# Service Panel Used As Junction Box

**URL:** <https://forum.nachi.org/t/service-panel-used-as-junction-box/6504>\
**Category:** Electrical Inspections\
**Created:** [August 11, 2006, 4:14pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504 "2006-08-11T16:14:05Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![mbazzo](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mbazzo/32/57038_2.png) [@mbazzo](https://forum.nachi.org/u/mbazzo)\
**Post date:** [August 11, 2006, 4:14pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/1 "2006-08-11T16:14:05Z")

</div>

Inspected a home yesterday that had a new addition added to the back, the old service panel is being used as a junction box as a new service was installed in the addition. This is a new one on me and not sure if this can be done or not, what do you think?

---

<div class="post-metadata">

**Author:** ![jsieg](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jsieg/32/2298_2.png) [@jsieg](https://forum.nachi.org/u/jsieg)\
**Post date:** [August 11, 2006, 4:21pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/2 "2006-08-11T16:21:24Z")

</div>

I have seen it done in the past as well. Before I did home inspections. I saw it in a home over in Hazel Park, MI.

I don’t know the rules about this but would like to know what others think.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [August 11, 2006, 4:27pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/3 "2006-08-11T16:27:09Z")

</div>

So long as it’s covered, it’s not a problem. Was there a hinged cover in addition to the dead front?

---

<div class="post-metadata">

**Author:** ![Speedy\_Petey](https://avatars.discourse-cdn.com/v4/letter/s/f6c823/32.png) [@Speedy\_Petey](https://forum.nachi.org/u/Speedy_Petey)\
**Post date:** [August 11, 2006, 4:31pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/4 "2006-08-11T16:31:08Z")

</div>

It is done quite often by DIYers and often suggested to them for some reason.  
I don’t care for this practice AT ALL and do not know why it is done so often.  
To me it reeks of DIY, but if covered properly and not overloaded there is nothing illegal or unsafe about it.

---

<div class="post-metadata">

**Author:** ![mbazzo](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mbazzo/32/57038_2.png) [@mbazzo](https://forum.nachi.org/u/mbazzo)\
**Post date:** [August 11, 2006, 4:31pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/5 "2006-08-11T16:31:18Z")

</div>

Yes a hinged cover was attached to the dead front. Not sure how well the dead front even with a loosly latched cover would contain a fire with out breakers helping to seal the can.

---

<div class="post-metadata">

**Author:** ![mbazzo](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mbazzo/32/57038_2.png) [@mbazzo](https://forum.nachi.org/u/mbazzo)\
**Post date:** [August 11, 2006, 4:36pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/6 "2006-08-11T16:36:20Z")

</div>

> [@Speedy Petey](#):
>
> I don’t care for this practice AT ALL and do not know why it is done so often.  
> To me it reeks of DIY, but if covered properly and not overloaded there is nothing illegal or unsafe about it.

I don’t like the looks of it either and certainly a dyi er at work. All those wire nuts made me alittle nervous as well. thought crimped connections would have been a better option.

---

<div class="post-metadata">

**Author:** ![jbushart](https://avatars.discourse-cdn.com/v4/letter/j/919ad9/32.png) [@jbushart](https://forum.nachi.org/u/jbushart)\
**Post date:** [August 11, 2006, 4:55pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/7 "2006-08-11T16:55:34Z")

</div>

Is there not a general provision in the code that prohibits the use of equipment for anything other than its designed purpose?

---

<div class="post-metadata">

**Author:** ![Speedy\_Petey](https://avatars.discourse-cdn.com/v4/letter/s/f6c823/32.png) [@Speedy\_Petey](https://forum.nachi.org/u/Speedy_Petey)\
**Post date:** [August 11, 2006, 5:10pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/8 "2006-08-11T17:10:19Z")

</div>

> [@mbazzo](#):
>
> All those wire nuts made me alittle nervous as well. thought crimped connections would have been a better option.

I would not say that at all. A correct wire nut plice is as sound as anything else.  
Crimping is the stuff of larger service conductors and stranded low-voltage wiring.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [August 11, 2006, 5:14pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/9 "2006-08-11T17:14:22Z")

</div>

> [@jbushart](#):
>
> Is there not a general provision in the code that prohibits the use of equipment for anything other than its designed purpose?

Yes, there is, and there is some contention as to whether or not splices and wire nuts are allowed in a panel board. It really comes down to the interpretation by the AHJ.

Typically, the conductors for the new service equipment are spliced at the existing panel (which is gutted) to the circuits. This is done by licensed EC’s quite commonly.

---

<div class="post-metadata">

**Author:** ![bkelly1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bkelly1/32/1536_2.png) [@bkelly1](https://forum.nachi.org/u/bkelly1)\
**Post date:** [August 11, 2006, 5:18pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/10 "2006-08-11T17:18:17Z")

</div>

It is alright here, and in Commercial applications I liked to install, and use terminal strips. They look so much better

---

<div class="post-metadata">

**Author:** ![psmothers](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/psmothers/32/60087_2.png) [@psmothers](https://forum.nachi.org/u/psmothers)\
**Post date:** [August 11, 2006, 5:45pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/11 "2006-08-11T17:45:24Z")

</div>

It is done by electricians all the time here.

