metadata">

**Author:** ![jdryden](https://avatars.discourse-cdn.com/v4/letter/j/a88e4f/32.png) [@jdryden](https://forum.nachi.org/u/jdryden)\
**Post date:** [February 13, 2014, 2:04am UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/1 "2014-02-13T02:04:33Z")

</div>

In new housing with plastic pex piping is it okay to ground the Service panel to the gas line as it exits the house?(normal Service grounding is to a copper water supply line)

---

<div class="post-metadata">

**Author:** ![sstanczyk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sstanczyk/32/175851_2.png) [@sstanczyk](https://forum.nachi.org/u/sstanczyk)\
**Post date:** [February 13, 2014, 2:06am UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/2 "2014-02-13T02:06:05Z")

</div>

Still NO ! And chances are, the gas line to the street is plastic anyway. Are you sure this isn’t just the bonding conductor?

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [February 13, 2014, 2:20am UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/3 "2014-02-13T02:20:55Z")

</div>

“new housing” will generally have a UFER grounding system. Gas piping may not be used as the GEC.

---

<div class="post-metadata">

**Author:** ![jdeoliveira2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jdeoliveira2/32/57038_2.png) [@jdeoliveira2](https://forum.nachi.org/u/jdeoliveira2)\
**Post date:** [February 13, 2014, 7:56am UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/4 "2014-02-13T07:56:32Z")

</div>

Lightning will only strike once, in that scenario.

Trolling question?

---

<div class="post-metadata">

**Author:** ![linkster](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/linkster/32/608_2.png) [@linkster](https://forum.nachi.org/u/linkster)\
**Post date:** [February 13, 2014, 10:14pm UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/5 "2014-02-13T22:14:58Z")

</div>

Just use PVC conductors for your ground, plastic to plastic should work really well. If you can’t find any just use weed whacker cord, it’s almost as good, and will also provide a good plastic to plastic ground if the gas pipe is PVC too. :twisted:

---

<div class="post-metadata">

**Author:** ![dcossar](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dcossar/32/1880_2.png) [@dcossar](https://forum.nachi.org/u/dcossar)\
**Post date:** [February 15, 2014, 4:06pm UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/6 "2014-02-15T16:06:23Z")

</div>

On the serious side:

I usually see a ground wire leading from the panel into the basement floor.

I suspect there is a ground rod or plate under the concrete. I also see the gas pipe bonded to the panel.

Hope this helps

Cheers

---

<div class="post-metadata">

**Author:** ![yolhovsky](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/yolhovsky/32/60213_2.png) [@yolhovsky](https://forum.nachi.org/u/yolhovsky)\
**Post date:** [February 16, 2014, 12:59am UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/7 "2014-02-16T00:59:00Z")

</div>

> [@dcossar](#):
>
> On the serious side:
> 
> I usually see a ground wire leading from the panel into the basement floor.
> 
> I suspect there is a ground rod or plate under the concrete. I also see the gas pipe bonded to the panel.
> 
> Hope this helps
> 
> Cheers

Doug, that is a UFER ground that Jeff mentioned above.

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [February 16, 2014, 10:17am UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/8 "2014-02-16T10:17:05Z")

</div>

[http://www.esgroundingsolutions.com/about-electrical-grounding/what-are-some-different-types-of-grounding-electrode](http://www.esgroundingsolutions.com/about-electrical-grounding/what-are-some-different-types-of-grounding-electrode).

---

<div class="post-metadata">

**Author:** ![rcooke](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rcooke/32/57038_2.png) [@rcooke](https://forum.nachi.org/u/rcooke)\
**Post date:** [February 16, 2014, 12:59pm UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/9 "2014-02-16T12:59:53Z")

</div>

> [@kwood](#):
>
> [http://www.esgroundingsolutions.com/about-electrical-grounding/what-are-some-different-types-of-grounding-electrode](http://www.esgroundingsolutions.com/about-electrical-grounding/what-are-some-different-types-of-grounding-electrode).

The above did not work for me try this one… Roy

> **[E&S Grounding Solutions](https://esgrounding.com)**
>
> We ENGINEER, EDUCATE and EMPOWER the worlds leading electrical engineers and companies to become safer and more profitable, every single day.

> **[E&S Grounding Solutions](https://esgrounding.com)**
>
> We ENGINEER, EDUCATE and EMPOWER the worlds leading electrical engineers and companies to become safer and more profitable, every single day.

---

<div class="post-metadata">

**Author:** ![jdeoliveira2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jdeoliveira2/32/57038_2.png) [@jdeoliveira2](https://forum.nachi.org/u/jdeoliveira2)\
**Post date:** [February 16, 2014, 4:22pm UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/10 "2014-02-16T16:22:00Z")

</div>

Thank you Roy

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [February 16, 2014, 5:46pm UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/11 "2014-02-16T17:46:42Z")

</div>

Thanks Roy also.

---

<div class="post-metadata">

**Author:** ![dcossar](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dcossar/32/1880_2.png) [@dcossar](https://forum.nachi.org/u/dcossar)\
**Post date:** [February 16, 2014, 8:57pm UTC](https://forum.nachi.org/t/service-grounding-with-pex/84449/12 "2014-02-16T20:57:52Z")

</div>

> [@yolhovsky](#):
>
> Doug, that is a UFER ground that Jeff mentioned above.

Thanks I try to learn something every day:mrgreen:

Cheers