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [August 11, 2006, 6:03pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/12 "2006-08-11T18:03:47Z")

</div>

Jeff, the panelboard was removed so this is just an enclosure. I have heard of AHJs who want the hinged cover screwed shut tho.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [August 11, 2006, 7:06pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/13 "2006-08-11T19:06:17Z")

</div>

> [@Greg Fretwell](#):
>
> Jeff, the panelboard was removed so this is just an enclosure. I have heard of AHJs who want the hinged cover screwed shut tho.

I know Greg, I was referencing the post by James where he commented on “listing and labeling.” This used to be a “panelboard” enclosure and has been modified into a “junction box,” which (technically) goes against its “listing and labeling.”

Every time I have seen this condition, the hinged cover has been screwed shut as well.

---

<div class="post-metadata">

**Author:** ![jtedesco1](https://avatars.discourse-cdn.com/v4/letter/j/258eb7/32.png) [@jtedesco1](https://forum.nachi.org/u/jtedesco1)\
**Post date:** [August 11, 2006, 8:42pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/14 "2006-08-11T20:42:18Z")

</div>

It was and still is a “CABINET” and according to its Listing and purpose is not a “JUNCTION BOX” and violates 110.3(B).

If further clarification is needed, the UL site [www.ul.com](http://www.ul.com) includes a telephone number that can be called to clarify my personal opinion.

The **Panelboard** was removed from a **Cabinet** and although a common practice, is legally considered to be a conflict.

[2006 UL White Book (large file - 5MB)](http://www.ul.com/regulators/clicks.cfm?ID=41&table=TechLibIndex)

See Cabinets

---

<div class="post-metadata">

**Author:** ![vmitchinson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/vmitchinson/32/1605_2.png) [@vmitchinson](https://forum.nachi.org/u/vmitchinson)\
**Post date:** [August 11, 2006, 9:03pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/15 "2006-08-11T21:03:33Z")

</div>

It is quite common here when Old houses that had fuse boxes are up dated to current standards. How ever the old fuse box is removed and a 6 x 6 x 3 metal box with screwed on cover is installed. Licensed Electricians and Electrical Inspectors have approved this so I do not question it.  
Usually there are two or more circuits from the new panel connected inside the new box.  
I do however wonder about the rule that forbids more then one circuit inside the same junction box.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [August 11, 2006, 10:02pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/16 "2006-08-11T22:02:08Z")

</div>

Enclosures are referred to as “cabinets” when they are equipped with a hinged door as their means of access.

Once this door is sealed, by means of “permanent” fasteners (screws), is it still considered a “cabinet?” It seems to me that it would now be simply considered an “enclosure.”

---

<div class="post-metadata">

**Author:** ![jtedesco1](https://avatars.discourse-cdn.com/v4/letter/j/258eb7/32.png) [@jtedesco1](https://forum.nachi.org/u/jtedesco1)\
**Post date:** [August 11, 2006, 10:20pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/17 "2006-08-11T22:20:46Z")

</div>

> [@jpope](#):
>
> Enclosures are referred to as “cabinets” when they are equipped with a hinged door as their means of access.
> 
> Once this door is sealed, by means of “permanent” fasteners (screws), is it still considered a “cabinet?” It seems to me that it would now be simply considered an “enclosure.”

See Article 312. I agree and if this was noted on the report the Home Inspector would be giving an opinion that is recognized by the electrical industry and scholars who spend countless hours helping them out with only one thing in mind, SAFETY.

The old cabinet used as the splice box here should be covered with a cover that is screwed on, and so noted as a “Splice Box”

PS: Keep in mind that someone, :roll: someday may say Duh! I am gonna restore this cabinel and put in this old panelboard I found in the flea market! 😃 😃 !

---

<div class="post-metadata">

**Author:** ![bglass](https://avatars.discourse-cdn.com/v4/letter/b/edb3f5/32.png) [@bglass](https://forum.nachi.org/u/bglass)\
**Post date:** [August 11, 2006, 10:57pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/18 "2006-08-11T22:57:36Z")

</div>

Over 29 years of home inspecting in the Denver, CO area, I have seen hundreds of old fuse boxes and obsolete breaker panels gutted out and used for junction boxes to extend the existing circuits to the the new panel. The wire nut joints must comply with the requirements of the NEC. The city electrical inspectors approve these every day and insist on two things:  
The box must remain accessible, and the cover must be screwed shut.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [August 12, 2006, 1:12am UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/19 "2006-08-12T01:12:26Z")

</div>

> [@jtedesco1](#):
>
> The old cabinet used as the splice box here should be covered with a cover that is screwed on, and so noted as a “Splice Box”

This is exactly what is required around here by the local AHJ’s.

---

<div class="post-metadata">

**Author:** ![mbazzo](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mbazzo/32/57038_2.png) [@mbazzo](https://forum.nachi.org/u/mbazzo)\
**Post date:** [August 12, 2006, 2:20pm UTC](https://forum.nachi.org/t/service-panel-used-as-junction-box/6504/20 "2006-08-12T14:20:37Z")

</div>

Thanks for all of your help guys, I appreciate it